im changing over the old danfoss 103 mechanical timer over to the danfoss FP75 programmer. It is a combi boiler so hot water side wont be used just wanted to check on wiring. The connections are

103 timer common terminal 3 linked to live
'on' terminal 1

FP75 programmer CH on terminal 4
CH off terminal 2

just to check where does cable on timer 103 terminal 1 'on' marked go on the programmer ?? CH on or off??
 
This programmer may not be suitable, as it has no dry relay contacts. The fp75 has only switch live outputs for CH and HW
 
Connect it to terminal 4 CH on

Good tip on damaging his boiler......A combi requires dry contacts as already stated. Lee sparks has posted 2 diagrams, one for volt free timer (which is required) and one for the Danfross fp75 which has switch live. (which will not work)
 
Good tip on damaging his boiler......A combi requires dry contacts as already stated. Lee sparks has posted 2 diagrams, one for volt free timer (which is required) and one for the Danfross fp75 which has switch live. (which will not work)

But the OP states that the live is linked to the common of the volt free switch on the existing programmer
 
Good tip on damaging his boiler......A combi requires dry contacts as already stated. Lee sparks has posted 2 diagrams, one for volt free timer (which is required) and one for the Danfross fp75 which has switch live. (which will not work)
I don't know what you mean by "dry contacts" if you mean volt free then the OP already said that live was linked to common on the 103 which means the boiler is mains switched.
So not likely to damage the boiler at all!
 
I don`t know any combi which works on switch live, all I seen are volt free switching to timer then stat.
The op states this is a timer he has not what was fitted, so link was on backplate
 
Last edited:
I don`t know any combi which works on switch live, all I seen are volt free switching to timer then stat.
The op states this is a timer he has not what was fitted, so link was on backplate

Worcester Bosch combi's all have a 240V switched live for external controls.

The OP states he has an old danfoss 103 in which the L has been linked to common which he is replacing with the new programmer.
 
Most do Vailant, Worcester, Baxi, Potterton and Glow Worm are the most common ones I wire for BG and all these have switched lives.
 
The 1st pic I posted is for the danfoss 103 the second is for the danfoss FP75 which the OP says he's replacing the 103 with.
so if the boiler has a 240v switched live which it must if Live and 3 are linked then on the new programmer number 1 from old time clock will go to number 4 on new programmer.
 
Last edited:
Suggest the op checks this out first against the combi`s manual, to be on the safe side. I don`t want to give out bad info.
 
Last edited:
If the OP could tell us which boiler he has we can confirm this.
But as me, Lee and Dave have all said if live and common are linked on the clock then the boiler is live switched.
 

Reply to Danfoss 103 mechanical timer to FP75 programmer in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
Replies
5
Views
1K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
639
Hi. We are looking at installing a Wiser smart heating system inc. trvs We are currently electric only, with normal rads and a Heatrae sadia...
Replies
8
Views
2K
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K
A question if I may before I dive in. I have an old gravity fed CH system which thanks to members here in the past - works very well. It has a...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock