Discuss Does this comply with 314? in the UK Electrical Forum area at ElectriciansForums.net

By the looks, the reg makes us responsible for equipment leakage in the installation design. For me to do that, the appliances would need to have a stated and rated leakage current. Or have I misunderstood?
Just now I can't recall working on a domestic dual RCD installation that was tripping for reasons other than a fault.
 
By the looks, the reg makes us responsible for equipment leakage in the installation design. For me to do that, the appliances would need to have a stated and rated leakage current. Or have I misunderstood?
Just now I can't recall working on a domestic dual RCD installation that was tripping for reasons other than a fault.

Same here, I'd one a fortnight ago, cheap 4way extension lead.
 
I am not aware of those proposals, are you saying it is proposed that a 63a RCD would be restricted to a load of 21a?.....then presumably a 32a RCBO would be restricted to under 11a?
So a 10kw shower would need a minimum 135a RCBO ?....Sorry if I'm having a blonde moment but that just doesn't make any sense.
as i read it, it's talking about leakage currents not being more than 30% of the mA rating of the RCD, unrelated to load current.
 
Since my #25 (trying not to big myself up too much here ;)),it has brought numerous comments and posts on 531.3.2 (draft 18th).

You'd been surprised perhaps, that the draft has only collected a few comments on this new proposed reg, which therefore may see its introduction in the 18th.

In fact the current '531.2 RCDs', will be Over Current Protective Devices. RCDs will be moved to 531.3, as far as I can make out. This includes the reg on unwanted tripping, as well as some other changes; '531.3.1.201 Except in certain special installations or locations (Part 7), for protection against electric shock, there is no requirement to disconnect/switch the neutral in TT or TN Systems'. Haven't noted that before, seem to recall members stating the opposite previously for a TT system (SP RCBO's)?

Apologies for hijacking your thread Murdoch, but you started it :)
 
^^ ha ha.

Seeing as nobody can explain why we can fit dual board now, I have come to conclusion that my interpretation of 314.2 is correct in the op and my example stands as a non compliance to the regs.
 
By the looks, the reg makes us responsible for equipment leakage in the installation design. For me to do that, the appliances would need to have a stated and rated leakage current. Or have I misunderstood?
Just now I can't recall working on a domestic dual RCD installation that was tripping for reasons other than a fault.

It's abundantly clear that the 18th will add further confusion to the regs.

Do the people who dream up these changes actually consider the impact of what they write and add. I don't think so
 
I decided to make up a small extension lead with the earth broken out so I can check the earth leakage of various plug in appliances by clamping the L+N.
It was very revealing, I checked 3 Miele appliances and found they were all around 3mA leakage; one of them was a brand new dishwasher. The leakage increased slightly when switched off on the machine. A Neff induction hob I clamped the cable and measured 2mA leakage.
These leakage currents add up and may be the reason that the proposed 18th edition is specifying a limit of 30% of the RCD trip current. Problem is I do not see how a sparky will know what appliances the householder will plug in, and will he have to check items that are hard wired like hobs. I think it is all the filters fitted to modern day electronic appliances that is giving rise to increasing leakage currents.
The only way around this, unless I am missing a trick is to fit all RCBO boards, even then you could easily exceed the 30% RCD current on 1 ring final.
 
I clamped my own house the other day. PC running, few led lights on, tv on, appliance turned on but not running. Clamp meter's a cheap en, but I had 14mA leakage. But I've have that split across RCD & RCBO's. Went to a job in the afternoon, semi with 1 x lighting, 1 x RFC & electric cooker. 9mA eath leakage.

^^^ ditto
 
^^ ha ha.

Seeing as nobody can explain why we can fit dual board now, I have come to conclusion that my interpretation of 314.2 is correct in the op and my example stands as a non compliance to the regs.
314.2 merely states that due account shall be taken of the consequences of the operation of any single protective device

As the rest of the installation will not be affected by the operation of the device in question at the present time it complies.
 
Hit, nail and head spring to mind..... I stopped fitting dual RCD boards when AMD3 boards arrived - far, far, far better when something trips.
For a larger property, I'd fit a high integrity CU with 2 or 3 RCBO's. The off the shelf RCBO populated CU's only come seem to come with 6 or so RCBO's, to make one up yourself is a tad expensive?

My own pad, which I did a few years ago, has a RCBO CU and single RCD CU for ono important circuits (314.2 considered ;)).
 
I'd give up Murdoch :rolleyes:

Not yet!

I need somebody to remind me why we ditched split load boards and introduced dual RCD's - somebody must have some memory of this?

Or as I said 314.2 my interpretation is correct!

There's nothing worse than a single RCD up front board ....
 
Being pragmatic, I think it is most useful and sensible to have lighting and power in a given area on different RCDs and whilst one might argue about the exact interpretation of 314 it would be poor design not to do this, and hence arguably non-compliant.

The main point of a 30mA RCD is to protect against electric shock, which is most likely to occur when someone has an accident of some kind with a portable appliance. To plunge them into darkness within a fraction of a second of having been shocked, simply on the grounds of economy, is not sensible. I think we get blinkered to this purpose of RCDs because we are so used to being called on to troubleshoot nuisance trips, we don't associate their operation with the moment they cut short a possibly fatal shock that could leave someone in a vulnerable physical condition.

On the subject of convenience, many elderly and infirm people are most at risk on the stairs. They might safely be able to cross the room to turn on the ceiling light if they have been using a table lamp when the RCD serving the ring trips, but would not venture downstairs or run a cable up if the stairwell and room lighting circuits went off too.

It was very revealing, I checked 3 Miele appliances and found they were all around 3mA leakage; one of them was a brand new dishwasher.

Really? The maximum permissible on a 13A plug is 3.5mA, I would be most surprised to see that much leakage from any domestic appliance or have they gone silly with filtering these days? I don't PAT any domestics but I see a lot of PAT results from industrial equipment and no single piece of kit ever reaches 3mA. Even the media systems that I build, with maybe 20 pieces of equipment built into a rack all run from one plug, rarely reach 2mA.
 
Being pragmatic, I think it is most useful and sensible to have lighting and power in a given area on different RCDs and whilst one might argue about the exact interpretation of 314 it would be poor design not to do this, and hence arguably non-compliant.

Thank you .......... which is the way I think about this subject.

Still nobody offering up why we ditched split load boards, and adopted dual RCD rather than single up front boards...............
 
Really? The maximum permissible on a 13A plug is 3.5mA, I would be most surprised to see that much leakage from any domestic appliance or have they gone silly with filtering these days? I don't PAT any domestics but I see a lot of PAT results from industrial equipment and no single piece of kit ever reaches 3mA. Even the media systems that I build, with maybe 20 pieces of equipment built into a rack all run from one plug, rarely reach 2mA.

Out of curiosity, where does that figure come from?
 
Thank you .......... which is the way I think about this subject.

Still nobody offering up why we ditched split load boards, and adopted dual RCD rather than single up front boards...............
Split load boards were relevant to the 16th Edition, protecting socket outlets with 30mA RCD protection and leaving the rest unprotected. With the advent of greater RCD protection with 17th Edition an appropriate method of protection was dual RCD boards, this addresses both the increased RCD protection required and the division of circuits guidelines in a practical way. For a domestic situation this is a practical approach, remembering the the division of circuits is worded clearly to indicate that this is not an absolute requirement.
This could be taken by common practice to be the minimum standard of compliance with the regulations.
It is always possible to exceed the minimum standard and fit an all RCBO board. I think there would be no doubt that this provides a greater division of circuits but at present the cost benefit analysis is still wavering and comes down in favour of the dual RCD board (by my analysis, but not by yours). As the cost of RCBOs comes down this will, and is, shifting the balance of what is reasonably practicable.

I would say that overall in a domestic property a single dual RCD board or two upfront RCD boards is compliant but a single all RCBO board would exceed the minimum requirements.
 
S
It is always possible to exceed the minimum standard and fit an all RCBO board. I think there would be no doubt that this provides a greater division of circuits but at present the cost benefit analysis is still wavering and comes down in favour of the dual RCD board (by my analysis, but not by yours).

If I'm challenged about my preference for fitting RCBO boards - I explain what happens when 1 RCD trips on a dual board - and most people then agree RCBO boards are better.

As for minimising inconvenience and 314.2 all it would take is 1 or 2 more sentences in 7671 to clarify.

I will continue not to fit small up front boards if the circuits contained in the the same room(s).

Last month I was working on an older MK split load board - instead of moving a circuit from the non RCD side to the RCD side, I opted to fit a RCBO - sure it cost the client about £50 but much better in the long run.

Personally I'd like to see boards split RCD / RCBO .......... sockets on RCBO's
 

Reply to Does this comply with 314? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
542
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Replies
12
Views
732
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
847
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
662

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock