Any advice gratefully received:

So in our new house theres a washing machine.

It seems to work fine. It's plugged in to a plug socket in the kitchen
Whenever I turn it on, it goes for a minute or two then trips the MAIN house circuit breaker (not the local circuit circuit breaker).

When I take an extension lead and plug it in to another socket in a different room, it runs the cycle fine and doesnt trip anything.

Doenst make much sense to me...I'm sure this is a simple thing to sort out - but not for me.
 
This Circuit breaker that trips after a few minutes, that would be the Residual Current Device( RCD)
When you pug it in via an extension lead, it works fine all right so far?
What you may have is a Consumers Unit (fuse board) that has some circuits that are protected by the RCD and some that aren't, your washing machine must have an earth fault possible a N to E fault, that's my diagnoses from afar and without any test equipment, you may need the assistance of a white goods engineer.
 
Can we assume that the ring final circuit socket in another room is protected by another RCD ?. Have you tried initial start up of washing machine in extension lead ?, if it then trips then it could be the washing machine. It could be two things with the 1st ring 1.existing leakage currents from other appliances and by a bit more has put the value over the threshold 2. fault /damage to circuit cable.
 
or could be a N-E reversal on the kitchen socket. soon as the heater kicks in, drawing a larger current, the load is across L -E, thus tripping the RCD.
 
try kettle direct into kitchen socket without extension lead. it's possible that the extension lead has a missing or damaged cpc.( earthing conductor ).
 
Can OP post a photograph of the distribution board with the offending breaker tripped. We will be able to tell if its an RCD, or a split board or whatever.
 
Sounds to me like there may be a marginal fault contact in the washing machine socket, or its supply, which leaks enough current to trip only when the washing machine electronics connect a decent sized load.
 
I would replace the washer ?
could well have a leak to ground,
A common thing with washers.

I'd test the entire system for a N-E fault first, if the OP replaces the washer and the problem persists he's wasted his money and will still have to employ the services of a sparks. Get an experienced electrician to carry out an insulation resistance test on the electrics first, probably cost an hour labour.
 
QUOTE - [ Sounds to me like there may be a marginal fault contact in the washing machine socket, or its supply, which leaks enough current to trip only when the washing machine electronics connect a decent sized load. ] END QUOTE .

Surely it should not leak any current, at any time, regardless of load ?
 
QUOTE - [ Sounds to me like there may be a marginal fault contact in the washing machine socket, or its supply, which leaks enough current to trip only when the washing machine electronics connect a decent sized load. ] END QUOTE .

Surely it should not leak any current, at any time, regardless of load ?

Pretty much everything has some degree of leakage. It all mounts up and so cumulative leakage can cause an RCD to trip. Especially if it is towards the lower end of its tripping current
 

Reply to Domestic electric puzzle in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
695
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
811
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
786
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock