hi all
job this morning downstairs /landing lights not working ...lights flickered and went off last night ( trip stayed on)..mcb working (another circuit connected to it works fine) tested this morning (no cpc ) joined line and neutral at board tested at ceiling rose continuity ok .. but no power to any points
any advice what to check for ?
 
hi all
job this morning downstairs /landing lights not working ...lights flickered and went off last night ( trip stayed on)..mcb working (another circuit connected to it works fine) tested this morning (no cpc ) joined line and neutral at board tested at ceiling rose continuity ok .. but no power to any points
any advice what to check for ?
It will be the same circuit if it's connected to the same OCPD!
 
Not 100% sure on what you are saying here. Do you have continuity on line and neutral from supply to the roses that are not working? Continuity tests will find this problem.
Is it 3 plate, or neutral at switch?
 
Not 100% sure on what you are saying here. Do you have continuity on line and neutral from supply to the roses that are not working? Continuity tests will find this problem.
Is it 3 plate, or neutral at switch?


3 plate at rose...continuity on line and neutral at roses that i checked but no power ....surely if continuity ok power should be there
 
You can't have continuity of the line and neutral supply or else the light would be lit!
 
Quick lesson... ohms law... voltage drop is proportional to the current flowing. Under load a high resistance joint may drop enough to prevent the lamps from lighting (depending on the type of lamps).

Depending on what test equipment you are using, it may or may not reveal high resistance joints... depends how much current it uses. So, if you're using a continuity function on a multimeter or AVI, it's not likely to provide reliable results... you should use the low ohms mode of an MFT or suitable stand alone meter as this will use quite a high test current (high test current = bigger voltage drop on small resistances).
 
Should have added, working systematically, work your way along the circuit checking for loose connections (physically and visually) and testing the resistance of each conductor (using a long lead test back to the CU). Pay particular attention to any lights that are not ceiling roses as these are likely to have concealed junctions or choc block attrocities.
 
agreed ...but i have and its not
What else is protected by the OCPD controlling the lights that aren't working. Reconnect the leg that you have dissed and as SC says check lights and switches for loose or broken connections.
 
It may be a stupid answer but have you actually operated the switch when testing.

The way I read it was that you have continuity between loop live and neutral and not switched live and neutral.
 
I was going to state what is above aswell. Are you testing at the switch side of the celing rose? Not the loop in the middle? Also have you checked the continuity of the flex drop aswell as there may be a loose wire in the drop its self and are you sure the drop is not damaged. Try changing it.
 
Unlikely to be a switch drop, as all the lights on that circuit have gone out. Time to start again with the continuity tests.
 
Hum .... interesting.

Linking L & N and using a meter is the best approach, so:

Did you make notes of the readings from different fittings?

Have you tried the same with the neutral not linked at the CU? This may sound odd but you may have a parallel path via another neutral.
 
hi all
job this morning downstairs /landing lights not working ...lights flickered and went off last night ( trip stayed on)..mcb working (another circuit connected to it works fine) tested this morning (no cpc ) joined line and neutral at board tested at ceiling rose continuity ok .. but no power to any points
any advice what to check for ?
What meter were you checking continuity with?
 
Is there a value associated with the ‘continuity’ you have tested?
Personally I have a few different testers having very different toloetances as to what they would show as being ‘continuity’ in the sense you are using the word.
 

Reply to downstairs lights looking for advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
608
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
737
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
458
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
627

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock