Hi all,

I replace about 30 lights from 2D to led, I'm under this impression I don't need to issue a certificate for this as it's only maintenance, am I wrong because the company are now chasing for a certificate

Many thanks
 
Take a look at chapter 63. You can use a minor works for change of current using equipment. That’s assuming you’ve changed the light fittings.
 
You are not wrong as it is like for like. However it is sage to at least offer a minor works and test Zs etc. I replaced 600 x 600 fluors for LED and found 89v on the earth just doing routine testing. Always wise to check imo.
 
Hi all,

I replace about 30 lights from 2D to led, I'm under this impression I don't need to issue a certificate for this as it's only maintenance, am I wrong because the company are now chasing for a certificate

Many thanks

I would issue a minor works certificate for each circuit worked on.
 

Reply to Does this work need a certificate? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
916
Hi Everyone, This is my last question/post for tonight, promise. Please can I ask for a little advice on certificates as I am now questioning...
Replies
4
Views
934
Hi all, I am a home owner and our builder has completed a garage conversion with the electrician installing a new 4 way distribution board. The...
Replies
18
Views
1K
Hi Everyone, I had a new consumer unit installed in December 2021, the electrician said that he had more testing to complete and would come back...
Replies
28
Views
3K
Please, what certification is required to work in usa or any other european country as a foreigner. I am an industrial electrician with masters...
Replies
2
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock