Hi All,

I'm trying to learn about discrimination and I came accross the LSIG characteristics of an Air Circuit Breaker. Howecerm there is something I really cannot understand about the Tsd. What's the difference between ON and OFF in the intervention? Thank you in advance
 

Attachments

  • Screenshot_20211228-100012_Chrome.jpg
    98.5 KB · Views: 6
To achieve selectivity with down-stream breakers you need both a higher trip current for the thermal curve aspect, but you also need some form of time delay on very high currents so if the fault goes above the thermal overload curve in to the magnetic 'instant' trip region the upstream device holds on for long enough that the downstream one can clear if possible.

So the larger breakers such as ACB and some MCCB (category B) often have a two-stage high current trip. There is often a fixed magnetic point where the breaker goes 'instantly' and tries to limit the fault energy, but below that you often have an electronic adjustable trip point in both short-time delay and related short-time trip current to allow some coordinated selectivity with those further down-stream.

However, having a fixed square curve for trip current and time is not necessarily the best way of getting good enough selectivity while still protecting the supply and cables, etc. So some devices have two curve options, a simple "step" mode where above Isd it holds for Tsd, and a I2t mode where there is a slope approximating the constant I2t sort of region that you might optimise for cable protection, etc. Here is a good overview but usually you need to check with the manufacturer's specifications as they are not all standard like MCB are:
 
To achieve selectivity with down-stream breakers you need both a higher trip current for the thermal curve aspect, but you also need some form of time delay on very high currents so if the fault goes above the thermal overload curve in to the magnetic 'instant' trip region the upstream device holds on for long enough that the downstream one can clear if possible.

So the larger breakers such as ACB and some MCCB (category B) often have a two-stage high current trip. There is often a fixed magnetic point where the breaker goes 'instantly' and tries to limit the fault energy, but below that you often have an electronic adjustable trip point in both short-time delay and related short-time trip current to allow some coordinated selectivity with those further down-stream.

However, having a fixed square curve for trip current and time is not necessarily the best way of getting good enough selectivity while still protecting the supply and cables, etc. So some devices have two curve options, a simple "step" mode where above Isd it holds for Tsd, and a I2t mode where there is a slope approximating the constant I2t sort of region that you might optimise for cable protection, etc. Here is a good overview but usually you need to check with the manufacturer's specifications as they are not all standard like MCB are:
Thank you for your reply.
Honestly? Your explanation is good but my level does not allow me to understand in full. I will have to process and further dig.

I will have a look at your link and get back to you.
Cheers
 
This gives a very basic overview of how two protective device curves have to be spaced in current and/or time to allow selectivity:

However, for real world products like ACB and electronic MCCB it is far more complex. This PDF paper covers just the ABB products, but shows some of the features and gives you some insight in to just how complicated it can become in large systems:

In most cases you just look at the manufacturer's selectivity tables to see what is going to work (fuse-MCB, MCCB-MCB, MCB-MCB, etc) but some companies have software tools to give the answers. Schneider has one but you have to register, also it only works for certain combinations of their products :( This rather bizare link works for me, seems they don't make it too easy to find:


(Also it is broken by ad-blockers, not even a message to say so, so really pretty crap web design)
 

Reply to Difference between ON and OFF intervention in the tsd of an ACB trip module in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
464
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
287
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock