Minimum requirements for earthing a steel framed shed? 4x3m
As3000 once again giving conflicting advice..

Incoming submain 6mm TPS 2 Core plus earth.
Incoming earth with 6mm is 2.5mm.

Section 5 of As3000 states that because my incoming is 6mm my earth to shed can be 2.5mm.

However, minimum requirement for equipotential Bonding is 4mm..

Thinking if I should do a earth rod behind shed, remove incoming earth from 6mm, create new MEN link (shed technically is an out building)..

Some advice would be appreciated.
I am a sparky fyi thanks in advance
 
I can't speak for your regs, but here in UK it's possible for bonding requirements to mean a larger earth (cpc) is needed. So it doesn't seem implausible.
I'd be surprised if your regs allowed you to create your own E and N link.
Any experts in the lucky countries regs around?
 

Reply to Earthing Arrangements in the Australia area at ElectriciansForums.net

Similar Threads

I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
541
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
This is my first posting here - I am not an electrician so please bear with me. I am trying to establish the best method to provide earthing of a...
Replies
12
Views
3K
Copied this from trainee section to see if I can get an answer, it is talked about a lot on the forum but reading through the old posts I can't...
Replies
40
Views
7K
Deleted member 26818
D
Hello everyone, I know this has come upquite often, I have gone back through the many threads relating tothis topic. The reason for wanting to...
Replies
26
Views
15K
GEOFF S
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock