Search the forum,

Discuss DIY Installation Help - I'm looking to install 2x 5ft LED batten lights (45w) along with a wall switch and 2x double wall sockets in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

RCX2020

DIY
Reaction score
3
Afternoon all,

Just bought a house with a remote garage, said garage has no power or lighting.

I'm hoping to use the garage as a gym and some storage so I'm looking to install 2x 5ft LED batten lights (45w) along with a wall switch and 2x double wall sockets.

Found this off-grid solar kit and after speaking to the company about my usage they said this kit should be perfect. 600W, 12V, 0.57kWh Deluxe Off-Grid Solar Kit - Sunstore Solar - https://www.sunstore.co.uk/product/600w-12v-0-57kwh-deluxe-off-grid-solar-kit/

What I need help with is everything else I'd need to get the job done, and if anyone can help, maybe a wiring diagram for the load where it connects to the inverter/solar controller?

Any help would be greatly appreciated.
Rich
 
I would like to assume that it would come with installation instructions and a list of any additional installation materials required.
 
I would like to assume that it would come with installation instructions and a list of any additional installation materials required.

Hi Strima,

Yea I'd imagine it has all the installation requirements listed to install. But I doubt very much it will give me a list of items required to split the wiring etc. in order to install the sockets and overhead lights?

Do I need an RDC, junction boxes, any particular wire I should try use?
 
if you're spending £1200+ on that gear, surely it's not unreasonable to pay an electrician a fe hundred to install it and associated equipment.
 
if you're spending £1200+ on that gear, surely it's not unreasonable to pay an electrician a fe hundred to install it and associated equipment.

I have looked into, struggling to find an electrician in my area that can install solar. Maybe I'm not looking hard enough but tried 3 places locally, and none of them are interested.
 
is wiltshire any where near Bath? couple of members there.
 
I have looked into, struggling to find an electrician in my area that can install solar. Maybe I'm not looking hard enough but tried 3 places locally, and none of them are interested.

Have you told them it's just a basic kit, rather than a fully installed system? Any electrician should be able to install that.
 
How remote is the garage? It might be more cost effective and reliable to get a supply from the house and give you more flexibility in what electrical equipment you can use in the garage.
 
Out of interest, what will you be plugging into the 2 double sockets?

As I'll be using the garage as a gym: a fan, a treadmill, an exercise bike, ipod dock.

The bike & treadmill will only in use for a max of an hour per day. Fan will only be on in summer months for a max of 2 hours per day. ipod dock will be on for around 2 hours per day maximum.

Then just overhead lights on whilst in the garage, but obviously not through the sockets.
 
As I'll be using the garage as a gym: a fan, a treadmill, an exercise bike, ipod dock.

The bike & treadmill will only in use for a max of an hour per day. Fan will only be on in summer months for a max of 2 hours per day. ipod dock will be on for around 2 hours per day maximum.

Then just overhead lights on whilst in the garage, but obviously not through the sockets.

So no heater during winter then?
 
I'd have to cross my neighbours land unfotunately, so cost & permission wise it would be too much hassle

That does makes things more awkward. I think I'd be worried that the limitations a small solar set up would impose would become frustrating though. You may not be able to use the gym when you want to in the winter or on a cloudy morning or evening in the summer. As Spoon says, you may find yourself needing a heater in the depths of winter.
 
That does makes things more awkward. I think I'd be worried that the limitations a small solar set up would impose would become frustrating though. You may not be able to use the gym when you want to in the winter or on a cloudy morning or evening in the summer. As Spoon says, you may find yourself needing a heater in the depths of winter.
Get a cheap calor gas one ? Would be far easier than using the power. And of course the winter months will give very little solar anyway...
 
Really roughly drawn and definitely not to scale!

But this is the plan I have for installation so far.. Do I need to put an RCD in anywhere or have I gone wrong anywhere?

Any helpful comments would be greatly appreciated.

1592398973078.png
 
Probably not as get too hot, but if I did then it would be one of those tiny little floor ones, and would prob only be on for 10-15 minutes a day.

The physical size of the heater doesn't dictate its power rating, if your solar system is rated at 600W then your heater will need a power rating of less than this.

Do you have the power rating of the treadmill and exercise bike?
[automerge]1592900323[/automerge]
Really roughly drawn and definitely not to scale!

But this is the plan I have for installation so far.. Do I need to put an RCD in anywhere or have I gone wrong anywhere?

Any helpful comments would be greatly appreciated.

View attachment 58902

Assuming the output of the inverter is properly protected for overload and short circuit then there would be no point installing addition fuse or mcb protection.

An RCD will only work if one pole of the output of the inverter is connected to earth permanently and reliably. In my opinion for such a small inverter it would be safe enough, if the installation is designed suitably, not to do this and keep it as an electrically seperate system.
 
The physical size of the heater doesn't dictate its power rating, if your solar system is rated at 600W then your heater will need a power rating of less than this.

Do you have the power rating of the treadmill and exercise bike?
[automerge]1592900323[/automerge]


Assuming the output of the inverter is properly protected for overload and short circuit then there would be no point installing addition fuse or mcb protection.

An RCD will only work if one pole of the output of the inverter is connected to earth permanently and reliably. In my opinion for such a small inverter it would be safe enough, if the installation is designed suitably, not to do this and keep it as an electrically seperate system.

I can find out the power rating for bike later this eve. Just sold the treadmill as it was s***. I may purchase another but for time being I'm going to stick to road running.

From speaking to the company where I plan to purchase the Solar kit from, they have assured me its a very reliable & internally protected inverter so I'm confident it should be fine to run the lights/ipod dock safely.
 
Hang on, hang on... but I've just looked up the typical power usage of a treadmill... it's like 1.5kW !

So, throwing some numbers at this... your proposed solution will have an AGM battery rated at 95Ah... giving a usable capacity of about 30Ah, being 360Wh... so assuming that no other power is used... just the treadmill... a fully charged battery will run the treadmill for about 24 minutes...

Adding in the fan (30W), the lights (45W), iPod speakers (10W)... I reckon you'll be lucky to get 20 mins of workout time...

All of this assumes that you're not doing it at midday with the sun blasting those panels of course.

Solution re-think needed I reckon... more AGM batteries ? Lifepo4 ? Portable Lifepo4 solution ?
 
Hang on, hang on... but I've just looked up the typical power usage of a treadmill... it's like 1.5kW !

So, throwing some numbers at this... your proposed solution will have an AGM battery rated at 95Ah... giving a usable capacity of about 30Ah, being 360Wh... so assuming that no other power is used... just the treadmill... a fully charged battery will run the treadmill for about 24 minutes...

Adding in the fan (30W), the lights (45W), iPod speakers (10W)... I reckon you'll be lucky to get 20 mins of workout time...

All of this assumes that you're not doing it at midday with the sun blasting those panels of course.

Solution re-think needed I reckon... more AGM batteries ? Lifepo4 ? Portable Lifepo4 solution ?

Ah shoot, sorry mate! I'll base the 1.5kW for the bike instead ;)

I shall be ringing that company again then, and see what they can suggest, as I usually spend 2 hours a night in there. + winter months won't yield as much charge.
 
Yea looks like I'll be needing the 1200w system:

This then allows for a max peak draw of 1200w so I could install electric garage door If I choose to to run through the system as well - but only if I do away with the exercise bike - which I think I will now consider keeping in the house to make life easier & cheaper.
 
Yea looks like I'll be needing the 1200w system:

This then allows for a max peak draw of 1200w so I could install electric garage door If I choose to to run through the system as well - but only if I do away with the exercise bike - which I think I will now consider keeping in the house to make life easier & cheaper.

For an off-grid install I would make sure the garage door can be manually opened on case of power failure. Unless there's a side door.
 
For an off-grid install I would make sure the garage door can be manually opened on case of power failure. Unless there's a side door.

Oh yes 100%. The last electric door we had on our previous house had no other mean of entrance, so they installed a barrel that could be removed with a key, then a manual wind handle could be inserted.
 
I can find out the power rating for bike later this eve. Just sold the treadmill as it was s***. I may purchase another but for time being I'm going to stick to road running.

From speaking to the company where I plan to purchase the Solar kit from, they have assured me its a very reliable & internally protected inverter so I'm confident it should be fine to run the lights/ipod dock safely.

It will be fine to run the lights and an ipod Dock, they take very little current.

Be wary of salespeoples assurances, they will say anything to get your money.

Hang on, hang on... but I've just looked up the typical power usage of a treadmill... it's like 1.5kW !

So, throwing some numbers at this... your proposed solution will have an AGM battery rated at 95Ah... giving a usable capacity of about 30Ah, being 360Wh... so assuming that no other power is used... just the treadmill... a fully charged battery will run the treadmill for about 24 minutes...

Adding in the fan (30W), the lights (45W), iPod speakers (10W)... I reckon you'll be lucky to get 20 mins of workout time...

All of this assumes that you're not doing it at midday with the sun blasting those panels of course.

Solution re-think needed I reckon... more AGM batteries ? Lifepo4 ? Portable Lifepo4 solution ?

You seem to have missed out the 600W output of the inverter in your calculations, so actually it won't run a 1.5kW load at all, it will trip out on overload (hopefully, or burn out if not)
 
Yea looks like I'll be needing the 1200w system:

This then allows for a max peak draw of 1200w so I could install electric garage door If I choose to to run through the system as well - but only if I do away with the exercise bike - which I think I will now consider keeping in the house to make life easier & cheaper.

A garage door opener usually only draws a small amount of power and won't be a problem as long as it isn't operating at the same time as something that uses a lot of power.

When working out how much power you need you shouldn't just add up everything you will use, you need to consider what will be using power at the same time and what will be using power seperately. You aren't going to have the garage door moving whilst both exercise machines are running, the heater is on and the fan is on!
 
A garage door opener usually only draws a small amount of power and won't be a problem as long as it isn't operating at the same time as something that uses a lot of power.

When working out how much power you need you shouldn't just add up everything you will use, you need to consider what will be using power at the same time and what will be using power seperately. You aren't going to have the garage door moving whilst both exercise machines are running, the heater is on and the fan is on!

Thanks davesparks,

That has actually helped my understanding a little more. I'm now feeling even more confident about installing the kit from having theses discussions.
[automerge]1592988373[/automerge]
what you need is an excercise bike in there as well. get the wife to act the part of Mr. Motivator while you run on your teadmill:
View: https://www.------------/watch/?v=186218128962607
HA! I can see my missus saying 2 words to that, first one beginning with F, second word is off.
 
Last edited:

Reply to DIY Installation Help - I'm looking to install 2x 5ft LED batten lights (45w) along with a wall switch and 2x double wall sockets in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I have been following this forum over a number of years reading endless discussions and picking up things along the way. I am a JIB gold...
Replies
9
Views
4K
Dear all - I am looking to install some LED strip lighting (it will be wall-mounted near the ceiling, behind some uplight coving). The plan is to...
Replies
35
Views
7K
Hello, I'm currently installing these LED tube lights in my garage...
Replies
12
Views
22K
Hi Guys, I am currently getting a kitchen overhaul and want to install some unit/kick-board lights. I want to be able to control the unit lights...
Replies
51
Views
5K
Hi Guys, I am currently getting a kitchen overhaul and want to install some unit/kick-board lights. I want to be able to control the unit lights...
Replies
100
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top