Discuss Domestic Lighting Circuit Methods In New Builds in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
26
To my knowledge, there are 3 methods of splitting the line conductor in each lighting circuit:

Joint box below floor, or above ceiling
Three terminal ceiling rose/batten lampholder
Joint in switch box (neutral)

I am wondering which method is most commonly used in new houses.

I have been in this house for nearly forty years and after upgrading the central heating from warm air to combi-boiler, the Scottish Gas Company's installers connected three smoke detectors to an octopus joint box.
After several years the downstairs lighting occasionally fails. After a time these lights begin to work again.

Being a retired spark, I checked all connections in the CU and they were all secure.

Not knowing where the octopus joint box for the entire four apartment house was located I lifted the fitted carpet upstairs landing and found it.

The line connection had approximately six conductors below a brass plate, but the added line conductor had caused the plate to ride on the additional conductor which was at an angle across the other six. Since the brass connection plate (about one inch long and secured at its centre by a single 2BA or 4mm brass screw had failed to put equal pressure on all conductors, time had caused it to develop an intermittent o/c of the line conductor feeding all downstairs lighting.

Summing up don't you think ALL future new builds should not use the octopus joint box system especially where it is sited below wooden floors with no removable hatch left for access nor even an indication of the position of same.
 
Back in the "old" days there was no appreciation of what happens to s screwed terminal joint. And no appreciation of just how long an installation can exist.

Nowadays we often work on installations that are decades old, and finding that Missing neutral connection in a buried terminal In a landing under a carpeted floor is a right PITA.

That's why, in hindsight, we have the requirement for all screwed terminations to be accessible.

In a few decades time, the Gods in IET may discover that the much lauded cure-all MF terminal has some shortcomings. But for now that's the regs we've got.
 
Well for a start the regulations were quite different 40 years ago to what they are now.
true. more common sense then, assuming that installations were carried out by competent sparks, now regulations get changed to allow for idiots.
 
When doing a new light circuit. i worship the WAGO gods with my nice WAGO connectors and MF enclosures. saves ----ing around with fiddly screws. Thus far the light gods do not seem to be unhappy.

I always try and have the enclosure next to a joist or beam where a floorboard ends so that its readily accessible in future. with a lot of the new ones there are little clips on back that attach to screws to hold in situ.
 
You need joint boxes when lights have been wired with the mains in out to the rose which can be standard in a new build when the house is not sold and it's basic spec.
Nothing wrong with this but say you then wanted to install downlights then joint boxes will be necessary.
 
You need joint boxes when lights have been wired with the mains in out to the rose which can be standard in a new build when the house is not sold and it's basic spec.
Nothing wrong with this but say you then wanted to install downlights then joint boxes will be necessary.
Alternatively if we all in future use the switch boxes as the joint box, then no joint boxes are necessary, even with down-lighters. The point is, joint boxes, if unable to be left easily accessible, then don't use them at all. The switch box method also makes inspection and testing easier and much quicker without going below floors or into attic spaces.
 
Alternatively if we all in future use the switch boxes as the joint box, then no joint boxes are necessary, even with down-lighters. The point is, joint boxes, if unable to be left easily accessible, then don't use them at all. The switch box method also makes inspection and testing easier and much quicker without going below floors or into attic spaces.
Can make things difficult to tap off a supply for another lighting point such as adding a light in a loft.
A harder task when all mains are located in the switch.
You maybe able to fish a cable down the wall depends really.

As said already if designing for downlights mains to the switch, if not there's no reason why you can't loop in out at the light.
No wrong way really.
Also one of our apprentices said the preferred way teaching at College is mains in out at the switch as it eliminates time spent 2nd fixing a light on steps which anything working off the ground is considered working at a height, eliminating accidents.
 
Last edited:
You need joint boxes when lights have been wired with the mains in out to the rose which can be standard in a new build when the house is not sold and it's basic spec.
Nothing wrong with this but say you then wanted to install downlights then joint boxes will be necessary.

I disagree. Why do you need joint boxes, especially hidden ones the op is going on about.

Neural at switch is the way I normally go these days.....
 
Can make things difficult to tap off a supply for another lighting point such as adding a light in a loft.
A harder task when all mains are located in the switch.
You maybe able to fish a cable down the wall depends really.

As said already if designing for downlights mains to the switch, if not there's no reason why you can't loop in out at the light.
No wrong way really.
Also one of our apprentices said the preferred way teaching at College is mains in out at the switch as it eliminates time spent 2nd fixing a light on steps which anything working off the ground is considered working at a height, eliminating accidents.
 
You are right, Ian.
Was thinking of the type of terrace house where the octopus system has been used with the large joing box below the upstairs floor and client has composite flooring fitted. This would be a nighmare to gain access to the joint box. As you say, there is no right way.
 
Best you define "sensibly" as I can't find that in the BYB!

Indeed, it's based entirely on my own opinion, and where I would be inclined to look for it.

So if in a loft I would mount it above insulation level, on a purlin or a board screwed to the uprights of trusses.
In a chalet bungalow it would be just inside the access into the eaves, again mounted above insulation level.
And if possible I will have a light fitting near it which is fed via a different circuit.
 
Hi please can somebody help answer my question
I got a total of 50 spot lights in a house i am goin to install. I am goin to use wagos
Do I HAVE to put every light wagos connectors in an enclosure if so why?
Some body said just put insulation tape on them
All this is happening in terraced house with no insulation in ceiling and the lights are double insulated , all gonna b with led 4 watt bulb
Thank u
 
Hi please can somebody help answer my question
I got a total of 50 spot lights in a house i am goin to install. I am goin to use wagos
Do I HAVE to put every light wagos connectors in an enclosure if so why?
Some body said just put insulation tape on them
All this is happening in terraced house with no insulation in ceiling and the lights are double insulated , all gonna b with led 4 watt bulb
Thank u

Yes'm every connection will need to be in an enclosure, the reason is that this is what is required by the regulations.
 
Hi please can somebody help answer my question
If you need to ask then you shouldn't be doing the job!
As above.
All terminations must be in an enclosure.
All cable sheaths must also enter the enclosure.
Unless the enclosure is screwed to a background,and the cables are clipped, then the enclosure must have strain relief for the cables.
If the termination is a screwed it must be accessible, or use a maintenance free termination.
There's probably more too.

Best to buy 50 Wagolight boxes to go with your downlights.
 
Yes'm every connection will need to be in an enclosure, the reason is that this is what is required by the regulations.
All joking apart, and based on practicalities, as what happened to me was my downstairs lights all failed one night. I checked all connections at the Consumer Unit and found them all to be tight. I removed two wall switches and saw that there must be a joint box or three terminal ceiling roses used but there were no three terminal ceiling roses in the installation. So where are the joints? Wiring was from the upstairs down to the ground floor switches, so the joint box/boxes had to be below the upstairs floor boards. I lifted the fitted carpet at one end of the long landing and found no sign of floor boards that had been marked to indicated where the joint box/boxes were. At last, I discovered the Octopus joint box system had been used. So all switch cables and ceiling point cables terminated in that box. It was, in effect a "Marshalling" box.
Upon opening the box I saw that the Gas Board electrician who installed the mains connected smoke detectors during the upgrade of the heating system from warm air to combi-boiler had connected his live feed under the connecting brass plate that joined all the switch feeds and the main feed for the circuit. But he had placed the copper at an angle over the existing coppers. The plate that clamped the six copper feeds was not making an effective pressure on all the coppers as a result. I assume that the coppers were seated in grooves in the octopus joint box. I tried to unscrew the brass 2BA or 4mm terminal screw but it was solid and it gave up till the next time. Since then the downstairs lights have never even flickered but I will go back and strip out the octopus box and use some other type of multi connecting method. I am trying to decide which method to use - terminal strips linked out, Wago's, solder the bloody coppers or whatever. Ideas please.
I give you all of this detail so that you will realise that joint boxes below wooden floors as a method of splitting the line conductor is very bad practice.
Suggestions welcome. Not prepared to move home!
 
All joking apart, and based on practicalities, as what happened to me was my downstairs lights all failed one night. I checked all connections at the Consumer Unit and found them all to be tight. I removed two wall switches and saw that there must be a joint box or three terminal ceiling roses used but there were no three terminal ceiling roses in the installation. So where are the joints? Wiring was from the upstairs down to the ground floor switches, so the joint box/boxes had to be below the upstairs floor boards. I lifted the fitted carpet at one end of the long landing and found no sign of floor boards that had been marked to indicated where the joint box/boxes were. At last, I discovered the Octopus joint box system had been used. So all switch cables and ceiling point cables terminated in that box. It was, in effect a "Marshalling" box.
Upon opening the box I saw that the Gas Board electrician who installed the mains connected smoke detectors during the upgrade of the heating system from warm air to combi-boiler had connected his live feed under the connecting brass plate that joined all the switch feeds and the main feed for the circuit. But he had placed the copper at an angle over the existing coppers. The plate that clamped the six copper feeds was not making an effective pressure on all the coppers as a result. I assume that the coppers were seated in grooves in the octopus joint box. I tried to unscrew the brass 2BA or 4mm terminal screw but it was solid and it gave up till the next time. Since then the downstairs lights have never even flickered but I will go back and strip out the octopus box and use some other type of multi connecting method. I am trying to decide which method to use - terminal strips linked out, Wago's, solder the bloody coppers or whatever. Ideas please.
I give you all of this detail so that you will realise that joint boxes below wooden floors as a method of splitting the line conductor is very bad practice.
Suggestions welcome. Not prepared to move home!

I have not suggested that joint boxes below wooden floors, or in any inaccessible location, is a good thing.

Also as far as I can see from your story the fault has been caused by the gas installer and so you should be pursuing them to rectify the fault.
 
The thing is, it has taken more than six years to show so forget that. If it had. Een a mere month or two ago, I would have got the fitter back. Even the system installers were subbies of the Brittish Gas.
I will repair the fault myself but am only showing what can happen in the life of an installation, for the younger age group of sparks out there.
Thanks to all who have posted.
 

Reply to Domestic Lighting Circuit Methods In New Builds in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
658
Hi There is a lighting circuit fault in a property with the downstairs lighting circuit. I have tested the voltage and there is 230v on both...
Replies
10
Views
1K
Hi, New to the forum. I have two very specific questions, for the setup below. Setup details: Currently I have a setup with an outlet used for...
Replies
6
Views
647
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
869
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
574

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock