Discuss EICR and RCD's. Is it a C2 or C3? in the UK Electrical Forum area at ElectriciansForums.net

That's all I have. Apart from a quotation to replace "fuseboard".
So do I spend many hundreds of pounds to replace the Consumer Unit?
Of course ideally ALL Consumer Units in every household should meet current regulations. This is not realistic. The bottom line is C2 (Potentially Dangerous) applicable given the data?

If a number of forum member have a c2 (potentially dangerous) opinion I will change the Consumer Unit.

Thanks for all your feedback....
 
Why would a landlord be responsible for stupid children and lazy parents?
If you have to ask that question then I don't think you'd really be able to understand the answer so probably best not to go into it.
 
You do not base findings in an EICR predicting the actions of a child. Your findings are based upon BS7671 which does not differentiate between a child and an adult.
 
According to the tick sheet there is supplementary bonding in the bathroom so no rcd required there. There is also IR values in L-N column, so everything got disconnected, all lamps removed etc to preform this test - I don't think so.
I would complain to NAPIT as the standard of the report is poor with unwarranted C2s.
All said though a board upgrade is a good recommend.
 
According to the tick sheet there is supplementary bonding in the bathroom so no rcd required there. There is also IR values in L-N column, so everything got disconnected, all lamps removed etc to preform this test - I don't think so.
I would complain to NAPIT as the standard of the report is poor with unwarranted C2s.
All said though a board upgrade is a good recommend.
Supplementary bonding does not remove the requirement for RCD protection of bathroom circuits. 30mA RCD protection of bathroom circuits may well remove the requirement for supplementary bonding though.
 
Without personally inspecting the property it’s difficult to know what has been discovered or missed by the previous inspection. I may issues a code 2, if for example,
1. Socket installed too close to a sink which can potentially be splashed
2. Any signed of water ingress
3. TT earthing system have no RCD protection
4. Outside socket (balconied) or potential to plug in and use an device outside.
5. High Zs reading not protected by RCD
6. No mechanical protected for cables (concealed <50mm, in metal framed partition, or otherwise)
7. Socket within 3m of zone 1
Or any other general safety conserns that want a risk assessment for admission of RCD (reg 411.3.3)

The fact that it’s probably got code 3 5 years ago and the recommendation goes ignored. Most people translate c3 to satisfactory and just ignore then until they get worse or C2s.
 
Last edited by a moderator:
If you have the eicr from 5 years previous did the spark ask to see it? As he’s ticked date of last inspection unknown but you say 5 years?
 
Last edited:
The tick sheet says there is RCD protection for the bathroom circuits.
Q1 it says u have 10 mmm main tails these are usually 25 or 16 min
If they are 10mm this is a C2 as they are undersized
Q2 report says u have AFDDs and surge protection
Defo not
Q3 did he inspect below the floors and above ceilings
Q4 did he carry out R1+ R2 tests as the numbers are exactly ZS-ZE
Q5 cable type 1 on report there is no type 1 it should be A
The values on the report are wrong 5.88 ??
You should send that report to NAPIT and ask for their comment and if possible post the response on the forum,,
The quality of testing is always a question raised ,
There is no rcd test results on his results
And he says there is rcd test notifications labels
 

Reply to EICR and RCD's. Is it a C2 or C3? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Replies
10
Views
838
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
737
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Replies
29
Views
4K
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
549

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock