Discuss Eic main fuse question in the UK Electrical Forum area at ElectriciansForums.net

Grezza

-
Reaction score
19
doing a EIC for new installation on a flat fed by a 16mm t/e.

Main fuse (100A) feeds fuse switch (63A) to cu in flat.

My question is; Ze taken from main fuse, Zdb taken from cu. but when filling in main switch, tails and earthing conductor, do I record what runs from main fuse to fuse switch or from fused switch to cu?
 
No 10mm with t/e just the 6mm cpc. Adiabatic Calcs seem OK for this and zs from sub board fine.

Spoken to 3 different sparks who all have a different approach. Considering this is a common situation, I'm surprised it's not more cut and dry.

Anyway,
Thanks for your responses
 
No 10mm with t/e just the 6mm cpc. Adiabatic Calcs seem OK for this and zs from sub board fine.

Spoken to 3 different sparks who all have a different approach. Considering this is a common situation, I'm surprised it's not more cut and dry.

Anyway,
Thanks for your responses
No gas and water all plastic then ? As for Ze it says it clearly under supply characteristics Nature of supply parameters Ze ---- Ze that part of the earth loop impedance which is external to the installation.
 

Reply to Eic main fuse question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Joining niceic and doing a sub main to a garage off a tns earthing arrangement using 6mm Swa. The question is I have 25mm tails on 100a main fuse...
Replies
20
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
289
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
700
Hi we have been asked to run a 3 phase supply into a boiler house to feed a DB fed from next to the existing meter. Would we need to install Tails...
Replies
2
Views
772

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock