TheCodboy

-
Arms
Reaction score
109
Hi all,I found a 6mm “cooker” circuit feeding 4 sockets in the kitchen as a radial. R1+R2 tests fine and Zs is low. Can’t see where they are jointed but it goes from 6mm to 2.5mm. If everything tests fine, can’t see a problem leaving it as is. Will have to downsize the mcb as it’s currently on a 32. It’s an old apartment within a block of apartments, probably 60’s built. Shows no sign of thermal damage etc. Can anyone see anything wrong I’m missing? What should I put on the paperwork for the conductor sizes? Many thanks!
 
Lolypop lolypop, oh lolly lolly pop.
Reminds me of a song!!
 
OP, if the cooker is no longer there then maybe they have joined the cables in the back box of the cooker switch and then plastered over it.
 
Record as the minimum csa (2.5) but make a note of it!
Might be work trying to locate the joint though as said earlier could just be plastered over!
 

Reply to Cooker circuit used as kitchen sockets radial in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
679
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
823
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
578

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock