This has messed my head up so much I’m not sure I can even explain it properly but hopefully someone out there may give me ideas of what to do next…


Had a call out to a house today with the owner (polish if it has any relevancy) saying he was getting small shocks off taps & was getting a reading on his socket tester which showed green green red which doesn’t have an explanation on the tester and the RCD was not tripping.

It is an 8 circuit setup over duel RCD. The owner said he had different mcbs set up for different sockets (1 for tv, 1 for comp room, 1 for lounge etc).

Although the ccu had only been in a year it had NO labelling (inc circuits), no installation certificate etc…

I tested the socket ring (32A) end to end r1, r2 & rn but with no continuity suggesting it was actually 2 radials.

I tested continuity (all unplugged) and found r1 & rn = 10 ohms, rn-r2 = 0.56 ohms, r1-r2 <999.

Checked sockets (which I had to break two of cos they were tiled in with broken screws) & found one had L/N reversed.
Found a socket with four spurs off it (to boiler switch, lounge socket*, upstairs, utility cupboard). The boiler switch had three spurs off it (to boiler, utility lights, upstairs socket). * which then had a spur to a lounge wall light

I did a alternative IR test on the boiler which failed (I believe due to the bonding becoming live)

I isolated the ‘faulty’ radial at ccu at L,N & E and tested the other sockets which showed the earth still live (50V). I isolated each & every circuit at a time at the mcbs but still got 50V on the other sockets. There was 50V getting back to the earth so I removed each cpc one at a time but still got 50V going back to the socket. Did the same with neutral & got the same result.

Alas I couldn’t think clearly any more & needed to eat so have left it for now.

I have 4 ideas at the moment:
1) two way landing lights using the cpc as live conductor. But would this affect the neutral?
2) another terminal wired with wrong polarity. But this wouldn’t make the cpc live? 3) A big screw going through the L/N & E
4) Water infiltration under the floor into a junction box.

Anyone come across anything similar with any tips and can save me having to test every circuit individually? It’ll take me ages just to label which circuit is which – especially as they seem to have this fault linking most of them together.

p.s. I replaced the RCD the ‘ring’ was on which wasn’t tripping, even at the button.
When I went to test the RCD I kept getting CON on my Megger (“wrong connection to instrument”)
 
This has messed my head up so much I’m not sure I can even explain it properly but hopefully someone out there may give me ideas of what to do next…


Had a call out to a house today with the owner (polish if it has any relevancy) saying he was getting small shocks off taps & was getting a reading on his socket tester which showed green green red which doesn’t have an explanation on the tester and the RCD was not tripping.
If he's getting shocks there's 2 faults. Firstly there's something floating outside the equipotential zone and not bonded, secondly there's probably an IR fault causing an earth leakage current assuming it's not functional leakage.

It is an 8 circuit setup over duel RCD. The owner said he had different mcbs set up for different sockets (1 for tv, 1 for comp room, 1 for lounge etc).

Although the ccu had only been in a year it had NO labelling (inc circuits), no installation certificate etc…

I tested the socket ring (32A) end to end r1, r2 & rn but with no continuity suggesting it was actually 2 radials.

I tested continuity (all unplugged) and found r1 & rn = 10 ohms, rn-r2 = 0.56 ohms, r1-r2 <999.
These test results make no sense.
I'd suggest you sort out the circuit first by either reestablishing the ring or making it into 2x radials on separate MCB's. Once you've done this then retest.


Checked sockets (which I had to break two of cos they were tiled in with broken screws) & found one had L/N reversed.
Found a socket with four spurs off it (to boiler switch, lounge socket*, upstairs, utility cupboard). The boiler switch had three spurs off it (to boiler, utility lights, upstairs socket). * which then had a spur to a lounge wall light
Sounds like you're going to be busy.

I did a alternative IR test on the boiler which failed (I believe due to the bonding becoming live)
I don't understand how bonding can become live. Fix the bonding.

I isolated the ‘faulty’ radial at ccu at L,N & E and tested the other sockets which showed the earth still live (50V). I isolated each & every circuit at a time at the mcbs but still got 50V on the other sockets. There was 50V getting back to the earth so I removed each cpc one at a time but still got 50V going back to the socket. Did the same with neutral & got the same result.
Instead of chasing phantom voltages on live circuits and disconnecting CPC's which is probably going to result in someone getting a whack, rather concentrate on each circuit one by one, do the dead tests and fix the issues they show up.

Alas I couldn’t think clearly any more & needed to eat so have left it for now.

I have 4 ideas at the moment:
1) two way landing lights using the cpc as live conductor. But would this affect the neutral?
2) another terminal wired with wrong polarity. But this wouldn’t make the cpc live? 3) A big screw going through the L/N & E
4) Water infiltration under the floor into a junction box.

Anyone come across anything similar with any tips and can save me having to test every circuit individually? It’ll take me ages just to label which circuit is which – especially as they seem to have this fault linking most of them together.

p.s. I replaced the RCD the ‘ring’ was on which wasn’t tripping, even at the button.
When I went to test the RCD I kept getting CON on my Megger (“wrong connection to instrument”)
You're running yourself around in circles.

No, there's no quick way out. Do the dead tests and fix the issues on each circuit one by one. Check and test the bonding.
 
Hi dude,Pretty well covered^,have you any results for test prior to above? Incomer type,earth arrangement etc?

You may have got a bit ahead of yourself...a methodical approach is required,when faced with a myriad of issues,such as described.

Not jibing you,but you mentioned changing an RCD,but did not list the testing on that component.

The customers' nationality is of no consequence whatsoever. His possession and use of a suck-it-an-see,might be...:smartass:
 
Thanks for your input guys.

To try and answer your points:

Davesparks, I tested with a voltage tester & also my megger.

Marvo,
P1) Quite possible
P2) I did separate the ‘ring’ onto 2x 20A mcbs & no, the readings made no sense (but nothing in that installation did).
P3) I’m already too busy, ergo me working on a Sunday at 5pm in the dark lol.
P4) I’m thinking a cpc has become live & working back to the ccu & bonding (then tracing back to the boiler?)
P5,6) I, of course, put the cpcs back ensuring no one was able to interfere while I tested. And you are right. I told him I would have to test each circuit one at a time (which will take a while, especially as there are so many radials & downlights and nothing is labelled)

Peg,
It’s tncs, 1361.
I tried to do it methodically but was coming across so many issues it kept taking me back to square one (and into the darkness – god, I hate winter!).
I tried doing an RCD trip test ½ & 1x but my megger was coming up ‘con’ which is wrong connection to instrument. I tried doing the RCD test button which did nothing so I swapped the RCDs around resulting in the test button now working (but not on the supposedly faulty one still - which I have swapped for a spare).
Nothing against poles, I just got the feeling his mate (if not him) had done the ccu & wondered if they had a habit of doing certain practices that might help explain this.
I guess it's back to square one testing each circuit. If he had this done on the cheap he's going to regret it now.

Just to add. He has two 2.5mm radials, one to his tv & one to his computer upstairs. Both on 32A.

Just something else I had to deal with ontop of the earth fault, the socket wired with reverse polarity, the faulty RCD, sockets with broken screws and glued in, 9 unmarked circuit (6 of which are sockets) & the multiple spurs off 1g sockets :dizzy2:

Incidentally, I tried identifying some circuits with a circuit finder but it was indicating several circuits including lights. Any ideas why this may be?

cheers again
 
Last edited:
I think you are getting carried away with it. You are there to find out why the owner is getting shocks. That will mean verifying earth continuity on each circuit and then IR testing each circuit,earthing and bonding etc. All the other issues you come across such as broken rings etc are incidental and should be recorded and made known to the client but you are under no obligation to fix or investigate.
 
I think his nationality might be an issue - sounds like some of his countrymen maybe installed the circuits - part p they don't give a hoot
I have seen it loads of times especially in London.
Not racist but just my observations

As others have said start at the beginning and break it down into sections of testing , otherwise you can be chasing your tail
Don't forget to tell the customer this us going to be expensive - saves on the startled face when you present the bill !!
 
Hi dude,Pretty well covered^,have you any results for test prior to above? Incomer type,earth arrangement etc?

You may have got a bit ahead of yourself...a methodical approach is required,when faced with a myriad of issues,such as described.

Not jibing you,but you mentioned changing an RCD,but did not list the testing on that component.

The customers' nationality is of no consequence whatsoever. His possession and use of a suck-it-an-see,might be...:smartass:

Yes, most customers have a socket and see.
 
This has messed my head up so much I’m not sure I can even explain it properly but hopefully someone out there may give me ideas of what to do next…


Had a call out to a house today with the owner (polish if it has any relevancy) saying he was getting small shocks off taps & was getting a reading on his socket tester which showed green green red which doesn’t have an explanation on the tester and the RCD was not tripping.

It is an 8 circuit setup over duel RCD. The owner said he had different mcbs set up for different sockets (1 for tv, 1 for comp room, 1 for lounge etc).

Although the ccu had only been in a year it had NO labelling (inc circuits), no installation certificate etc…

I tested the socket ring (32A) end to end r1, r2 & rn but with no continuity suggesting it was actually 2 radials.

I tested continuity (all unplugged) and found r1 & rn = 10 ohms, rn-r2 = 0.56 ohms, r1-r2 <999.

Checked sockets (which I had to break two of cos they were tiled in with broken screws) & found one had L/N reversed.
Found a socket with four spurs off it (to boiler switch, lounge socket*, upstairs, utility cupboard). The boiler switch had three spurs off it (to boiler, utility lights, upstairs socket). * which then had a spur to a lounge wall light

I did a alternative IR test on the boiler which failed (I believe due to the bonding becoming live)

I isolated the ‘faulty’ radial at ccu at L,N & E and tested the other sockets which showed the earth still live (50V). I isolated each & every circuit at a time at the mcbs but still got 50V on the other sockets. There was 50V getting back to the earth so I removed each cpc one at a time but still got 50V going back to the socket. Did the same with neutral & got the same result.

Alas I couldn’t think clearly any more & needed to eat so have left it for now.

I have 4 ideas at the moment:
1) two way landing lights using the cpc as live conductor. But would this affect the neutral?
2) another terminal wired with wrong polarity. But this wouldn’t make the cpc live? 3) A big screw going through the L/N & E
4) Water infiltration under the floor into a junction box.

Anyone come across anything similar with any tips and can save me having to test every circuit individually? It’ll take me ages just to label which circuit is which – especially as they seem to have this fault linking most of them together.

p.s. I replaced the RCD the ‘ring’ was on which wasn’t tripping, even at the button.
When I went to test the RCD I kept getting CON on my Megger (“wrong connection to instrument”)

has same green green red on socket tester today. fault causing this was a blown cable ( L-E short which had melted the cpc and the L wasn't much better). still got no earth on several sockets but socket tester show 3 greens. moral is not to trust a socket tester. they're only a basic tool. there's 55V on the cpc of 6 sockets till we dig up bedroom floor tomorrow. ( thee duff leg is isolated atm, btw).
 
Last edited:
has same green green red on socket tester today. fault causing this was a blown cable ( L-E short which had melted the cpc and the L wasn't much better). still got no earth on several sockets but socket tester show 3 greens. moral is not to trust a socket tester. they're only a basic tool. there's 55V on the cpc of 6 sockets till we dig up bedroom floor tomorrow. ( thee duff leg is isolated atm, btw).

Which backs up something i was told as a lad...if something/someone is not telling you the FULL story...they could be telling you ANY story :blush5:

Although it is surprising,the number of supposedly "authority" institutions,who routinely send out their operatives,with such devices.
 
Is it TNCS by any chance?
Possible lost supply neutral and bonding has effectively become the neutral.....??
This may be completely out as you haven't mentioned proving the supply 1st.
Start from the beginning.
 
It is tncs rich.250. Interesting point & one I haven't come across yet. I did do a polarity check on the incoming which I don't think showed anything wrong if memory serves. I will double check it when I go back tho. Where would the Neutral be lost? It would have to be between the incomer & neutral bar wouldn't it? cheers
 
It is tncs rich.250. Interesting point & one I haven't come across yet. I did do a polarity check on the incoming which I don't think showed anything wrong if memory serves. I will double check it when I go back tho. Where would the Neutral be lost? It would have to be between the incomer & neutral bar wouldn't it? cheers

If you loose a neutral it will normally be a connection on a overhead line.
The exact reason most DNOs will refuse to provide an earth now on overhead supplies.
Making nearly every new supply in my area TT!!
 
.... SO, I managed to get back to have a look at it today.

I did dead testing on all circuits (which wasn't easy as the house has radials criss-crossing to sockets all over the place & hidden sockets in cupboards conceiled with clothes etc, :bomb: ) and all the circuits tested ok. I did however find doing a alternative IR test (LN-E 250v) on the boiler resulted in <1Mohm but this was disconnected during other tests anyway.

I'm still getting up to 40V on the earth though. I observed it starts as 0 with all circuits dead and goes up steadily to 40V as each circuit is reenergised.

Any suggestions my good fellows?
 
Hi,when you say "on the boiler",do you mean the fixed wiring to the boiler,with boiler disconnected,or.....

Also,what were you measuring between,when you observed the increasing voltage to earth? Ta
 

Reply to Earth leakage on sockets in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
747
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
599
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock