Discuss Earth Loop / Dimmer in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
52
Had a strange one today, would appreciate folks take on it. I'm probably missing something obvious!!
Installing some downlights via metal dimmer switch.
Earth loop impedance was 50 ohms at last light!, at switch it was about 1.5 ohms. Dimmer fully up, voltage at light around 230 . Bypass switch and readings come down to 1.8 ohms.
Why would a dimmer cause this?, anyone else come across this ? Am I being a total idiot ( probably!!, it's been a hard week!)
Thanks in advance for any advice.
 
dimmer electronics will throw your readings down the pan. need to be bypassed for efli testing and IR tests.
 
Thanks folks.
My confusion is, if I test without the switch and get 1.8 , but when switch is fitted it's nearer 50, what is the true reading ?
When the switch is fitted , is the true ELI 50 ohms or is that just a misleading result .? I hope I'm making sense here.
Thanks again, much appreciated.
 
Thanks folks.
My confusion is, if I test without the switch and get 1.8 , but when switch is fitted it's nearer 50, what is the true reading ?
When the switch is fitted , is the true ELI 50 ohms or is that just a misleading result .? I hope I'm making sense here.
Thanks again, much appreciated.
Your bog standard dimmer switch only lets current through on part of the cycle, it is effectively chopping it which reduces the RMS current hence it "dims".
Your tester will not cope with this and will either give no reading or a false reading. Under a fault condition the internal triac should fail and allow this fault current to flow and hopefully trip the OCPD. Be careful doing EFLI tests through a dimmer as this can also damage the triac. So your reading of 1.50 is correct.
 
easy enough to check. bybass the switch with the circuit de-energised then get a R1+R2 reading.
 

Reply to Earth Loop / Dimmer in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
426
Hi, Would like to change existing single pole light switch to attached dimmer switch. I have a live and neutral coming from consumer unit, and...
Replies
8
Views
2K
This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed...
Replies
1
Views
1K
Hello everyone. Thank you in advance for any help you can provide. I tried installing a dimmer to a 3-way circuit. The dimmer has a hard...
Replies
3
Views
1K
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
883

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock