What is the proper procedure for ELI testing circuits with UPS back up, ie radial circuits under computor room floors?
Do you test with the mains bypass connected? with the UPS/ mains in normal operation? or in UPS status only?, ie mains failure.
Thanks.
 
What is the proper procedure for ELI testing circuits with UPS back up, ie radial circuits under computor room floors?
Do you test with the mains bypass connected? with the UPS/ mains in normal operation? or in UPS status only?, ie mains failure.
Thanks.

Any EFLI tests through a UPS will give artificially high readings from the output stage of the UPS.

The test should be carried out on bypass and values should be as expected for the system parameters.

The UPS will be fault limited on battery operation and will usually shut down after say 100ms to protect the inverter and prevent any damage to cables etc. being caused by the fault.

This automatic shutdown is type tested as part of the EN 50091 and EN62040 standards.
 

Reply to Earth loop tests on circuits with UPS backup in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
823
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
671
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock