Hello
I’ve pulled out a electric oven and the connection plate at the back for the cooker circuit has 2.5mm hardwired to the 6mm circuit for a 1.76kw load and also a 6mm connecting a induction hob,unknown load.
Does the 2.5mm need to be fused down or is it okay being spurred off the cooker circuit?
 
Hi - sorry to start with this - what do the manufacturer’s installation instructions have to say?
I assume it’s got a 32A mcb on the circuit?
 
The 2.5 doesn't necessarily need fusing down as the oven is likely to be a fixed load which is not subject to overload. In this case cables can usually be sized according to design current rather than nominal current.
 
Hi - if manufacturer is silent and the 2.5 mm flex is suitable I’d press on. The circuit 6mm twin and earth has 2.5mm cpc which is deemed fit for purpose. The 2.5mm flex has the same size conductor for cpc so I don’t see an increased risk during fault clearance :) .
 

Reply to Cooker circuits fusing down ??? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
952
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
864
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi So converting a 6mm cooker connection point into a 13a unswitched fuse spur with the load being a 2.5mm pre wired cable from a oven . is this...
Replies
2
Views
2K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
704

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock