Discuss EICR and RCD's. Is it a C2 or C3? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi,

My EICR is a C2 because the consumer unit does NOT have RCD's.
Is it correct?
My last EICR five years ago stated RCD as recommended.
What's changed?
The flat is on the 2nd floor built in 1997!
The electrician has quoted for a NEW Consumer Unit.

Thanks

Victor
 
Id have said c3...unless you wanted alterations but even then you could slap in an rcbo to protect the circuit you're altering.
If it met requirements when it was installed then it's fine. Feel your electrician may be trying to swindle you, dont get me wrong having rcd or rcbo protection is great but lack of does not necessarily garuntee a failure of the installation.
 
should have had RCD protection to socket circuit/s back in 1997, but stilll a C3 IMO.
 
Hello Victor,
It may be a C2 or a C3 depending on a number of factors.
I would however definitely recommend you have RCD protection as it is a life saver and well worth the £400 - £500 quote for the new consumer unit.
Also, the regulations change all the time. Within the last 5 years the regulations have required RCD protection for more and more situations.
 
My issue is he has given a C2.
My seeking opinion is to confirm that the EICR should be a C3 with
a strong recommendation in fitting RCD's or RCBO.
Is the consumer unit really C2 (Potentially Dangerous)?
How many Consumer Units in the UK that have no RCD or RCBO?
 
Not strictly true. Whether it was permissible when installed or not is completely immaterial to how safe or unsafe it is now.
No you're right but we all know a lot of sparks who go in an start sucking their teeth whilst rubbing their hands telling the client something is unsafe whilst already counting the pound signs.
Ive come across a few who tell people they need to splash out on a new cu simply because its not metal.
If nothing else was wrong and it was simply a lack of rcd the electrician could have also suggested putting an rcd before the board.
 
No you're right but we all know a lot of sparks who go in an start sucking their teeth whilst rubbing their hands telling the client something is unsafe whilst already counting the pound signs.
Ive come across a few who tell people they need to splash out on a new cu simply because its not metal.
If nothing else was wrong and it was simply a lack of rcd the electrician could have also suggested putting an rcd before the board.
A single RCD for the installation would not be a compliant solution.
 
I am confused sorry. To be compliant for the EICR to be satisfactory I need RCD's?
Nobody here knows as we have not done the inspection nor know what the issue regarding lack of RCDs actually is. There is no regulation that says "a consumer unit must incorporate RCDs", but rather a number of specific regulations that require RCDs for different applications.

You can always get a second opinion from another local electrician if you want by letting them see the report.
 
I really think we need to instil the virtues of RCD's when a member of the public asks a question rather than use strong terms about the electrician who has given a C2 for lack of RCD's. The electrician may well be wrong (perhaps not though, I have given C2's for lack of RCD's in certain situations) but rather than say he's trying to swindle you (which I doubt he is) which makes the customer focus on the electrician rather than the importance of the life saving RCD, we could say it may well be a C3 but would be a very, very good idea to get done.
 
Could I ask if you are living in the property Victor or renting it out? The reason I ask is that you have said the last EICR was 5 years ago which makes me think you are renting it out.
As a landlord I would feel much happier with my tenants having RCD protection in their house especially if there are children who may enjoy sticking knives in toasters etc etc. :)
 
Hi,

My EICR is a C2 because the consumer unit does NOT have RCD's.
Is it correct?
My last EICR five years ago stated RCD as recommended.
What's changed?
The flat is on the 2nd floor built in 1997!
The electrician has quoted for a NEW Consumer Unit.

Thanks

Victor
No it’s not correct.
There is no requirement to install RCDs in Consumer Units.

There are requirements to protect some circuits, which would require an RCD be placed in or very close to the Consumer Unit.
However, the person who conducted the Inspection should be listing the instances where RCD protection is required but not been provided, and then applying a code for each of those instances.

In many instances, RCD protection can be provided, simply by the installation of an RCD or RCBO in or close to the Consumer Unit.

Only thing that’s changed, is the person who conducted the latest inspection, wants to make money from you.
 
Can people here not discourage cowboy landlords from having RCD protection for their tenants.
I don't think anyone is doing that. Questions have been asked about a report that is based on facts and minimum requirements and the answers have mainly been in the same spirit.

Questions about reports should not be subject to assumptions, such as the landlord is a cowboy.....
 

Reply to EICR and RCD's. Is it a C2 or C3? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Replies
10
Views
832
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
715
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Replies
29
Views
4K
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
537

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock