Discuss Earth Rod - Advice please! in the UK Electrical Forum area at ElectriciansForums.net

K

Kaydee

Hi, I am not an electrician, but need some advice from one, if you wouldn't mind helping, please?
We've just paid £3,500.00 to have a 3-bed semi completely rewired and are told the job is now finished. (We paid half up front, they now want the other half).
Outside the front of the property, they've installed what they've told us is an 'earth rod'. There's a long piece of thick, black, plastic tubing, leading to a unit that is fixed to the ground.
It comes almost onto the driveway, right in front of an attractive bush to the side of the front door and looks really unsightly.
We questioned them about it and were told it was 'regulation' that it had to be installed that way, a metre from the house, in a straight line.
I haven't seen anything like this in front of any other property, including ones that have been recently rewired, but want to check my facts before challenging them on this.
Is this normal? Can it/should it be buried underground?
 
Thank you, telectrix, that's the sort of thing I HAVE seen outside other houses.
In your opinion, would the total cost we have been charged cover the cost of this? We've had new board put in, 4 spotlights in the kitchen and the rest is just basic rewiring with a couple of extra sockets.
I'm only asking because I want to be prepared if I challenge the electician and he says it'll cost extra.
 
Can you post a picture of the earth rod's current set up? Is your propery in a remote location or do you have other properties close by.? Hard to comment on the price without a full spec but it doesnt sound that unreasonable.
 
seeing this from both sides, as it were,

1. there is payment outstanding, so from your point, you have a bargaining chip. you could insist that he alters it to get paid.

2. from his point of view, he's done what he quoted for, so is entitled to the outstanding payment.

playing devil's advocate, considering the above, I'd advise that you speak with him, explain your disappointment with how the earth rod has been installed, and come to a n agreement to alter it whereby you pay him a bit extra, albeit not as much as it would normally cost. the key word is negotiation. then you'll maintain a good relationship for any future works required.
 
Without sounding out of turn, the electrician should have known that an earth rod needed installing upon surveying the property during quoting purposes. The method you described is quite common and tends to be the cheapest easiest solution. This said, personally I would have discussed this with the client prior to commencing work and made provisions in the quote to install the rod within the regs as per clients spec. As its a "basic" re-wire and we know nothing of your agreed contract with the electrician, its difficult to make comment about your situation.
My guess is he/she will advise that the alterations you require will be charged extra to the original quote if nothing was agreed prior.
 
you post pics by using the "upload a file" next to the reply button, but i think you need a minimum number of posts to be able to do.
 
I'd also like to see a pic. has he installed a decent rod, or just a 3ft. "twig". and is the Ra/Ze suitably low.
 
service head or cut-out:
images

contains the supplier's fuse.
 
Without sounding out of turn, the electrician should have known that an earth rod needed installing upon surveying the property during quoting purposes. The method you described is quite common and tends to be the cheapest easiest solution. This said, personally I would have discussed this with the client prior to commencing work and made provisions in the quote to install the rod within the regs as per clients spec. As its a "basic" re-wire and we know nothing of your agreed contract with the electrician, its difficult to make comment about your situation.
My guess is he/she will advise that the alterations you require will be charged extra to the original quote if nothing was agreed prior.
I think you're probably right David, but as he knew we were preparing the house for marketing it, I would have hoped he would have discussed this sort of thing with us, which he didn't!
 
Without sounding out of turn, the electrician should have known that an earth rod needed installing upon surveying the property during quoting purposes. The method you described is quite common and tends to be the cheapest easiest solution. This said, personally I would have discussed this with the client prior to commencing work and made provisions in the quote to install the rod within the regs as per clients spec. As its a "basic" re-wire and we know nothing of your agreed contract with the electrician, its difficult to make comment about your situation.
My guess is he/she will advise that the alterations you require will be charged extra to the original quote if nothing was agreed prior.
I think you're probably right David, but as he knew we were preparing the house for marketing it, I would have hoped he would have discussed this sort of thing with us, which he didn't!
Can you post a picture of the earth rod's current set up? Is your propery in a remote location or do you have other properties close by.? Hard to comment on the price without a full spec but it doesnt sound that unreasonable.
earth rod2.jpg
earth rod1.jpg

I'd also like to see a pic. has he installed a decent rod, or just a 3ft. "twig". and is the Ra/Ze suitably low.
 

Reply to Earth Rod - Advice please! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...
Replies
19
Views
3K
Hi, I’m after some advice for an existing car charger that’s on one of our newly inherited sites. We have a Rolec 2x 7.2kw pedestal charger, just...
Replies
0
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
I was away at the weekend & the electrician came round to fix something. While there he decided to condemn an outdoor electrical light as he said...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock