Hi I need some impartial advice about my plastic consumer unit. It is mounted on the wall above some stairs in my flat. I have been told it doesn't meet building regs and must be replaced with a metal one. Would this area count as an escape route? Do I have to change the unit?
Many many thanks for any help at all.
 
The Best Practice Guides No. 4, which covers electrical installation condition reports suggest a classification of C3, improvement recommended... if you only had C3s on a report it would be classed as satisfactory.


Page 16 I thin if you'd like to look it up for yourself.

Yes, it would be a safety improvement, but it is not required. And if someone has told you it's not compliant with building regulations... they are incorrect. It is not compliant with the current edition of the wiring regulations (BS 7671) which is the standards document which defines the standards to which all electrical work in the UK should be carried out.

If we installed a plastic consumer unit in a house today, it would be non-compliant, but as it was installed some time ago, yes it's non-compliant but it's not necessary to remove it if the only reason is 'it's plastic'.

Hope that helps.
 
The Best Practice Guides No. 4, which covers electrical installation condition reports suggest a classification of C3, improvement recommended... if you only had C3s on a report it would be classed as satisfactory.


Page 16 I thin if you'd like to look it up for yourself.

Yes, it would be a safety improvement, but it is not required. And if someone has told you it's not compliant with building regulations... they are incorrect. It is not compliant with the current edition of the wiring regulations (BS 7671) which is the standards document which defines the standards to which all electrical work in the UK should be carried out.

If we installed a plastic consumer unit in a house today, it would be non-compliant, but as it was installed some time ago, yes it's non-compliant but it's not necessary to remove it if the only reason is 'it's plastic'.

Hope that helps.
Thank you so much. My only thought was that the location could be classed as an escape route but I couldn't find anything definitive on it. Your explanation is really helpful. Thanks again ????
 
And to clarify your other question about an escape route... if it's the sole means of exiting the property in an emergency, then yes, it's an escape route.
 
I'll add this... if this has come about as a result of an electrical installation condition report, the classifications are down to the person carrying out the inspection/testing. The Best Practice Guide is just that, a guide.

That being said, personally, if everything else checked out (and there are better reasons to change your consumer unit if you don't already have them, such as RCD protection) I wouldn't classify a plastic consumer unit as a C3 unless it was in the situations listed in the Best Practice Guide. As @mattg4321 this seems to be becoming quite a popular mechanism by which some people are trying to extract work from unsuspecting punters such as yourself.

The sad fact is a lot of people aren't prepared to pay us to do a decent report and thus there are alot of people doing cheap reports with lots of issues on them. If I put my super cynical head on, I suspect they've told the homeowners only they can do the remedial works because they did the report... if you hear this, it's a lie and you should avoid future dealings with the individual concerned. You can have anyone do the remedial works.

If it has come about as a result of an EICR, if you'd like a second (third, fourth, fifth....) opinion, redact any personally identifiable information (names, addresses, report number, signatures etc.) and post it here. We'd be more than happy to give you a more thorough second opinion, but please bear in mind this is ultimately limited as we won't have access to the installation but it can be handy if we spot things that make us think the worst.
 
I have been told it doesn't meet building regs and must be replaced with a metal one.
Ask the person who told you the above, which particular Building Reg it does not comply with.

Do you own and live in this flat or rent it out to someone?
What was the reason for having an Electrical Inspection done, that's now highlighted this, or was there another reason the issue has been raised?

Have any of the other flats been inspected and found to have the same issue?
 
Hi, I have received an EICR with a few observations noted:
PVC consumer unit - C3
RCD main switches are in place however they are type AC and cover a large area of the house meaning they may be vulnerable to saturation from DC voltages - C2
alarm - the MCB is rated too high for the size of the cable - C2
basic insulation is exposed at all spotlight terminations that were checked - C2
there is no surge protection device to the installation - C3 (it doesn't state which device)

We are buying the property, which is 10 years old, and the previous owners have shared the report that has just been completed.
I've read about the PVC consumer unit and think I'll just leave this. I am however unsure of the severity of the other defects listed. Could somebody please advise?
Thank you :)
 
Hi, I have received an EICR with a few observations noted:
PVC consumer unit - C3
RCD main switches are in place however they are type AC and cover a large area of the house meaning they may be vulnerable to saturation from DC voltages - C2
alarm - the MCB is rated too high for the size of the cable - C2
basic insulation is exposed at all spotlight terminations that were checked - C2
there is no surge protection device to the installation - C3 (it doesn't state which device)

We are buying the property, which is 10 years old, and the previous owners have shared the report that has just been completed.
I've read about the PVC consumer unit and think I'll just leave this. I am however unsure of the severity of the other defects listed. Could somebody please advise?
Thank you :)
PVC consumer unit I wouldn't be worrying about.
AC RCDs would be a bone of contention and the most likely way to rectify this is a replacement consumer unit. I would not be losing sleep over it, most people would Code 3 this.
The alarm mcb being too high should be rectified but the likelihood of it causing a major problem is remote, probably an easy cheap fix.
Spotlight terminations need rectifying, cost wise dependant on quantity and if they possibly need replacing to resolve.
Surge protection device, these are generally now fitted to protect any electrical equipment from unforseen surges. Although separate surge protection devices can be fitted a new consumer unit is probably the best option (only one is required). I would not be losing sleep over it.
If you are buying the property these issues shouldn't be of a concern.
 

Reply to Do I have to replace my plastic consumer unit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Doing some work in a commercial restaurant/kitchen the builders had already boarded and plastered the walls meaning my only viable route is to use...
Replies
31
Views
1K
Hi, NAPIT report was carried out due to flood, all kitchen appliances, wall/light switches, fire/heaters etc need replacing. The electrician...
Replies
4
Views
898
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock