Discuss Double socket problems!! in the UK Electrical Forum area at ElectriciansForums.net

rennie158

DIY
Reaction score
0
I’m changing my double socket and upon removing the old one, I seem to have 3 separate wires coming in to it. So essentially I have 3 live wires, 3 neutral wires, and 3 earth wires. How do I connect the earth wires to the new socket as it only has 2 terminals? I’m fitting new chrome black sockets so want to be careful!!
 
image.jpg
 

Attachments

  • image.jpg
    358.8 KB · Views: 57
Looks like you have the original ring (reds and blacks) then someone spurred off the ring in new cable (brown and blue)

Reds/Brown
Black/Blue
Green Yellows
 
You can either put the earths into one terminal or two in one and one in the other it doesn't matter as the terminals are connected together.
 
That wiring (the red and black bit) is over 50 years old. Might be time to think about replacing the bits of the installation not on show, rather than just the decorative bits.
 
A rewire seems extreme. No reason why that black and red won't pass IR tests.
Not as such, but the number of points fitted in the '60s falls well short of what most people require today, and I'd almost guarantee that further inspection would unearth some very dubious modifications and additions.
 
Not as such, but the number of points fitted in the '60s falls well short of what most people require today, and I'd almost guarantee that further inspection would unearth some very dubious modifications and additions.
Why limit that to the 60's? Could easily apply to late 80's and early 90's and well beyond. With modern builds it seems spec is low to hit for extra's left right and centre. Was on one today, 4 bed done around 2012, master bedroom and the big bedrooms 2 double sockets per room, small bedroom had 1. At least it was double sockets mind.

@westward10 may appreciate this...SHOCKING
 
Parker Morris report in 1961 set the minimum number of sockets, etc in a dwelling. Not sure if it's been superseded.
My childhood home had two singles in each bedroom, opposite diagonal corners. Nothing on landing. Single in hallway downstairs.. I think only 4 singles in living room, even behind the telly and I really can’t remember the original kitchen.

Kept Woolies going in selling 4 way adaptors in those days.
 
Luxury! I currently have 2 singles in each bedroom, a single in the hall, and 2 doubles and a single in the living/dining room.
There are some old heater outlets i could repurpose, but adding new sockets would be a tedious and messy affair as all the internal walls are brick. My PC setup has a a 6-way trailing socket, 2 4-ways and a 5-way, with only a couple spare, all hanging off a single wall socket...I really need to sort this.
 
Oh there’s a lot more now, with changing singles to doubles, repurposing unused storage heater points, new kitchen and having an electrician as a son…
 
Ok I’m new to this so please don’t anyone listen to my advice here but if you might humour me a while can I take an opportunity to check my learning on this basic post please? I’m hoping someone might be kind enough to confirm (and also I need to make several posts before I can apply to join the trainee forum)? Thanks in advance for any help :)
put the;
2red together with the brown conductors into L,
2black together with blue conductors into N
3 cpc (green/yellow) conductors in any combination (1in1,2in other or whatever) into any of the 2 earth terminals
 
Ok I’m new to this so please don’t anyone listen to my advice here but if you might humour me a while can I take an opportunity to check my learning on this basic post please? I’m hoping someone might be kind enough to confirm (and also I need to make several posts before I can apply to join the trainee forum)? Thanks in advance for any help :)
put the;
2red together with the brown conductors into L,
2black together with blue conductors into N
3 cpc (green/yellow) conductors in any combination (1in1,2in other or whatever) into any of the 2 earth terminals

Yes indeed.
 
My childhood home had two singles in each bedroom, opposite diagonal corners. Nothing on landing. Single in hallway downstairs.. I think only 4 singles in living room, even behind the telly and I really can’t remember the original kitchen.

Kept Woolies going in selling 4 way adaptors in those days.

Luxury! I currently have 2 singles in each bedroom, a single in the hall, and 2 doubles and a single in the living/dining room.
There are some old heater outlets i could repurpose, but adding new sockets would be a tedious and messy affair as all the internal walls are brick. My PC setup has a a 6-way trailing socket, 2 4-ways and a 5-way, with only a couple spare, all hanging off a single wall socket...I really need to sort this.
At the risk of turning this into a remake of a Monty Python sketch, I don't think there was any room in my childhood home that had more than a single 13A socket, or any room, except the bathroom, without one.
Wife's childhood home was even worse. Upstairs just had a single 13A socket on the landing, and none at all in the bedrooms. As an electrician in my early 20s, it was while fitting extra sockets upstairs, and an electric shower, that I was shadowed by the 17 year old daughter of the house...
 
True, might have been red & black up to 2004/6

However, it seems to have stranded conductors so I guess it is imperial size cable and not the 2.5mm T&E?
2.5mm² stranded T&E was manufactured until at least 1983/4 by AEI and was actually specified by some customers in their tender documents at the time
 
Most of the imperial cable I've dealt with has been tinned. Did this apply right up to the end of production?
The cable in the pic isn't tinned.
Did the stranded 2.5 have a stranded cpc as well?
 
The house of my first memory was in Highbury and had gas mantles 😎 we rented the ground floor off two old ladies that lived upstairs and we where allowed to use the bathroom once a month, our loo was outside with the mangle and my mother would wash my brother and I in the wood fired copper in the scullery which was our kitchen, my first school was Drayton Park, not far from Arsenal, this was in Melgand Road just up from the library in Holloway Road.
 
Last edited:
Just found this Datasheet

On page 3 it shows *H6242YST 2 x 2.5 Nominal stranding of conductor 7 / 0.67 & CPC 1 / 1.38 (1.5mm²)

So stranded 2.5 is still manufactured and the sheet also shows stranded 1.5
 
Last edited:
Just found this Datasheet

On page 3 it shows *H6242YST 2 x 2.5 Nominal stranding of conductor 7 / 0.67 & CPC 1 / 1.38 (1.5mm²)

So stranded 2.5 is still manufactured and the sheet also shows stranded 1.5
Interesting, has anyone seen it stocked though?

I can see some advantages to stranded 2.5mm as more flexible so easier for pulling though conduit, etc, but that is not really done often.
 
Just found this Datasheet

On page 3 it shows *H6242YST 2 x 2.5 Nominal stranding of conductor 7 / 0.67 & CPC 1 / 1.38 (1.5mm²)

So stranded 2.5 is still manufactured and the sheet also shows stranded 1.5
I have not seen sigle strand 2.5 outside T&E it all seems to be multi strand in Europe, stocked by TLC in the UK.
 
I have not seen sigle strand 2.5 outside T&E it all seems to be multi strand in Europe, stocked by TLC in the UK.
Conduit cable certainly is usually stranded in 1.5mm & 2.5mm where T&E is single.

I don't see stranded T&E on TLC site?

EDIT: For 1.5mm/2,5mm as bigger is usually stranded
 
For some reason I have seen a lot of stranded 2.5 T&E in schools new and old colours the cpc is always solid.
 

Reply to Double socket problems!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
622
Hope someone can help, ran 3 spotlights and double switch all wired with 1.5mm twin and earth cable from my upstairs bedroom to switch ceiling...
Replies
7
Views
317
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
773
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
865
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
324

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock