Hello chaps and chapettes,
Continuity of final ring circuit I measured:

L-L = 1.45
E-E = 0.8
but measuring N-N I got 108.8....???!!!!!!

Any ideas..? Or are those readings good in my limited experience and consequently I'm an idiot.

A out of date Cadbury's cream egg for the most sarcastic answer but a sensible one would be nice.
 
Not meaning to sound cheeky but if you don't know if those readings are good or bad and you don't know what would cause those readings then you should stop doing electrical work and go back to learning.
 
Nice one Murdoch you might win with that
end to end on L-L and N-N should be the same and E-E should be greater if the csa of earth is reduced to that of L-L.
if this is for an exam then make sure you use R1 for line Rn nutral and R2 for earth any way hope this helps .
 
Hello chaps and chapettes,
Continuity of final ring circuit I measured:

L-L = 1.45
E-E = 0.8
but measuring N-N I got 108.8....???!!!!!!

Any ideas..? Or are those readings good in my limited experience and consequently I'm an idiot.

A out of date Cadbury's cream egg for the most sarcastic answer but a sensible one would be nice.


They are Not very good readings to be honest (post was edited by admins, the original word is not acceptable on these forums) but it did rhyme with right.
 
Last edited:
Nice one Murdoch you might win with that
end to end on L-L and N-N should be the same and E-E should be greater if the csa of earth is reduced to that of L-L.
if this is for an exam then make sure you use R1 r1 for line Rn rn nutral and R2 r2 for earth any way hope this helps .


Corrections in red
 
or a loose connection in OP's head. ( where's me cream egg?)
 
Whats the problem there fine put it back together and walk away. I am sure a real spark will love the job to fix it after the fire.

(thats my entry for the creme egg!)
 
L-L should be within (*.**) of N-N. E-E should be *.** x greater than the the values you recieved for L and N if the cpc isn't the same as the conductors.

GN3 and OSG can be quite useful you know...
 
so can david cockburn's efforts, when you run out of bog roll.
 
Leeds United are Short Sighted,
Never scored a goal in history...
They wear rubies on their boobies,
Sha la la la la, la la la la.

(bring back my childhood)
 
Im actually really excited too find out who se7aq is going to award this cream egg too.

Genuinley.

Me personally would like him to come back and say he has rectified his problem, then we can all take our right hand and place it on our left shoulder, Then give ourselves a pat on the back for being so helpful
 

Reply to Continuity of Final Ring circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
650
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock