Hi guys, I have recently bought a Fluke 1652C and I am trying to work out how to carry out testing (course coming up soon) however I am a bit stuck with a continuity test I wanted to do on a ring circuit and would appreciate some help !

I was lucky enough to have an empty flat so carried out safe isolation, polarity of incoming feed, then ZE and PFC, however when I tried to do the continuity test in the consumer unit all the earths are connected on one main bar with no numbering on at all. There were about 20 earth connections and in the end I gave up !

Is there some magic way to work out which CPC's belong on which circuit ?

Thank you

Mike

PS All the wiring comes out of the wall behind the CU and it is impossible to see them !
 
if you can't physically see the cpc's coming out the T/E at the CU, all you can do is dis all the cpc's, bonding and main E, then link L and E at end of circuit, and ohm meter to find which is which. on RFCs, fins which cpc's are s/c to each other first. that will eliminate a few.
 
Thanks telectrix, I didn't think of joining the L & E together at the other end of the circuit, at least that way I can stay at the CU to carry out the OHMS testing. I guess I could use my "magic plug" as described by the Part P Doctor and put a link between L & E on that with one of my test leads from the Fluke. I suppose the other way would be to undo a socket and connect the L & E using may be a WAGO ? Unless I am missing an easier way ?
Thanks again Mike
 
you can use your breakout box and a link, but bear in mind that you will measure the R1+R2 + any resistance in the breakout and link. be sure to safely isolate and lock off the CU first, though.
 
Cool, back to the flat for more fun and games !
Thanks telectrix, all the best Mike
 
And dont forget you are trying to find 2 CPC's when you have disconnected them all and carrying out Tels method.

If you have the course planned, then this will be good experience for you. for some reason it is ring continuity testing that seems to get most people tied up in knots.

Once you have identified your conductors, try to test the ring as per GN3, and if you dont fully understand it , then shout up and ask, it is really easy once you know how.

Cheers.....................Howard
 
Hi guys, I have recently bought a Fluke 1652C and I am trying to work out how to carry out testing (course coming up soon) however I am a bit stuck with a continuity test I wanted to do on a ring circuit and would appreciate some help !

I was lucky enough to have an empty flat so carried out safe isolation, polarity of incoming feed, then ZE and PFC, however when I tried to do the continuity test in the consumer unit all the earths are connected on one main bar with no numbering on at all. There were about 20 earth connections and in the end I gave up !

Is there some magic way to work out which CPC's belong on which circuit ?

Thank you

Mike

PS All the wiring comes out of the wall behind the CU and it is impossible to see them !
Three words: patience, logic & tenacity
 
If I'm testing ring continuity for an EICR, I'll sometimes break the ring at a socket and test there. Then I only have two CPCs to deal with.
 
Always good on those old 3036 boards where you cant work out what goes where and you dont want to start meddling incase something breaks!
 
Always good on those old 3036 boards where you cant work out what goes where and you dont want to start meddling incase something breaks!

Or a stray wire makes its way over to the incoming line terminal which has lost its little push-on cover.
 
Always good on those old 3036 boards where you cant work out what goes where and you dont want to start meddling incase something breaks!

This is exactly the thinking needed for the 2395 exam and periodic insp and test in real life. It says somewhere in GN3 that consideration must be given to unnecessary dismantling or words to that effect, just for the reason you mention.

Its worth remembering.

Cheers...........Howard
 
linking the live and cpc for the r1r2 tests this is where the lever wago's come into their own
 

Reply to Continuity Testing Help please ! in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
474
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
766
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
610
Hi, I would love some help understanding an issue Iā€™m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi guys. I posted yesterday about a suspected faulty starter motor.. I've had the starter out and cleaned everything up and all seems to be...
Replies
6
Views
772

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock