Discuss council advice in the UK Electrical Forum area at ElectriciansForums.net

jon small

-
Mentor
DIY
Reaction score
38
just been to help my neighbour and thought I'd share with the forum, she's painting walls outside of her wet room / bathroom and got a belt off the paint brush, puts brush down and without thinking touches wall - another zap! so she phones the council helpline explains situation to call centre monkey - gets passed to duty head of maintenance explains again and is advised " get someone else to touch wall in case your imagining it or stick a piece of gaffer tape ( wet painted wall ffs ) if your worried, will try to get someone out next week sometime as a 50 mile round trip and not really a priority"


bear in mind single mother 4 young kids just out of abusive relationship and wall by wet room, kitchen and only entrance / exit to property.


went round to look and found a nail through unearthed metal conduit containing switch line drop that had several layers of paint over protecting it till she sanded the wall and applied paint.


I spoke to council to explain situation and was told they might get a spark out tonight or might wait for a job order next week, 10 mins later they phone me back to ask if I thought she'd put the nail in to hang a picture ( between 2 architraves 3.5 inches apart so would be very small picture ) obviously hoping to offload blame and make it chargeable, I said definitely an old nail and explained that I considered the advice given earlier to be very ill thought out and potentially lethal guys attitude seemed to be - oh well it's only a council tenant / single mother ( lowlife scum ) when I asked if they'd authorise me to repair as I'm a fully qualified spark answer was no but suddenly he decided he could get a spark out immediately so will see what happens - makes me so angry some salaried bell end can be so cavalier with other peoples lives b@574*%5
 
You should go and sit in the living room Jon and pretend you are not a spark and see what he says about it when he turns up, he may try to gazzump you with bull and you can then make him look a prat if he does by exposing the fact you are a sparky lol, I would love to be a fly on the wall when that happened.
 
Welcome to the public sector, they don't work like most normal businesses do. Far too many hoops and such like to jump through to get even the smallest job done. Spent several years working in it and could never get my head around it.
 
You should go and sit in the living room Jon and pretend you are not a spark and see what he says about it when he turns up, he may try to gazzump you with bull and you can then make him look a prat if he does by exposing the fact you are a sparky lol, I would love to be a fly on the wall when that happened.

This... Definitely do this. Maybe hook up a live webcam so we can observe.

Disclaimer- not in a weird way
 
council spark should be turning up at 9pm will be there just for fun to see what happens
Can't wait, make sure you let us know what happened, I wonder if he even bothers to get a tester out of the van? and even worse will he just create a joint and shove it in the wall lol
 
Can't wait, make sure you let us know what happened, I wonder if he even bothers to get a tester out of the van? and even worse will he just create a joint and shove it in the wall lol

You will probably find this will be a contractor with a call out contract and not one of the council monkeys who would do just that. So more than likely they will just isolate the fault and return on Monday during office hours.
 
well he finally turned up 3/4 hour late, had a look and said "there's a nail through the wire" then got out hammer and bolster to chop out conduit (flimsy oval not real conduit) to "repair" wire, I pointed out (1) my young daughter was asleep 10 feet away (2) easy job to pull the nail out,pull in new switch line as only 1 board to lift, no carpet to worry about, trap already cut and screwed - can't do that without job order ffs! quicker and easier than chopping out and "repairing" existing so I suggested pulling sw line from rose so other lights could go back on and come back another day to complete - hallelujah we have a winner so at least it's safe now and most lights working but has taken from about 4.30 till now to get it sorted bang out of order really wonder how long til they come back and sort it - wish I'd just done the job as a favour but on crutches at the mo so can't reach lights grr but at least get plenty of quality drugs for free!!
 
Welcome to the public sector, they don't work like most normal businesses do. Far too many hoops and such like to jump through to get even the smallest job done. Spent several years working in it and could never get my head around it.

Worked in the public sector for 16 months and know exactly what you're talking about! lol
 
well he finally turned up 3/4 hour late, had a look and said "there's a nail through the wire" then got out hammer and bolster to chop out conduit (flimsy oval not real conduit) to "repair" wire, I pointed out (1) my young daughter was asleep 10 feet away (2) easy job to pull the nail out,pull in new switch line as only 1 board to lift, no carpet to worry about, trap already cut and screwed - can't do that without job order ffs! quicker and easier than chopping out and "repairing" existing so I suggested pulling sw line from rose so other lights could go back on and come back another day to complete - hallelujah we have a winner so at least it's safe now and most lights working but has taken from about 4.30 till now to get it sorted bang out of order really wonder how long til they come back and sort it - wish I'd just done the job as a favour but on crutches at the mo so can't reach lights grr but at least get plenty of quality drugs for free!!
Honestly, if I was the council appointed spark, you would irritate the **** out of me suggesting what I should do. Id be thinking************
 
Last edited by a moderator:
apologies in advance to mods if this is out of order

meggerman - who the ************do you think you are calling me a ************ on crutches wannabe spark but cant". you don't know me or my situation, (1) I'm not a sponger I still work for a living even on crutches , (2) been a fully qualified apprentice trained spark for over 25 years not a Electrical Trainee , (3) the guy was a bit out of his depth and going to chop out wall, cut away conduit and tape up the cable - do you consider that acceptable ? and he asked for advice from me which I was happy to give in a non condescending way - it's called professional courtesy, google it if you don't understand and (4) if you said that to my face even on crutches ************
 
Last edited by a moderator:
no just defending myself from a lazy half assed judgement from someone who doesn't know me or my situation and wasn't there , I'm a pacifist really right up to the point I have the red mist blackout
 
Jon , I do not think it was meant at you in person !?
I have to admit that when I did out of hours for a large southern association , it would be somewhat annoying turning up in the small hours to find some smart arse trying to tell you how to do your job .
And although his approach to fixing the problem may of seemed daft , you have to remember that he is only being paid to make it safe for another in hours department to fix it in day light , and will at the very least not get paid for his extra effort and at the worst get the boot for none sanctioned work !
I know this ludicrous fact first hand and is why I only covered the contract for 9 months in the end , because it did not sit well with me to just bodge a repair and would not do so . Don't get me wrong it was phenomenal money whilst I did it , but it did not feel like honest money !
I mean no disrespect in my post and think it was good on you to hang around for her to make sure she did not get had over .
 
Come on guys, Jon is using a bit of poetic license here to have a go at the council contractor system. He has contradicted himself already stating he asked council if they could give him the job but they wouldn't and in later post says what a shame he could not do job as he is on crutches and enjoying the free drugs!! Also, who are we to believe the council sent to this job, a handyman perhaps? Must have been cause there is no way even the most mediocre of sparks would be bamboozled with this basic job and turn perplexed to the armchair spark waving his sticks at him for a solution.
 
sorry for the rant guys have had a bad day and was right grumpy, do not take too well to being accused of being a lazy, half assed wannabe scrounger by someone with no knowledge of me, personal attacks like that bring out my dark side
I understand the way council work is handled as the firm I worked a few years back did a lots of council / housing association work and I was on 24 hour call for electrical and plumbing emergencies and was always happy to listen to the advice of other professionals and still am as sometimes another pair of eyes and brain will come up with something easier / better as a solution to a problem.
that said would still never put speed /expedience ahead of safety - too much of that going on these days from those lacking training / experience / concience
 
Honestly, if I was the council appointed spark, you would irritate the **** out of me suggesting what I should do. Id be thinking *********** on crutches wannabe spark but cant".

apologies in advance to mods if this is out of order

meggerman - who the ******do you think you are calling me a *********on crutches wannabe spark but cant". you don't know me or my situation, (1) I'm not a sponger I still work for a living even on crutches , (2) been a fully qualified apprentice trained spark for over 25 years not a Electrical Trainee , (3) the guy was a bit out of his depth and going to chop out wall, cut away conduit and tape up the cable - do you consider that acceptable ? and he asked for advice from me which I was happy to give in a non condescending way - it's called professional courtesy, google it if you don't understand and ************

Any more and you'll both be on a weeks vacation from the forum.
 
appology offered to marvo and the forum, I went off on one and will calm down , can't stand people who make judgements and personal attacks without knowing facts.
this armchair electrician ( the free drugs reference was meant to be tongue in cheek ) would have got my apprentice to do the part of job that I couldn't if the council had authorised the repair but instead they sent someone who was young and inexperienced ( cheap ) and didn't really want to be out at 10 pm on a saturday night and looking for a quick easy solution.
Meggerman I withdraw the bit about the teeth have had a cr*p day and it was an ill judged reaction on my part but hope you will lay off the personal attacks as I work as hard as anyone and am always willing to talk with other members of the trade exchanging ideas and knowledge both ways courteously without demeaning anyone. I have made no personal comments about you as I don't know you please extend the same courtesy to me as you don't know me and let us go forward in a polite, professional way.
 

Reply to council advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
1K
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
1K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
593
Evening all, Currently 1st fixing new extension however the existing cooker hood duct which was on outside wall will now be part of new utility...
Replies
2
Views
692

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock