  1. KeenPensioner
    Offline

    KeenPensioner Never stop learning

    Location:
    Scotland
    HI, as my profile says I'm not a sparky and know my limitations. I'm trying to learn (for the sake of it only as I'll never do it) what tests for "Ring Final Circuits" are. I understand how the Tests 1, 2 and 3 are done but in one of the videos I watched the presenter (John Ward) mentions a "crossover" see image and says that this "could lead the current being shared in an undesirable fashion. I don't understand that.
    ring_main_crossover.jpg
     
  2. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    That single piece of cable in the ring cannot carry the full current on its own as much as the "doubled up cable" effect of the ring.
     
  3. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    The ring is a bit of an historic artefact, but a good one in my view. With the middle cross over it is no longer possible to perform a single test end to end. It doesn't improve the current capacity but it does make it much harder to test. My quick thought is it won't ruin the current handling capacity of the ring, but it's not the construction method shown in Appendix 14 of BS7671.
     
    • Agree Agree x 1
  4. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Actually thinking about it I retract my previous statement. Pretty stupid really.
     
  5. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    It's not done strictly in accordance with the good book, but there are worse arrangements!

    The major issue is that, when you do testing on a ring final, you crodd connect the conductors in a sort of figure of 8 arrangement. Then you test at each socket and check the R1+R2 resistance. In a properly installed ring final, the R1+R2 at each socket should be more or less identical.

    The circuit would fail this test because of the the 'lollypop' arrangement in your post.

    Learn more about this test HERE

    Or, if you love John Ward
     
  6. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    It’s really too complicated to explain.
    Also your diagram is not ideal.
    Having a bridge reduces the resistance, so that more current can flow along one leg of the ring.
    Current that should be in one leg gets diverted to the other leg which could result in the other leg being overloaded.
     
    • Agree Agree x 3
    • Like Like x 1
    • Friendly Friendly x 1
  7. HandySparks
    Offline

    HandySparks Forum Mentor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    Although I think you'd be hard pushed to find a case where an overload has actually occurred due to a link in a ring.
     
    • Agree Agree x 1
  8. wirepuller
    Online

    wirepuller Forum Mentor

    Location:
    south uk
    TBH I cant really recall any damage to cables on any of the hundreds of incorrectly wired rings I've come across over the years. In fact in the domestic sector it's pretty rare to find a correctly wired ring unless the house is fairly recent. The one I'm rewiring at the moment has spurs off spurs off spurs in the kitchen (now ripped out), no sign of thermal damage at all.
     
    • Agree Agree x 3
    • Dumb Dumb x 2
    • Like Like x 1
  9. kingeri
    Offline

    kingeri Electrician's Arms

    Location:
    Yorkshire
    I think in reality it's highly unlikely that an incorrectly wired ring in a domestic setting would ever see high enough loading of sufficient duration to actually cause any cable damage. Seen a fair few 2.5mm^2 and even a few 1.5mm^2 radials on 30A/32A OCPDs and don't recall seeing any evidence of overload damage. Obviously, it's not good though!
     
    • Like Like x 1
  10. wirepuller
    Online

    wirepuller Forum Mentor

    Location:
    south uk
    Yayyy! I got a dumb!
     
    • Like Like x 1
    • Dumb Dumb x 1
  11. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    I get them every so often.
     
  12. kingeri
    Offline

    kingeri Electrician's Arms

    Location:
    Yorkshire
    I can't see why though!
     
  13. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    I wouldn’t worry about it. Check out the profile of who gave you the rating!...
    Only one post since 2012, and two dumb ratings:rolleyes:
    I’ve reset the balance for you:)
     
    • Dumb Dumb x 1
  14. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    It's amazing in some respects, you answer a post get, say 3 likes and a couple of agrees and 1 Dumb, that's like saying all the likes and agrees are dumb as well, yes I always check the profile, some are genuine,most are as you say TTC
     
    • Agree Agree x 1
  15. Upton Sparks
    Offline

    Upton Sparks Regular EF Member

    Location:
    London
    Business Name:
    Kilowatt Electricals Ltd
    Bit Harsh I thought as well.
     
Loading...
Similar Threads - Crossover ring circuit Forum Date
2357 wont include 17th or 18th due to crossover? Electrical Course Trainees Only Sep 18, 2018
HELP 3 phase masonary saw wiring Industrial Electrician Talk Today at 3:48 PM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job