Hello, I’ve not come across this symbol on an RCD before. It is the rectangle box with a line through the middle, which means fuse. Could this mean that the RCD could be fused to 80a? If that’s the case I know it would be classed as an RCBO but definitely doesn’t look like one! If it isn’t fused/doesn’t have overcurrent protection it would need upgrading to a 100a rated RCD because the cut out fuse is 100a. Thank you in advance.... (I cannot upload a picture so have had to find one the same on the internet).
https://willrose-electrical.co.uk/p...0ma-double-pole-80a-lexic-trip-legrand-r8030/
 
That is just an RCD, not an RCBO. As you suspect, the 80A is its current rating, not a tripping current. Im is the making current and 10kA the breaking capacity when backed up with a suitable fuse or M10 rated OCPD*. On an RCBO the In rating and characteristic curve will both be shown, and the schematic will show the thermal and magnetic tripping elements.

* E2A, that I think must be 100A or less. Therefore I believe that if the supply fault current is less than 10kA and the RCD is protected against overload downstream (e.g. by feeding circuits with a total In <100A) then a 100A BS88 fuse upstream fully protects the RCD. If the total load In >100A then this specific case doesn't apply.
 
Last edited:
If you mean the one that has 10000 next to it on the linked RCD, then I believe it means the breaking rating in Amps. Or the largest number it can take on a fault and still function.

Used mostly when checking whether it can cope with the pfcc/pscc in a given installation. (Though Type testing usually ups it to 16kA for a consumer unit assembly)

Edit: Beaten to it by Lucien!
 
What loads will be going on the RCD? You are not supposed to solely use diversity factors (536.4.202) but if you only have 2 x 32A and 1 x 6A on it then you could use an 80A RCD. (depending on Manufacturers instructions)

Hager fairly recently starting putting 100A RCDs in all their premade domestic boards fairly recently citing a regulation, but there are still plenty of manufacturers selling dual RCD boards with 80A RCDs.

This document sums it up fairly well for Hager, but not sure what other manufacturers specify.
 
Good, that tallies with my observation above. 536.4.202 is the new bit that rules out relying on diversity, which was historically exploited for main switches and RCDs.
 
Thank you very much for the helpful responses. The total load going on the RCD is 92A. I believe it would have once been suitable until someone added a 16A radial for a garage feed. I will recommend that this RCD is uprated to 100A. Thanks again everyone!
 
If you mean the total In of the downstream breakers is 92A, certainly in a domestic situation it is most unlikely to see anywhere near that and it would pain me to code it, but on paper it's not compliant.
 

Reply to Due to this symbol does this RCD have overcurrent protection? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
410
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
From another thread: I'm thinking about this and it's got me all confuzzled. Don't fuses protect anything downstream ie my laptop's charger...
Replies
16
Views
2K
Hi all, Apologies for long post. I have been asked to change two ceiling lights, an extractor fan and shaver socket in a bathroom, this is like...
Replies
5
Views
800
Hi I’m looking for advice on the following: I’ve yet to contact my local council about installing a light in Zone 1 of my bathroom (this due to...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock