Discuss Distribution Circuit in the UK Electrical Forum area at ElectriciansForums.net

K

Kingston555

Hi all, I want to feed a small 2-way distribution board from a spare way in the main consumer unit.
The new 2-way board will have either two B6 MCBs for separate lighting circuits, or there'll be one lighting circuit and a separate socket circuit. What sized breaker do I need to use in the spare way in the main consumer unit and what csa for the feed cable from the main consumer unit to the 2-way board. The 2-way board has a 63 Amp double pole main switch. Thanks!
 
If you are enquiring as to what rating of device will provide Selectivity (discrimination), the simple answer is no two BS EN 60898 circuit breakers will discriminate with each other under fault conditions.
 
Why are you adding another board?

If it's just lighting, can you put it all on one circuit? If power and lighting, can you run a power circuit with a fused connection unit for the lights?
 
Hi all, I want to feed a small 2-way distribution board from a spare way in the main consumer unit.
The new 2-way board will have either two B6 MCBs for separate lighting circuits, or there'll be one lighting circuit and a separate socket circuit. What sized breaker do I need to use in the spare way in the main consumer unit and what csa for the feed cable from the main consumer unit to the 2-way board. The 2-way board has a 63 Amp double pole main switch. Thanks!

Where is the new DB going to be sited? How far away?

Whats the Ib?


You need to provide more info to be honest. This is pretty standard stuff. :)
 
Good job I checked your profile mate I was about to go into print with some abuse, but you're a Trainee so all is forgiven, just take note of the advice already given it's sound advice from knowledgeable people.
 

Reply to Distribution Circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
758
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock