Discuss Earth terminated outside. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
34
Hi All

Seen this on a few jobs now where they have on the Downlight fittings where the CPC is terminated outside the enclosure of the Downlight due to not having a earth connection inside. Does anyone know the reg that states that this is not permitted and earth connections should be inside enclosure. As on a EICR I would usually put down C3 but if you look at the Downlight connection side, the earth cable usually comes out the terminal enclosure single insulated and then connected on the side of the Downlight. Will look forward to responses cheers
 

Attachments

  • 3CA7E9BA-FDB0-46EE-9494-110F68868823.jpeg
    315.2 KB · Views: 58
The earth lead between enclosure and fitting is part of the fitting and therefore subject to type testing and ce certification.
fixed wiring ends at the termination point so no code, but if you want to it could be put in the notes.
 
How are they connected? If the connection is good then I would say no code.

Remember an EICR is not the same as initial verification, you are not assessing absolute compliance with bs7671.

If the connection is sound then it is neither a C1 or C2.

That leaves C3 as the only possibility, so what improvent for safety could be recommended?
 
Connections are good they are the LAP fittings where they don’t have a earth connection so they have neatly termed the L&N of the T&E folded the CPC back outside of the term box and then installed connector block and wago on some cases. This is just directly outside of enclosure then taped the earth connection back on to the T&E ?
 
Connections are good they are the LAP fittings where they don’t have a earth connection so they have neatly termed the L&N of the T&E folded the CPC back outside of the term box and then installed connector block and wago on some cases. This is just directly outside of enclosure then taped the earth connection back on to the T&E ?

My personal opinion, others will disagree, is that I wouldn't code that as long as the live conductors are properly enclosed.
 
New posts

Reply to Earth terminated outside. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Replies
37
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
645

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock