Hi

I was wondering if someone could offer some advice?

The business is doing a lot of kitchen and bathrooms and every so often they need a new cooker circuit or extractor fan, FCU for a standalone oven that sort of thing. At present I wire it in test it and then a lad I know comes and test it and signs it off for me but this has become a pain as I have to wait for him and his work load is increasing as is mine.

I've spoken to NAPIT and they have said I can become Part P registered however I have no intention of doing full rewires or changing CU and it seems like a lot of cost and work for something simple like adding a cooker or oven to a CU. If the CU needed upgrading I'd sub it out to an electrician as I just don't have time to do that sort of thing with multiple projects on the go.

Is this really the only way to be able to certify a new circuit apart from BRegs? NAPIT were going on about 3 phase and commercial stuff and that I could change CU and do rewires and I just could not get it through to them that is not what my business does.

Do all kitchen & bathroom fitters become Part P to wire in a circuit?

Many thanks
 
Hi

I was wondering if someone could offer some advice?

The business is doing a lot of kitchen and bathrooms and every so often they need a new cooker circuit or extractor fan, FCU for a standalone oven that sort of thing. At present I wire it in test it and then a lad I know comes and test it and signs it off for me but this has become a pain as I have to wait for him and his work load is increasing as is mine.

I've spoken to NAPIT and they have said I can become Part P registered however I have no intention of doing full rewires or changing CU and it seems like a lot of cost and work for something simple like adding a cooker or oven to a CU. If the CU needed upgrading I'd sub it out to an electrician as I just don't have time to do that sort of thing with multiple projects on the go.

Is this really the only way to be able to certify a new circuit apart from BRegs? NAPIT were going on about 3 phase and commercial stuff and that I could change CU and do rewires and I just could not get it through to them that is not what my business does.

Do all kitchen & bathroom fitters become Part P to wire in a circuit?

Many thanks
Oh my
 
The shortest and no worry way is to use an electrician who is in a CPS scheme. The complications legally and otherwise are too much to go into but trust me when I say it is better to do this. In this way you will avoid any liability for defective electrical work. It may be a pain but it is better to do it properly in the first place than deal with the fallout if it goes wrong. There is lot more then just part p for installing a circuit, not to mention the expensive test gear you need apart from a level 3 electrical qualification.
 
Does your insurance cover you for electrical work?
 
as said above. ^^^^^^.you can certify your work, no problem, but you can't notify it unless you are in a scam such as napit. niceic, elecsa etc. part pee is a joke. a Electrical Trainee wetbehind the ears with little or no practical experience can join a scam and be registered with part pee. but a qualified spark with 20+ years on the tools is penalised for not wanting to have to pay to work.
 
Hi

I was wondering if someone could offer some advice?

The business is doing a lot of kitchen and bathrooms and every so often they need a new cooker circuit or extractor fan, FCU for a standalone oven that sort of thing. At present I wire it in test it and then a lad I know comes and test it and signs it off for me but this has become a pain as I have to wait for him and his work load is increasing as is mine.

I've spoken to NAPIT and they have said I can become Part P registered however I have no intention of doing full rewires or changing CU and it seems like a lot of cost and work for something simple like adding a cooker or oven to a CU. If the CU needed upgrading I'd sub it out to an electrician as I just don't have time to do that sort of thing with multiple projects on the go.

Is this really the only way to be able to certify a new circuit apart from BRegs? NAPIT were going on about 3 phase and commercial stuff and that I could change CU and do rewires and I just could not get it through to them that is not what my business does.

Do all kitchen & bathroom fitters become Part P to wire in a circuit?

Many thanks

Sounds like you have been bodging and old mate down the pub is taking 100 for the cert each time o_O
 
10 out of 10 for asking the question .... there are many kitchen and bathroom fitters around who don't give a monkeys about any building regs ..... So this means, especially in kitchens that Kev the botch artist leaves a trail of mess and when people are spending vast amounts on their refits, not doing the electrics properly is such a poor approach

So if you have the competence, the qualifications and the necessary test equipment etc you should consider it.

Stroma only charge £240 + VAT per year - so not too much.

BUT why don't you get a decent spark involved so that when you need them, they do ALL the electrics .......... anyone asking me to sign off "a n others" work don't get a yes from me.
 
The shortest and no worry way is to use an electrician who is in a CPS scheme. The complications legally and otherwise are too much to go into but trust me when I say it is better to do this. In this way you will avoid any liability for defective electrical work. It may be a pain but it is better to do it properly in the first place than deal with the fallout if it goes wrong. There is lot more then just part p for installing a circuit, not to mention the expensive test gear you need apart from a level 3 electrical qualification.

I have a Megger MFT1721 that I bought when I did my electrical training courses
 
Sounds like you have been bodging and old mate down the pub is taking 100 for the cert each time o_O

Why bodging it? I have the qualifications and experience I calculate the diversity I choose the right cables I comply to the regs, I use the correct tables for the appropriate way it is mounted reducing the amps for the cables for the way it is fitted/depth/insulation, I check continuity, insulation resistance. This is all then rechecked and more when my mate signs it off. Is that bodging it?
 
10 out of 10 for asking the question .... there are many kitchen and bathroom fitters around who don't give a monkeys about any building regs ..... So this means, especially in kitchens that Kev the botch artist leaves a trail of mess and when people are spending vast amounts on their refits, not doing the electrics properly is such a poor approach

So if you have the competence, the qualifications and the necessary test equipment etc you should consider it.

Stroma only charge £240 + VAT per year - so not too much.

BUT why don't you get a decent spark involved so that when you need them, they do ALL the electrics .......... anyone asking me to sign off "a n others" work don't get a yes from me.

Thanks did not think of Stroma. The problem is my mate would do the work but chasing one cable for a cooker when it takes 1/2 an hour to do holds up the tiler who is waiting for the plasterer to finish, who is waiting for a sparkie to turn up and chase and wire one circuit.

When you have multiple jobs on the go its not always practical to have a subcontractor as I did have a spark but if he was booked in to do a quick circuit and got a full days work it would fall by the wayside and hold up my projects and with subbies waiting to get started it did not work well.

Guess the way forward is to get registered

Thanks to everyone for the advice :)
 
Sorry did not realise you had qualies etc. So yeh get part P and BS7671 when the 18th comes out. Then pay for scam scheme I mean. Then you are good to go. I am with Stroma they are thorough on the assesment. If you decide to bite the bullet get back to us for info on the assessment. Good luck.
 
This day and age of accountability and blame when the proverbial hits the fan its a risk putting your name to anything... when all this tower fire fallout happens accountability will go in to overkill with record keeping and risk assessments aplenty

I worked in the offshore industry for over 20 years and everything is RA, TBT, you can't fart without someone signing it off. I ran a team of 30 guys and they would be pressure testing at 4000bar running gear off 100kVA generators. Every morning would be a TBT go through what was happening and it was strict, recorded and regimented.

When I left and started up my own business I could not believe how relaxed everything was in the domestic world. It was a real eye opener! But no trade seemed to accept any responsibility for the work they under took, turn up have a cuppa, mobile, smoke, cuppa and then a moan about the weather! All I can say is after getting through loads of subcontractors I have a good bunch and they work how I want them to. Might cost me more then the going rate but I know they are doing it right.

As part of a trusted trader scheme I have to keep the records of each job and do my own RA for any out of the ordinary tasks again time consuming but its about keeping the guys safe and covering your a55.
 
Sorry did not realise you had qualies etc. So yeh get part P and BS7671 when the 18th comes out. Then pay for scam scheme I mean. Then you are good to go. I am with Stroma they are thorough on the assesment. If you decide to bite the bullet get back to us for info on the assessment. Good luck.

I've just emailed them I've done Part P couple of years ago but will need 2391 and I think the 18th is July 2018? Cheers for info will drop you a line when I've had a chat with them about the assessment.
 
There was a defined scope system which was meant for people doing exactly what you describe,unfortunately for you,because you seem to be a very responsible person and company,I think the system is no longer available
Full scope registration is the way now I suppose

You could even directly employ someone with the necessary electrical qualifications, he could act as your qualifying supervisor for all the companies electrical tasks carried out by the workforce,even electricians like to broaden their skills on occasion
 
You don't have to be a member of a scheme or incur extortionate Building Control fees to sign off for part P.

See here

"The BCB can also use the IET/BCA alliance document. The Institution of Engineering and Technology (IET) and the Building Control Alliance (BCA), co-produced this document and it is downloadable free from the IET website, to gauge an individual’s level of electrical and Building Regulations competency. The BCB can then use this information to adjust building control charges accordingly, based around the level of risk an individual poses and how much work the BCB would incur to confirm this. Using this method, a BCB may accept a BS 7671 Electrical Installation Certificate (EIC) from an un-registered competent person."

And here

"I ET-BCA Guidance for Local Building Control Bodies: Electrical Installation Qualifications and Competence (within England and Wales)
The purpose of this new peer reviewed Guidance document is to outline the skills and competences required for an individual to carry out electrical installation work within dwellings in England and Wales. Specifically work that falls under the remit of Part P of the Building Regulations and referred to in Approved Document P.

An individual’s competence level or skills are afforded a risk rating, explanation and action outcome within the Guidance document. These may then be used to calculate if any additional work may need to be taken into account by a local Building Control Body (BCB)."

If you have the skills and the qualifications then there's no reason for a BC officer to visit, so the costs should be no more than the admin fee to issue the certificate. I would imagine £15 to £20.

If your only doing a few Part P jobs a year then this route has got to be cost -effective..

All the schemes do is take some of the admin, ie. The requirement to keep a register of competent persons, out of building controls hands.

When Part P was enacted there was no intention to give the scheme providers an absolute monopoly, But that's how it seems to have become, especially with the schemers perpetuating the myth that that is the only way to go.

I don't know how easy this route is to achieve but it can't be any more onerous than joining a scheme. I don't know anyone who has done it. Perhaps there are some on here who have? It doesn't seem to be a well know alternative.

I should add that this route appears to be just another scheme and there is nothing to stop you approaching BC personally with your certificates etc. And they may accept that you are a competent Person.

My quotes are from here if anyone wants to read more.

Building Regulations - Part P certification schemes - IET Electrical - http://electrical.------.org/building-regulations/part-p/certification-schemes.cfm
 
i cover west lancs ,chorley and wigan councils i just send in my bs7671 certs downloaded from iet website stick them in a folder with my 2391 never had a failure yet.

I've seen this (as mentioned by Devonchris) avenue described before. Is this the route you took multimick? Do your LBC make any charges?

I might just make an enquiry with my LBC via email, to see what the bobby more is. However, last time I phoned with a general building regs question, I was told I could not receive any guidance unless it related to a current planning/building reg approved application, or when that has just been submitted. So I can't see them too accommodating.
 
Trust a trader..... Is it worth the expense?
I've been validated by Norfolk County Council on their Trusted Trader scheme which is regulated by Trading standards and references left on Referenceline.

Is it worth it? Costs £195 + VAT and it is bit of an arduous process however so far this year I've had 26 jobs from it averaging from £500 - £5000 so if you look at it like that its cost me £7.50 per job. Thats without the quotes I have done which have not happened but I have found people who use it are more likely to not be time wasters, good payers and you also have the protection if they decide not to pay the Trusted Trader scheme will fight your corner to get the money from them if they find their reasons not genuine.

Personally for me I can't fault it and customers who use it say its a great way to get a good reliable tradesman.
 
You don't have to be a member of a scheme or incur extortionate Building Control fees to sign off for part P.

See here

"The BCB can also use the IET/BCA alliance document. The Institution of Engineering and Technology (IET) and the Building Control Alliance (BCA), co-produced this document and it is downloadable free from the IET website, to gauge an individual’s level of electrical and Building Regulations competency. The BCB can then use this information to adjust building control charges accordingly, based around the level of risk an individual poses and how much work the BCB would incur to confirm this. Using this method, a BCB may accept a BS 7671 Electrical Installation Certificate (EIC) from an un-registered competent person."

And here

"I ET-BCA Guidance for Local Building Control Bodies: Electrical Installation Qualifications and Competence (within England and Wales)
The purpose of this new peer reviewed Guidance document is to outline the skills and competences required for an individual to carry out electrical installation work within dwellings in England and Wales. Specifically work that falls under the remit of Part P of the Building Regulations and referred to in Approved Document P.

An individual’s competence level or skills are afforded a risk rating, explanation and action outcome within the Guidance document. These may then be used to calculate if any additional work may need to be taken into account by a local Building Control Body (BCB)."

If you have the skills and the qualifications then there's no reason for a BC officer to visit, so the costs should be no more than the admin fee to issue the certificate. I would imagine £15 to £20.

If your only doing a few Part P jobs a year then this route has got to be cost -effective..

All the schemes do is take some of the admin, ie. The requirement to keep a register of competent persons, out of building controls hands.

When Part P was enacted there was no intention to give the scheme providers an absolute monopoly, But that's how it seems to have become, especially with the schemers perpetuating the myth that that is the only way to go.

I don't know how easy this route is to achieve but it can't be any more onerous than joining a scheme. I don't know anyone who has done it. Perhaps there are some on here who have? It doesn't seem to be a well know alternative.

I should add that this route appears to be just another scheme and there is nothing to stop you approaching BC personally with your certificates etc. And they may accept that you are a competent Person.

My quotes are from here if anyone wants to read more.

Building Regulations - Part P certification schemes - IET Electrical - http://electrical.------.org/building-regulations/part-p/certification-schemes.cfm

I've just contacted my LBC and have asked the question if they operate the scheme. Be interested to see what they say!
 
Just an update on this. I contacted the following early part of the week to see what they could offer and my situation.
ELECSA - never replied
NICEIC - never replied
STROMA - never replied
LBC - never replied

The only people to reply were NAPIT who wanted me to do all manner of things totaling close to £1200 to sign off a simple cooker circuit or new shower circuit. I know its wrong but I now know why people just do it. Appears the schemes have a monopoly on it and its their way or nothing which is so frustrating when you want your work to be above board safe and legal.

Thanks for all the advice greatly appreciated - time to decide I guess!
 
Hi, thanks for the feedback. Very interesting.

As you say, it seems to be a monopoly. And this makes me mad because Building Control are dealing with it irresponsibly . They are the ones that are allowing this to happen. They are responsible for administration of the regs, not the scheme providers.

If I was you I would try again to contact them, keep evidence of that, and if you get no response then on your next job summit your BS 7671 Cert to them and see what happens. Alternately you could contact the the Local Authority Ombudsman and complain.

They have a responsibility to recognise a competent Person. See here from building regs Part P.

3.10 An installer who is competent to carry out inspection and testing should give the appropriate
BS 7671 certificate to the building control body, who will then take the certificate and the installer’s
qualifications into account in deciding what further action, if any, it needs to take. Building control
bodies may ask installers for evidence of their qualifications.

3.11 This can result in a lower building control charge as, when setting its charge, a local authority is
required by the Building (Local Authority Charges) Regulations 2010 to take account of the amount
of inspection work that it considers it will need to carry out.

Good luck with whatever way you go.
 
Well for the past 8 days I have sent the same email to LBC asking them what I need to do to certify the work and what they want to see from me to prove I can do the work

8 emails later and still nothing so I've made it my first morning chore to resend the original email everyday until I do get a reply!

Anyone want a sweep stake to see how long or if I ever get a reply? :)
 
Appears the schemes have a monopoly on it and its their way or nothing which is so frustrating when you want your work to be above board safe and legal.

Its not a monopoly, its worse then that, its a Cartel - all pretty much price fixed with no real competition.......
 
it's a complete farce as well.the intention was to eliminate cowboys, but by increasing the costs for genuine, competent sparks, all it has done is give the cowboys a licence to undercut prices, as they don't have to stump up scam membership and all the other associated costs incurred by us. end of the day, customers ( domestic side ) will generally go for the cheapest quote, as long as it works.
 
Try sending the email, stating how long you have been waiting for a response, with a copy to the chief executive of the council, the chairman of the council and your local MP. That should stir things up.
 
11 days later and I finally have a reply from the LBC which is below
Good Afternoon
Further to your e-mail, from the information/ C&G details you are competent to carry out this type of works. Your two choices would be to become a member of one of the Part P self certification schemes or on each job (where applicable) you would need to submit a Building Notice application for the electrical works if it was not already not covered by an existing Building application for ie, House or extension etc.
Unfortunately, we would not keep a data sheet of your certificates and thus you would need to send your details in on every application.
I trust the above helps

That sounds like a round about way of saying get your a55 on a self certification scheme to me
 
yeah. and you submit a building notice application along with a cheque for £300.
 
Hi thanks for keeping us informed on this saga. They have obviously been mulling it over and taking advice before replying.

Here's my take on it.

The Regs does not say you have to submit a building application submission. It says you have to inform a building control body before work begins.

They have accepted you are competent to carry out the work.

Email them before your next notifiable job. Give them 3 or 4 days notice. (Not too long to give them plenty of time to think about it.) Head it something like, building regulations, part P, notifiable work, prior information of work to be carried out.

Details of property

Details off work

Date work is to commence

Add ; in accordance with the building regs and your acceptance of my competence to carry out this work, I will be submitting BS7671 certification of inspection and testing, along with copies of my qualifications, on completion of the work.

That would (in my opinion) cover all the requirements in the regs.

See here

Certification by a building control body
3.8 If an installer is not a registered competent person and has not appointed a registered third-party
certifier, then before work begins the installer must notify a building control body.
3.9 The building control body will determine the extent of inspection and testing needed for it to
establish that the work is safe, based on the nature of the electrical work and the competence
of the installer. The building control body may choose to carry out any necessary inspection and
testing itself, or it may contract a specialist to carry out some or all of the work and furnish it with
an electrical installation condition report.
3.10 An installer who is competent to carry out inspection and testing should give the appropriate
BS 7671 certificate to the building control body, who will then take the certificate and the installer’s
qualifications into account in deciding what further action, if any, it needs to take. Building control
bodies may ask installers for evidence of their qualifications.
3.11 This can result in a lower building control charge as, when setting its charge, a local authority is
required by the Building (Local Authority Charges) Regulations 2010 to take account of the amount
of inspection work that it considers it will need to carry out.

Sorry if this sounds like I'm trying to teach you to such eggs, it was just the easiest way to get down my thoughts.

Good luck. If you pull this off you will be a hero to the sole trader electrician and sworn enemy of the scheme providers.
 
It's obvious from Multimick's earlier post that some Councils are more in tune with the Regs than others, but you shouldn't be discriminated against dependant on where you work.

i cover west lancs ,chorley and wigan councils i just send in my bs7671 certs downloaded from iet website stick them in a folder with my 2391 never had a failure yet.
 
From my rambling posts it may appear that I am anti Scheme Providers. I'm not in general. It just appears that they have lost sight, probably due to complacency, of what they should represent.

They should be a trade body representing their members interests but they seem to have lost sight of that. Can you imagine someone turning up at a tube station offering to drive the train for half the going rate? and what the reaction would be from the drivers representatives? In effect, that's what's happening. But as long as people have to join to get their work signed off there is no incentive for the schemes to offer much else.

We don't seem to have any public information regarding the danger or potential difficulty of selling a house with dodgy electrics. Why can't the schemes get together and fund that?

Imagine if one of them got together with a meter manufacturer and came up with a MFT with a sim card and smartphone type interface, fill in the details of the property etc. Do the tests, press send, job done. Now perhaps that would be worth joining for. It could even be leased and included in your annual fees. To be returned if you left the scheme.

But while ever they have a monopoly on part P its not going to happen. Because at the moment it's all about profit and not about how to attract members.

Perhaps some of them will read this and decide to change. Then again.
 
This is the reply I have sent this morning to my LBC. A massive thankyou to Devonchris for all the advice given

Many thanks for your reply however I am unsure it has actually answered the question originally asked

After viewing Part P Electrical Safety - Dwellings Part 6 Section 3 may I draw your attention to the following points

Certification by a building control body
3.8 If an installer is not a registered competent person and has not appointed a registered third-party certifier, then before work begins the installer must notify a building control body.
* No where does the regulations stipulate that a Building Notice Application needs to be submitted. Could you please clarify your reason for stating this?
3.9 The building control body will determine the extent of inspection and testing needed for it to establish that the work is safe, based on the nature of the electrical work and the competence of the installer. The building control body may choose to carry out any necessary inspection and testing itself, or it may contract a specialist to carry out some or all of the work and furnish it with an electrical installation condition report.
3.10 An installer who is competent to carry out inspection and testing should give the appropriate BS 7671 certificate to the building control body, who will then take the certificate and the installer’s qualifications into account in deciding what further action, if any, it needs to take. Building control bodies may ask installers for evidence of their qualifications.
3.11 This can result in a lower building control charge as, when setting its charge, a local authority is required by the Building (Local Authority Charges) Regulations 2010 to take account of the amount of inspection work that it considers it will need to carry out.
3.12 Once the building control body has decided that, as far as can be ascertained, the work meets all Building Regulations requirements, it will issue to the occupier a Building Regulations completion certificate (if a local authority) or a final certificate (if an approved inspector).
The majority of my work will involve adding an extra kitchen socket/s or and FCU for a white appliance above the worktop to comply with current electrical regs whilst installing a kitchen. As I have already been deemed to be of competence from the information and C&G details supplied I would expect to be able to submit the following 5 working days prior to starting the work
Details of property

Details off work

Date work is to commence

And in accordance with the building regs and your acceptance of my competence to carry out this work, I would submit a BS7671 certification of inspection and testing, along with copies of my qualifications, on completion of the work.

That would in my opinion cover all the requirements that are clearly stated in the Regulations.


Could you confirm if this would indeed to acceptable?
 
How does showing your qualifcations demonstrate you are competent?
I qualified in 1981, I could of been driving a bus ever since but as long as I forward a copy of my C&Gs I'm competent?
 
How does showing your qualifcations demonstrate you are competent?
I qualified in 1981, I could of been driving a bus ever since but as long as I forward a copy of my C&Gs I'm competent?

I did not write the regs but thats what they require.
I agree qualifications do not make you competent but I do now have a reference from a registered spark for some of the work I have done that he has checked and signed off on and willing to vouch the work I do and have done coincides with all the regs required.
Plus it does state in 3.10 they will access what further testing would be required but the underlying question is can it be done so I and others who are not on a Part P competent scheme and do the work without needing registration as the electrical is not our main core business but falls inside of our scope of work sometimes.
Personally I feel the schemes are not set up for the sole traders and certainly for people such as myself we are being bullied into a scheme that we don't actually need.
 
I did not write the regs but thats what they require.
I agree qualifications do not make you competent but I do now have a reference from a registered spark for some of the work I have done that he has checked and signed off on and willing to vouch the work I do and have done coincides with all the regs required.
Plus it does state in 3.10 they will access what further testing would be required but the underlying question is can it be done so I and others who are not on a Part P competent scheme and do the work without needing registration as the electrical is not our main core business but falls inside of our scope of work sometimes.
Personally I feel the schemes are not set up for the sole traders and certainly for people such as myself we are being bullied into a scheme that we don't actually need.
I was making a general point Bear.
I've been in the trade for 35 years and I wouldn't be able to assess a persons competence just by looking at a few certificates, so what chance has a person sitting behind a desk at LBC?
Not sugesting for one minute that you don't go down that route, I would.
Just saying that part or the regs is flawed.
 
A little bit more info here which supports your campaign.

2012 consultation on changes to the
Building Regulations in England

29. We could also amend the Building (Local Authority Charges) Regulations 2010 to
ensure that building control charges would be lower where qualified third party
electricians took over responsibility for inspection and testing from the building
control body and were able to issue a BS 7671 inspection and testing form. The lower
charges would recognise the savings in building control time, and reflect the fact that
the amendments to the Charges Regulations would require local authorities to take
into account third party certification in setting their charges.

30. These lower building control charges would apply equally to qualified electricians
capable of inspecting and testing their own notifiable electrical installation work (and
of issuing a BS 7671 Electrical Installation Certificate), and who under the existing
arrangements choose, for whatever reason, not to join a registration scheme.
 
I was making a general point Bear.
I've been in the trade for 35 years and I wouldn't be able to assess a persons competence just by looking at a few certificates, so what chance has a person sitting behind a desk at LBC?
Not sugesting for one minute that you don't go down that route, I would.
Just saying that part or the regs is flawed.

Not sure the schemes are the right answer either ........................ they "inspect" 1 or 2 jobs - which are the ones the installer suggests .................... nobody in their right mind would take an assessor to a job thats below par .................

AND the schemes seem to do nothing about complaints..................

What a fantastic situation......................

I was on a job moving a BT point recently. The builder was Part P registered and his work left a lot to be desired ...................
 
Not sure the schemes are the right answer either ........................ they "inspect" 1 or 2 jobs - which are the ones the installer suggests .................... nobody in their right mind would take an assessor to a job thats below par .................

AND the schemes seem to do nothing about complaints..................

What a fantastic situation......................

I was on a job moving a BT point recently. The builder was Part P registered and his work left a lot to be desired ...................
It's not perfect by a long way Murdoch, but it's better than just showing a certificate to someone who has no electrical knowledge.
It might only be 2 jobs but it's 2 jobs more than the LBC see, and they're both inspected by a qualified electrician/engineer.
Then there's the fact that you need to show you know how to undertake testing to the latest regs including answering various question. You are required to show your test equipment including callibration evidence, show your insurance documents and show all the necessary publications relevent to the work you undertake, ie regs, on-site guide, part p doc and so on.
 
It's not perfect by a long way Murdoch, but it's better than just showing a certificate to someone who has no electrical knowledge.
It might only be 2 jobs but it's 2 jobs more than the LBC see, and they're both inspected by a qualified electrician/engineer.
Then there's the fact that you need to show you know how to undertake testing to the latest regs including answering various question. You are required to show your test equipment including callibration evidence, show your insurance documents and show all the necessary publications relevent to the work you undertake, ie regs, on-site guide, part p doc and so on.

TBF you do not know who is looking at the certs and it could be a trained spark with a lifetime of electrical knowledge? I have been informed they do have some working for the LBC
LBC will certainly inspect or check the first few jobs or appoint someone else to check my work which I strongly agree with. The idea is they perform these checks ascertain what you are competent at how you have done the testing and collate that information and give you a risk factor for the work you do. This can vary from needs further checking of your work on future jobs or that you are competent to perform that particular work again with no further inspections required.
As a limited company and part of the councils trusted trader scheme the LBC will already know that I have insurance as it is a requirement for them and Trading Standards. I also had to provide them with documentation of any calibrated equipment and regulation books I work to which also included me proving I had copies of Part F,G,H and P. When the renewal comes up I will have to submit it all again.
Obviously this is just for my company but as you have said I am unsure whether LBC would check those things but as a TT member I have to check that all my subcontractors are insured for the work they do and part of the Construction Industry Scheme.
If I were to undertake full rewires, CU I understand the necessity for the schemes but for those of us who do the odd little bit here and there it is not practical. If I come across a house that I think needs a rewire or a CU done I get a subcontractor in who does it for me who incidentally has exactly the same qualifications as me but I would deem more competent than I to do that sort of work. Hence why I call in a pro!
I guess the bottom line is whether you agree with it or not the facility to do what I am asking is there and should not be a battle to try and get a LBC to abide by the rules but instead the schemes and LBC seem to have forgotten about it and want you to join the masses of paying out your hard earned money for not a lot in return.
 
^^ I see more poor installs in kitchens and bathrooms by so called "fitters" than any other work on lecky in houses
C,mon every trade has their rouge tradesmen who have no pride in their work or respect for their customer and have a "that will do attitude" Sorry you seem to have found so many but its certainly not how my company or subcontractors conduct themselves.
 
The LBC challenge is to determine competence in each and every case. As you will hear and read competence is a topic of hot discussion. In this less than perfect world the CPS does give LBC a way. While there are other options available, I think LBC choose this path as its minimum work and responsibility for them to achieve their bit. The other paths are clearly possible but the saying "lead a horse to water ..." comes to mind.
 

Reply to Do you have to become Part P registered to certify work? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi all, I am going to fully rewire my house. What do I HAVE to do once I’ve rewired it? I am an approved spark, but do not have part P. Do I need...
Replies
11
Views
2K
Hello. I have a quick question for registered sparks on here. Can/ will / do you certify notifiable work done by others? I guess I’d have to...
Replies
18
Views
2K
Hi, sorry if this is the wrong place to ask, I am wondering about becoming an electrician of some form or another and thought to come to an...
Replies
15
Views
1K
I put some news lights in a bathroom and new extractor fan. Did the tests and filled out form. A couple of days later another electrician came in...
Replies
2
Views
316
Can I have a napit assessment with only on CU change? Really struggling to find work to be assessed as only just starting up with my company...
Replies
2
Views
841

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock