Anna Rack

I've got 3 under cabinet lights which are 12v 10w each, supplied by an electronic transformer, 10-60w.

I would like to add a dimmer, and wondered if this is possible and what type would be suitable.

There are no markings on the transformer indicating whether it is dimmable or not.

Thanks in advance.
 
It will be the switch that need to do the dimming, there are transformers that will work with a dimmer, but not all, you will need to look at the specification of the transformer, and then there are the lamps to consider, these also need to be of the dimmable type, get any of this wrong and you will have a nightmare with flickering, buzzing, blown lamps and transformers etc.

To be fair mate, i think you are wasting both your time and money, this stuff gets used once or twice, the novelty wears off and the get left either fully on or turned off. But it is your choice.

If you retrofit a dimmer switch, you will need a 35mm deep back box, so be prepared to dig the wall out, don't try to cram the dimmer into a 25mm or worse still a 16mm, or you will have some real problems if you do.

Cheers…………..Howard
 
as above ^^^^. pointless excercise in a kitchen. the lights are there to see which finger you're cutting, not for mood lighting.
 
Thanks for the replies, left things as they are with just a normal switch.
 

Reply to Dimmer for electronic transformer in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I purchased a house that has a really cool 12v halogen setup where two wires are suspended across the ceiling in two different locations, and each...
Replies
9
Views
909
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Thanks in advance for any help. I've got an old lamp (inherited from my gran) that I want to add a switch to and lengthen the wire. It doesn't...
Replies
4
Views
1K
I have installed a number of 120v smart light switches and smart bulbs which I have set up on a schedule via an app. I would like to add another...
Replies
1
Views
1K
The house I've just moved into is fitted with the light switches shown in the pics. They are fitted to each bedroom and the landing. The landing...
Replies
9
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock