Search the forum,

Discuss Earthing a gas pipe in attached garage in the UK Electrical Forum area at ElectriciansForums.net

(gentle cough) ... Pete says no with reasons back in post #3 ...

It's even more no with the EV charging point that's in play. There are couple of ways to proceed with a domestic EV design with PME at the house, and one of them (at least) would be busted with the OP proposal.


Is the gas pipe metal or extraneous, can see that in any of the OP's posts?
 
Haven't the foggiest about EVCI, but I do see that reg 722.411.4.1 is so ambiguous as regards PME, that the grown ups have decided to clean it up a bit with the forthcoming 18th.
 
but I do see that reg 722.411.4.1 is so ambiguous as regards PME, that the grown ups have decided to clean it up a bit with the forthcoming 18th.

hum.... many of our regs are ambiguous.........................

Still want them to add a definition of "accessible" to the regs.
 
hum.... many of our regs are ambiguous.........................

Still want them to add a definition of "accessible" to the regs.

But that is a particularly vague one, 722.411.4.1, PME no you can't - well alright you can. In the draft for the 18th, the exception concerning reasonably practicable, has been deleted.
 

Reply to Earthing a gas pipe in attached garage in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock