Discuss Dead RCBO? or Brain fart in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
This could just be a Friday evening brain fart after a long week but,
Got home tonight to find the downstairs lighting cicuit has tripped, tried to reset the RCBO and it blew again straight away. IR tested the circuit, all fine.
While the circuit was disconnected I tried turning the rcbo on and re-energising the board and RCBO trips again. I took the neutral flying lead out of the neutral bar and RCBO doesn't trip. Like I say, could be my brain isn't functioning correctly and I'm missing something obvious or has the RCBO failed? Any thoughts appreciated.
 
This could just be a Friday evening brain fart after a long week but,
Got home tonight to find the downstairs lighting cicuit has tripped, tried to reset the RCBO and it blew again straight away. IR tested the circuit, all fine.
While the circuit was disconnected I tried turning the rcbo on and re-energising the board and RCBO trips again. I took the neutral flying lead out of the neutral bar and RCBO doesn't trip. Like I say, could be my brain isn't functioning correctly and I'm missing something obvious or has the RCBO failed? Any thoughts appreciated.
What IR tests did you carry out L-E, N-E, L-N? and what were the results?were all of the circuit under test dissed from the CU?
 
Same as Wirepuller, if it trips with circuit live and neutral disconnected replace it with a new one.
 
I had a faulty MCB the other day where there had been a L-N short in a pull cord and they had tried turning it back on so the KA had got the better of it.
 
Sounds like the rcbo if it does it without the circuit connected, as already stated. Have you tried connecting it to another rcbo in the board.
 
It should be replaceable under warranty and I think Hager would be interested in its return.
 
I thought I had a "soft" Hager RCD on a recent job.
I had added downlights in a kitchen, under cabinet lights and kickboard lights and changed the switch to a 3 gang.
Every so often the switch for the cabinet lights tripped the RCD. Not every time, and it had all tested ok. I thought initially it was either the transformers I put in, the LED lamps or a knackered RCD
It gradually became every time I used the switch... on or off. IR now showed a short between neutral and earth. Worked my way from the board disconnecting neutrals and testing until I found the cable with the problem;- switch wire to outside light at the front door. Luckily easy to replace.
How come a neutral to earth fault only affects the RCD when I turn on a switch at the other end of the house?
 
Maybe the switch was slow to operate and the arcing caused some earth leakage via the surge arrestors in the driver or transformer.
 

Reply to Dead RCBO? or Brain fart in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
479
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
741
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock