Search for tools and product advice,

Discuss double pole or single pole rcbos in the Electrical Tools and Products area at ElectriciansForums.net

WallaceP

-
Arms
Reaction score
235
What is everyone's thoughts on double pole rcbo's vs single pole, I mostly use Fuse Box these days with the odd Hager board if i'm feeling flush. I usually use the single pole fuse size rcbos. recently I tried the mini double pole rcbos but for the extra cost I think I will go back to using the single pole ones. Just wondering what your guys and girls think of sp vs dp rcbos.

Thanks
 
Well some advantages of DP are easier IR testing on TNCS setups (if manufacturer allows testing on the outgoing terminals) and ability to totally isolate a circuit for fault diagnostics.
I have occasionally used single pole if budget is tight (and once purchased accidentally!) but prefer double pole.
 
Personally, I think the question needs to be asked the other way around, especially in 3ph boards - why would you not use a DP device? The Neutral is a line conductor, after all.
 
Personally, I think the question needs to be asked the other way around, especially in 3ph boards - why would you not use a DP device? The Neutral is a line conductor, after all.
If only they made N-switching RCBOs for 3P boards!

I think Schneider do a N busbar in some of their 3P boards but never had one to play with. Really it is time that was the norm so you just plugged in MCB or RCBO and did not lose a slot or two to get the extra RCD protection.
 
If only they made N-switching RCBOs for 3P boards!

I think Schneider do a N busbar in some of their 3P boards but never had one to play with. Really it is time that was the norm so you just plugged in MCB or RCBO and did not lose a slot or two to get the extra RCD protection.
Can't remember what thread it was but I posted up the other day about my annoyance with Eaton 3PN RCBO's that are only best used on the right hand side bus bar and rob you of a 1ph (or 3ph by extension) slot.
 

Reply to double pole or single pole rcbos in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi everyone, just wanted to ask if any other sparks who use scolmore click mode have recently noticed a drop in the quality of their accessories...
Replies
25
Views
2K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
4K
Hi everyone. The title should sound crazy enough, but it's what happening in my 72-years old home we've purchased 2 years ago. I found the crazy...
Replies
1
Views
512
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
I've been carrying out quite a few domestic extension first fixes recently which involves providing a power supply installed from the properties...
Replies
7
Views
2K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock