Discuss Cooking appliances. Diversity versus practice in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
2
Hi, I have a customer who has bought a 7Kw hob to compliment a 4.8Kw double oven. He didn't realise the extra power consumption would put additional loading on the existing 6mm cable. My initial response was to tell him that an additional circuit was required and due to locations of consumer unit and hob it won't be straightforward
However I looked at diversity regarding cooking appliances and 51amps loading reduces to 23 or 28 amps which is within the capacity of the existing wiring.
I will probably still go with the additional circuit but what's the point of having diversity if we don't apply it. Thanks for your thoughts.
 
Whats the point of cable and current carrying capacities if you are then going to disregard all the evidence and recommendations to then make up your own presumptions and install extra cable where none may be required
 

Reply to Cooking appliances. Diversity versus practice in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, I'm getting a 32a induction hob and a 13a oven installed as part of a kitchen refurb. The existing cooker circuit is 6mm protected by a...
Replies
7
Views
2K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
Hi all, Looking for some advice if possible please! Got one if then jobs that you get roped in to and that’s turned from a quick simple...
Replies
3
Views
3K
Hi, I would appreciate some views on the following issue I have. The Cooker radial in a house has been wired in 2.5mm T&E, to save the expense...
Replies
12
Views
3K
Hello, I am getting a bit bogged down with detail as I always try my best to meet every best practice but I am very out of practice as I have...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock