Discuss Disconnected Neutal Still Showing Connection To Neutral (somewhere) in the UK Electrical Forum area at ElectriciansForums.net

J.A.J.

-
Reaction score
3
hi i am replacing a consumer unit over and came across a strange problem with the neutrals when i isolated the old consumer unit. When isolated from supply im still getting 240v between incoming live and out going neutral. I have disconnected all neutrals from block (which clears it from outgoing at main switch) but all circuit neutrals now show still connected to neutral (somewhere). I was thinking it was the obvious old hookey supply, live chopped away but neutral still connected,but it still dosent make sense. Hope someone here can shed a little light on the subject please. Thanks in advance J.A.J
 
So long as there is any earth reference (or any voltage reference) on the neutral circuit, even fairly slight, then the incoming live (which is still live presumably) at 230V will show that there is 230V between it and the neutral.
It would only be if the entire circuit were totally "floating" that the voltage would not register.
 
Hi thanks for the reply , I have supply totally disconnect from meter

Like Richard said, if there is anything still connected somewhere on the installation and it has some possible earth path via the neutral, then it is possible still show a voltage to live. (obviously discounting a fault, or some unknown factor) If all neutrals are disconnected at both ends and are floating then I would say this indicates an earth/neutral fault on a circuit.
 
If there's an earth/ neutral fault on any of they circuits ,surely it would trip the rcd
He is installing a new CU. maybe the old CU (fuseboard) does not have an RCD> so it won't trip.

As above, needs IR test on the circuits, if there's an E>N fault, somewhere then there may be a path to earth through copper pipes, etc..
 
If there's an earth/ neutral fault on any of they circuits ,surely it would trip the rcd
Sorry, with you not mentioning whether or not the existing installation was RCD protected I just assumed that was possibly the reason for the swap of the CCU. Though you may still have a neutral to earth path that doesn't trip the RCD, where any leakage current is less than 30mA.
 
It's a puzzler, but I'm liking Midwest's thought of an IR problem, otherwise as JAJ says the RCD would have been telling us? Cheers, David.
 
Thanks ,I was upgrading from an older (not ancient CU ) which was a split board,the rcd in the existing board didn't trip of either before I disconnected it
 
Sorry, with you not mentioning whether or not the existing installation was RCD protected I just assumed that was possibly the reason for the swap of the CCU. Though you may still have a neutral to earth path that doesn't trip the RCD, where any leakage current is less than 30mA.
If there is a current less than 30mA on more than 1 circuit wouldn't this trip the rcd
 
What do you mean "stop from tripping"
I'm led to believe, if you think of how an RCD works, imbalance between live & neutral, with an earth neutral fault, the fault current in the earth can flow back through the neutral, negating any trip. That's how it was explained to me. But being not expert on the technical bit, however I've had that happen to me.
 
I'm led to believe, if you think of how an RCD works, imbalance between live & neutral, with an earth neutral fault, the fault current in the earth can flow back through the neutral, negating any trip. That's how it was explained to me. But being not expert on the technical bit, however I've had that happen to me.
I believe this can happen on TT systems, for example if you have a neutral/earth fault, the current flow will take the path of least resistance and this is likely to be the neutral path and not earth due to the electrode impedance, hence the rcd will not sense an inbalance to make it trip.
 
I still dont get it. A fault current would still cause an imbalance and trip the rcd. Daz
 

Reply to Disconnected Neutal Still Showing Connection To Neutral (somewhere) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
659
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock