Discuss Cpc connection wylex in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
15
Hello can anyone advise what they would do in this situation please. I have a wylex 100amp switch fuse that has an incoming and out going cpc connection which takes up to a 16 mm cpc. I have 16mm incoming and outgoing cpc, however how do I then earth the enclosure and the banjo as the cpc connection has no connection with the enclosure
 
Is it one of those where there are the earth terminals at the main switch isolated from the earth terminal on the back box.
 
Hello can anyone advise what they would do in this situation please. I have a wylex 100amp switch fuse that has an incoming and out going cpc connection which takes up to a 16 mm cpc. I have 16mm incoming and outgoing cpc, however how do I then earth the enclosure and the banjo as the cpc connection has no connection with the enclosure
 

Attachments

  • FF8EEE30-9A68-4E7E-A4D8-AFA627336585.png
    974.3 KB · Views: 30
It is a stupid design, being 100A I would have thought that terminal would take 16.0 have you tried it.
 
Tails in swa out
Could you just take the 16mm CPC to a crimp lug bolted to the SWA's banjo and, assuming 3C SWA, also put a lug on the cable's SWA conductor to the same bolt?

i.e. Ignore the switch's through-CPC connection and the box's terminal strip completely.

EDIT: Also you could use a nylock nut if concerned about it coming loose.
 
Could you just take the 16mm CPC to a crimp lug bolted to the SWA's banjo and, assuming 3C SWA, also put a lug on the cable's SWA conductor to the same bolt?

i.e. Ignore the switch's through-CPC connection and the box's terminal strip completely.

EDIT: Also you could use a nylock nut if concerned about it coming loose.
Yes I think that is the only option, it’s a lot of extra faff and the switches are not cheap
 
Yes I think that is the only option, it’s a lot of extra faff and the switches are not cheap
Could you knock the existing small terminal block off the box and fix something like this in its place with a pair of machine screws:

https://www.NoLinkingToThis/p/ced-4-way-earth-block/12386

You might need to have nuts on top and use countersunk heads coming through from the back to is fixes flush though.
 
Could you knock the existing small terminal block off the box and fix something like this in its place with a pair of machine screws:

https://www.NoLinkingToThis/p/ced-4-way-earth-block/12386

You might need to have nuts on top and use countersunk heads coming through from the back to is fixes flush though.
That’s a good option it’s a shame I have fifteen to do of these
 

Attachments

  • F4409C8C-B1A3-4561-98BF-31944FDE34FB.jpeg
    165.9 KB · Views: 22
Could it be fixed physically with one of the box fixing screws, then a 6mm jumper to the box's terminals? Or maybe better just a 10mm jumper to lug on piranha / Earthing nut as quicker than banjo, etc?
I will get over with unnecessary work as the switch fuse by wylex is very poorly designed
Could it be fixed physically with one of the box fixing screws, then a 6mm jumper to the box's terminals? Or maybe better just a 10mm jumper to lug on piranha / Earthing nut as quicker than banjo, etc?
i still think there are a lot of these installed where the installer thinks the cpc connection is common to the enclosure
 
It really is a terrible design putting in such a small separate terminal however Wylex may have calculated the worst scenario for fault protection and that a 6.0 would satisfy. I would email them.
 
They are rubbish considering the price of them, as usual the designer has never had to fit one or they would have noticed the massive cock up with the earth terminal!
The last one of those I fitted I ran the SWA cpc to the earth banjo bolt and lugged the 16mm outgoing on that as well. As stated above an earth nut would probably be quicker!
Sy
 
They are rubbish considering the price of them, as usual the designer has never had to fit one or they would have noticed the massive cock up with the earth terminal!
The last one of those I fitted I ran the SWA cpc to the earth banjo bolt and lugged the 16mm outgoing on that as well. As stated above an earth nut would probably be quicker!
Sy
Yes I agree that’s what I will do thank you
 
Yes but if it’s 100amp supply and both 16mm earth connections are used there is no where to get another earth bond from
Put a separate 6.0 in. I would personally email them they have taken a real step backward from the previous design.
 
Yes I will and I I get a reply I will let you know
I’ve fitted loads of these switch fuses. In fact I will be fitting one on Friday coming.

I ignore the earth terminals with Allen heads. I just use the terminal for on the back of the enclosure which you think only takes 6mm2. Unless they have changed the design in the past couple of months (very much doubt) then this earth bar has space for 3x 16mm2 cables. It may look as though it doesn’t but I’ve done it many times. One incoming earth, one outgoing earth and one to banjo.
 
I’ve fitted loads of these switch fuses. In fact I will be fitting one on Friday coming.

I ignore the earth terminals with Allen heads. I just use the terminal for on the back of the enclosure which you think only takes 6mm2. Unless they have changed the design in the past couple of months (very much doubt) then this earth bar has space for 3x 16mm2 cables. It may look as though it doesn’t but I’ve done it many times. One incoming earth, one outgoing earth and one to banjo.
I asked in #13 If a 16.0 would fit.
 
I’ve fitted loads of these switch fuses. In fact I will be fitting one on Friday coming.

I ignore the earth terminals with Allen heads. I just use the terminal for on the back of the enclosure which you think only takes 6mm2. Unless they have changed the design in the past couple of months (very much doubt) then this earth bar has space for 3x 16mm2 cables. It may look as though it doesn’t but I’ve done it many times. One incoming earth, one outgoing earth and one to banjo.
Hi Matt I really didn’t think you could get 16mm in that little earth block
 
Put a separate 6.0 in. I would personally email them they have taken a real step backward from the previous design.
I've always rated Wylex as decent and solid but they've taken a few backward steps, IMO. That looks a bit of a mess all round. As someone said, go back to the old method and link everything via chassis bolt.
With their latest CU's the whole internal unit is no longer fully removal from the chassis making things awkward with replacement units.
 

Reply to Cpc connection wylex in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
893
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
Not the usual per-1966 sort of "no CPC in wiring issue" but plastic light switches in plastic back-boxes in trunking wired in singles. The lights...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top