- Reaction score
- 17,087
I'm having a bit of a brain fog moment (changing medication is such good fun!) and am looking for confirmation that I'm either right or talking nonsense.
I've been to a job to have a look at why a set of ammeters aren't working, I've established the main reason they don't work is that someone has disconnected them, pretty simple so far.
But the CT's which fed these ammeters have been disconnected and left open-circuit, I'm pretty damned sure they should have been either shorted out or removed and that's what I'm looking for confirmation of.
And the second question how would you code this on an EICR? I would give it a C2 as it is behind a panel on a switchboard but is a set of terminals with, potentially, a 4 figure voltage between them.
I've been to a job to have a look at why a set of ammeters aren't working, I've established the main reason they don't work is that someone has disconnected them, pretty simple so far.
But the CT's which fed these ammeters have been disconnected and left open-circuit, I'm pretty damned sure they should have been either shorted out or removed and that's what I'm looking for confirmation of.
And the second question how would you code this on an EICR? I would give it a C2 as it is behind a panel on a switchboard but is a set of terminals with, potentially, a 4 figure voltage between them.