Search the forum,

Discuss dasy chaining boards ? in the UK Electrical Forum area at ElectriciansForums.net

F

falcon0310

a big hotel group has asked us that they want 2 way dbs in each bedroom feeding one socket and 5 lights all led fittings, but they want the supplies to boards daisy chained from 10mm t&e or swa feeding 4 rooms per circuit. the only way ive ever done this is sub per board, but cant find anything in the regs, as so many jobs this is to save money but surely its not right
 
Not sure what you mean, 4 rooms fed from 1 number 10mm T&E? 1 D/B in each room? so in effect you will have a radial of 4 x 10mm connection points?
 
I'd want a section board on each floor feeding a room board off a 32A mcb. 4mm 3 core SWA to each

How you have described has a couple of issues, you would run the risk of overload and good luck trying to to terminate 2x 10mm SWA in a 2 way DB

Also nuisance tripping is a big problem, supply mcb trips under overload and you plunge 4 rooms into the 12th century.
 
they be mk sentry boards so that's not problem, only feeding 2 rcbos so that's why said 2 way but say use 8 mod with blanks be used, load be one double and say 300w max lighting
 
one db per room and will be supplied via 10mm looped in and out to feed other boards if that makes sence

As Hightower says good luck trying to terminate 2 10mm SWAs into a 2 way board, his suggestion has merit
 
What do your diversity calcs say ?
As hightower says, nuisance tripping is gonna be your get out here. Reg 314.1, division of circuits.
 
Falcon I'm not trying to pick holes in your design. If they want db's in each room then I really wouldn't be daisy chaining boards, I assume that the 10mm radial would be fed from a local board, so what happens when this circuit trips with overload because you have people like my lads who bring all sorts of equipment into hotel rooms.

Then the residents will have to wait till the night manager trips it back in and hope there's no fault.

Get a short circuit fault and the hotel has got 4 rooms off for maintenance
 
What do your diversity calcs say ?
As hightower says, nuisance tripping is gonna be your get out here. Reg 314.1, division of circuits.
I know what your saying, and even if goes on 40a c type at main db riser, as its hotel the room boards could feed the double socket on 10a, rcbo to stop this, they do not want geasts to plugin heaters and so on, but you are going get somone plugin hairdriers that could trip the 10a out
 
Falcon I'm not trying to pick holes in your design. If they want db's in each room then I really wouldn't be daisy chaining boards, I assume that the 10mm radial would be fed from a local board, so what happens when this circuit trips with overload because you have people like my lads who bring all sorts of equipment into hotel rooms.

Then the residents will have to wait till the night manager trips it back in and hope there's no fault.


Get a short circuit fault and the hotel has got 4 rooms off for maintenance

Hightower as got it bang on , why are they asking for this, how many room's in this hotel.
I seriously think a better design is needed here.
And i just used my 800th post for this, so tell them they need to listen.
 
Falcon I'm not trying to pick holes in your design. If they want db's in each room then I really wouldn't be daisy chaining boards, I assume that the 10mm radial would be fed from a local board, so what happens when this circuit trips with overload because you have people like my lads who bring all sorts of equipment into hotel rooms.

Then the residents will have to wait till the night manager trips it back in and hope there's no fault.

Get a short circuit fault and the hotel has got 4 rooms off for maintenance
this is not my idea its there's !!!!!!!!!!!! save money on cable we all know that you should have one supply per board
 
I know what your saying, and even if goes on 40a c type at main db riser, as its hotel the room boards could feed the double socket on 10a, rcbo to stop this, they do not want geasts to plugin heaters and so on, but you are going get somone plugin hairdriers that could trip the 10a out

What kind of customer's are staying in this hotel :thinking:
 
Stand up to them and tell them it's a bad design, as for installing an 8 module board, well that's just plain daft
 
the hotel has 150 rooms, with so called electrical expert, that wants board per room that does make sense so only board in the room can trip out, so I agree but never have I looped board before, there other idea I cant even say as worse
 
this is not my idea its there's !!!!!!!!!!!! save money on cable we all know that you should have one supply per board

That's why I'd go back to them with a written summary outlining why it shouldn't be done and staying reg numbers!.

Also testing and certificating this would be a pain.

Multiple 10mm radials is not going to be all that much cheaper than individual 4mm's

Could even look to put multiple section boards on the floors if it's a big place.
 
the hotel has 150 rooms, with so called electrical expert, that wants board per room that does make sense so only board in the room can trip out, so I agree but never have I looped board before, there other idea I cant even say as worse

Oh go on, you need to tell us now lol.

It wouldn't be selsdon park would it ?
 
the hotel has 150 rooms, with so called electrical expert, that wants board per room that does make sense so only board in the room can trip out, so I agree but never have I looped board before, there other idea I cant even say as worse

Falcon you know this is not the way to do the job as you have said, so you need to sit them down and explain it on a level they will understand. If you go with this design believe me you will be getting called back constantly, and they won't want to pay because they will blame you.
Regarding the " Electrical expert my advice would be take him to the top floor of the hotel, open a window and throw him out.
 
Falcon you know this is not the way to do the job as you have said, so you need to sit them down and explain it on a level they will understand. If you go with this design believe me you will be getting called back constantly, and they won't want topay because they will blame you.
Regarding the " Electrical expert my advice would be tae him to the top floor of the hotl, open a window and throw him out.
the widows are nailed shut sir ! gas costs money to heat hotels so I was told
 
Falcon you know this is not the way to do the job as you have said, so you need to sit them down and explain it on a level they will understand. If you go with this design believe me you will be getting called back constantly, and they won't want to pay because they will blame you.
Regarding the " Electrical expert my advice would be take him to the top floor of the hotel, open a window and throw him out.

Explain to the client that if the SWA ever has a fault then they are looking at 4 rooms of for maintainence until it can be sorted!

Hotel management dislike nowt more than having rooms off!
 
the widows are nailed shut sir ! gas costs money to heat hotels so I was told

The hotel is not called Fawlty tower's by any chance. And the owner answer's to the name of Basil
 
As soon as it all goes tats up you'll be in the firing line so my suggestion if you do it is to get it in writing first. Or like me if not happy walk away and let some other nugget play the bodge game
 
As soon as it all goes tats up you'll be in the firing line so my suggestion if you do it is to get it in writing first. Or like me if not happy walk away and let some other nugget play the bodge game
I agree, staying at home to earn no money is better than going to work and earn no money.
 
I agree, staying at home to earn no money is better than going to work and earn no money.

Yep there'salways jeremy kyle to watch if ya get bored
 
As soon as it all goes tats up you'll be in the firing line so my suggestion if you do it is to get it in writing first. Or like me if not happy walk away and let some other nugget play the bodge game

Great advice. If you can't talk someone into doing things right, then they aren't worthy of your services. They will find some other muppet eventually, but some people just don't care.
 
Great advice. If you can't talk someone into doing things right, then they aren't worthy of your services. They will find some other muppet eventually, but some people just don't care.
they also want 35 rooms done in 3 weeks so that's total floor 35 boards, sub mains and re wire corridor's,
 

Reply to dasy chaining boards ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
686
I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps. The distribution...
Replies
26
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K
Hi guys looking for some guidance ,i am assisting with the renovation of an old building that contains a commercial kitchen and restaurant the...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top