Discuss Cooker / Hob connection in the Electrical Appliances Forum area at ElectriciansForums.net

Reaction score
13
Just had a new kitchen installed. The new cooker and hob didn't come with any cable. The hob is rated at 6Kw and the single oven at 2.2Kw. The circuit is a 32A mcb, 6mm t&e to a ccu and then 6mm down to the connection unit.

MI says to use H05V2V2-F T min 90C. Is this Butyl? I was going to buy 6mm 3 core and wire both the hob and cooker into the connection unit. Are they normally big enough to take two lots of 6mm? Is there a better way to do it?

Cheers.
 
Without diversity 2.5mm was just too small from memory. I don't think price wise there was too much difference between 2.5 and 4.0 mm, especially as I'm only buying 4 metres.
4mm heat resistant flex can be physically quite large when trying to connect to an appliance, especially a hob. Why not apply diversity?
 
4mm heat resistant flex can be physically quite large when trying to connect to an appliance, especially a hob. Why not apply diversity?

Good point I didn't think about the overall diameter. I think 2.5mm could take 25A whereas 6kw comes out at 26A, so there wasn't much in it anyway.
How would you terminate it onto the hob and oven? I thought about using insulated ring crimps but it doesn't look like the terminals are designed for them. I didn't want to just wrap the cores around the terminals.
 
What make of hob is it? Majority I've connected have kind of screw cage terminal. Think you'll find little room for any insulated lugs, but you should use a suitable bootlace lug.
 
this dual cooker connection outlet plate by scholemore is one of those products that have come on the market that makes connection of two appliances so easey
 

Reply to Cooker / Hob connection in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
Replies
2
Views
383
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
681
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
633
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock