GBDamo

-
Esteemed
Arms
Reaction score
3,010
Doesn't really matter as I have spare capacity and VD well within limits but I have a sub board fed with 10mm SWA.The sub supplies a 32A socket ring, 6A lights and a 20A radial to a 16A switched commando serving a 10A fixed load motor. All single phase 230V.

Which would you calculate the diversity based on, from OSG table A2;-

1, count (based on 4) 100% of the largest motor, therefore 10A. As there is a 10A motor on the socket at present.

2, count (based on 9) it as a socket radial and use 40%, therefore 4A. Anything could be plugged in in all reality.

3, count (based on 4) 100% of the largest load possible to go on the commando socket, therefore 16A as a larger motor could be feasibly be plugged in.

In this case a 6mm SWA was very borderline to begin with so a 10mm will be used and gives a lot of wiggle room but just wondering how people would approach the situation if things were a bit tighter.

???
 

Reply to Diversity Question...... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
703
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Got an issue with gym equipment. ( I keep telling my wife I’m going to the gym, but she doesn’t believe me!) The gym owner says the circuit for...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock