Just want to than you for your advice.

It is clear that I really cant explain myself, and that isn't helping you to aid me.

Personally I have never seen an RCD trip on a no trip before when it hasn't been a faulty RCD. I also understand that my terminology is not great, and that must be frustrating.

The circuits I was testing normally have several computers, florescent tube fittings and 12v transformers on it. When testing the circuits, they were all disconnected and all readings were fine. I then reconnected and moved on to an under floor heating circuit, disconnected the load side of the FCU and tried to do the Zs test at this point the RCD tripped. If I turned off all MCB's it still tripped, if I removed all the nuetrals for the circuits Im not testing, the readings are good.

The original point for the EICR is that it by design has 15mA leakage and was strictly asking if this was a c3 with further investigation, or should I just leave it as is.

If this is still confusing, then I will not waste anymore of your time, but thank you for not being nasty about it.
 
Just want to than you for your advice.

It is clear that I really cant explain myself, and that isn't helping you to aid me.

Personally I have never seen an RCD trip on a no trip before when it hasn't been a faulty RCD. I also understand that my terminology is not great, and that must be frustrating.

The circuits I was testing normally have several computers, florescent tube fittings and 12v transformers on it. When testing the circuits, they were all disconnected and all readings were fine. I then reconnected and moved on to an under floor heating circuit, disconnected the load side of the FCU and tried to do the Zs test at this point the RCD tripped. If I turned off all MCB's it still tripped, if I removed all the nuetrals for the circuits Im not testing, the readings are good.

The original point for the EICR is that it by design has 15mA leakage and was strictly asking if this was a c3 with further investigation, or should I just leave it as is.

If this is still confusing, then I will not waste anymore of your time, but thank you for not being nasty about it.

If you have a 15mA background leakage, i'll ask if high integrity earthing has been applied to these circuits?? Many here would say that circuits supplying primarily IT/computer loads shouldn't be provided with RCD protection, but that's open for discussion....
 
If you have a 15mA background leakage, i'll ask if high integrity earthing has been applied to these circuits?? Many here would say that circuits supplying primarily IT/computer loads shouldn't be provided with RCD protection, but that's open for discussion....

High integrity earthing has been applied. Oddly enough the two RFC that supplied the computers were mixed up and missing one leg at the start.
 
you could bridge the RCD to get your Zs readings on high current. don't forget to remove the bridging links immediately after, though.
 
Well if high integrity earthing has been applied, why are you questioning the 15mA inherent leakage?? If RCD has also been provided then as stated early on, test the RCD at it's disconnected load terminals!! You only need to test the RCD device itself, ''NOT'' the circuit or circuits that it is protecting. Never test an RCD downstream on the circuit wiring when conducting official results that will form part of a test report. Fine for fault finding and the like, but not for testing the permissible operational parameters of an RCD device!!
 

Reply to Earth leakage and EICR's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
709
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock