Discuss Drayton 3 port valve - confirmation of fault? in the Central Heating Systems area at ElectriciansForums.net

A

alanl

Called out to newly installed boiler, using the old Drayton MA1 3 port valve.
When HW is on, CH is also on.
Checked all connections/wiring, all seemed connected correctly.
But, getting voltage at the white cable (HW on) at the valve.
Clearly something wrong there, as there should be no voltage unless CH is calling.

So, long story short, 'HW on' cable was not live when disconnected from valve.
But white wire was live, clearly getting a back-feed from somewhere.

Before I go and order a new actuator, I'd like confirmation that it is likely to be a faulty microswitch on the valve causing this fault, or have I missed something?

Thanks
Alan.
 
Yes, that is my point, white is live, when it is not connected to anything.

Checked the feed to white, (disconnected from white) and it is live when calling, dead when not.
So that is correct.
Voltage is getting to white from inside the valve, I suspect a faulty microswitch, or faulty circuit board.
 
As a follow up, yes, it was a faulty actuator.
I havent had time to take the old one apart yet, but I suspect a faulty microswitch inside it.
 
Last edited by a moderator:
Don't forget that if the valve is in the 'manual' position mid position) you will get feed back through the switch if hot water is called for and heating is not.
 
I've since took it apart, and found the micro switch was jammed down, meaning the CH would always be on when there was power to the valve.
 

Reply to Drayton 3 port valve - confirmation of fault? in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
619
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hi I have a heatmiser uh4 wiring centre and a grant vortex combi condensing oil boiler, doing the heat and HW in a small cottage, the room stats...
Replies
1
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock