drew35
I carried out the new PIR / condition report today and found a diy bodger had added two way light switching, in flex ,using the cpc as a live, in almost every room!
Now I thought code 2, but I cant find any reference to it in the best practise guide. I know it was once upon a time a done thing to use the cpc as a live in two way light switching, but this has been done recently.
I was sure there was a regulation stating that a cpc can never be used as anything but, even if it was sleeved? I can't find it except for single core reference.
411.3.1.1 A cpc shall be run to, and terminated at each point in wiring, and at each accessory.
514.3.2 Every core of a cable shall be identified at its terminations and preferably throughout its length. Sleeves for identification should comply with...
514.4.2 "SINGLE CORE CABLES" that are coloured green and yellow throughout there length shall only be used as cpc and not over marked at their terminations.
But 411.3.1.1 demands an earth anyway so its still wrong even if it were sleeved? I'm trying to recommend the best fix, without destroying every other wall and rewiring, all I can think of is to convert to one way switching with an earth? Although you can have a lighting circuit without a cpc as long as you comply with all the requirements, so do I put a sticker on the consumer unit saying the lighting circuit has no cpc and then sleeve all the live cpc's brown at each termination?
Now I thought code 2, but I cant find any reference to it in the best practise guide. I know it was once upon a time a done thing to use the cpc as a live in two way light switching, but this has been done recently.
I was sure there was a regulation stating that a cpc can never be used as anything but, even if it was sleeved? I can't find it except for single core reference.
411.3.1.1 A cpc shall be run to, and terminated at each point in wiring, and at each accessory.
514.3.2 Every core of a cable shall be identified at its terminations and preferably throughout its length. Sleeves for identification should comply with...
514.4.2 "SINGLE CORE CABLES" that are coloured green and yellow throughout there length shall only be used as cpc and not over marked at their terminations.
But 411.3.1.1 demands an earth anyway so its still wrong even if it were sleeved? I'm trying to recommend the best fix, without destroying every other wall and rewiring, all I can think of is to convert to one way switching with an earth? Although you can have a lighting circuit without a cpc as long as you comply with all the requirements, so do I put a sticker on the consumer unit saying the lighting circuit has no cpc and then sleeve all the live cpc's brown at each termination?