Discuss EICR Classification codes Main bonding in the UK Electrical Forum area at ElectriciansForums.net

S

serpico4321

Hello all,

i failed a periodic inspection today and am still in debate with the client. He's obv not happy.

An NICEIC registered electrician terminated the bonding into a metal back box of a socket outlet connected to the CPC of the radial s/o circuit.

the regs say protective conductors for main bonding should run from point of entry into MET

What would you do?

i said the above and he didn't believe me. Shall I just show him the regs book or am I interpreting wrong?

P.s shocking niceic man to not bond to met
 
do you mean he took the bonding from water/gas to a socket? if so he's a numpty.
 
No none of the Regs that I'm aware of state any such thing.
The Regs as far as I'm aware stipulate that the bonding conductors should be connected to the main earth terminal.
However, that does not mean that the conductor has to be continuous, or even of the same material through out.
The Regs, actually allow for a protective conductor to be part of the structure of the building, and even in some instances pipework, as long as certain conditions are met.
 
Thanks,


For remedial works he's looking at board upgrade in August (it's about 1965 - pre met)


He would like the cert changing from C2 to C3. Would this be ok? (In your opinion)
 
Thanks,


For remedial works he's looking at board upgrade in August (it's about 1965 - pre met)


He would like the cert changing from C2 to C3. Would this be ok? (In your opinion)

You are the one signing the document, that said you've signed it so stick to your guns or go down the slippery slope of dodgy EICR's
 
Not really, stick with your coding, it may be worth checking wheter the main bonding is actually required, i .e. plastic incomer/plastic pipes.
This bond though were does it run from? from the fuseboard to a pattress, or from the incoming service to a pattress?
 
C2 - potentially dangerous i.e. dangerous under fault conditions.

I'd say that pretty much describes lack of adequate main bonding.
In fact it's one of the examples of a C2 on the ESC EICR guidance.
 
No none of the Regs that I'm aware of state any such thing.
The Regs as far as I'm aware stipulate that the bonding conductors should be connected to the main earth terminal.
However, that does not mean that the conductor has to be continuous, or even of the same material through out.
The Regs, actually allow for a protective conductor to be part of the structure of the building, and even in some instances pipework, as long as certain conditions are met.

im pretty sure it does have to be continuous with no breaks in the cable, for example if you were using the same peice of cable for 2 pipes you would cut the insulation off instead of cutting. trying too find my osg at the moment too make sure but its hiding >.< , could be wrong
 
im pretty sure it does have to be continuous with no breaks in the cable, for example if you were using the same peice of cable for 2 pipes you would cut the insulation off instead of cutting. trying too find my osg at the moment too make sure but its hiding >.< , could be wrong

That is a reccomendation, as is the 'within 600mm of the point of entry'. You couldn't really code bonding (i.e. to gas and water) that was cut and joined. Spin is right although certain conditions need to be met and it is inlikely they could be met in a house.
 
Last edited:
im pretty sure it does have to be continuous with no breaks in the cable, for example if you were using the same peice of cable for 2 pipes you would cut the insulation off instead of cutting. trying too find my osg at the moment too make sure but its hiding >.< , could be wrong

myth / fake reg / old wives tale im afraid.
 
Yes the CPC may well be under sized as a bonding conductor.
If that is the case, then it will warrent an observation and a code.
However the fact that a bonding conductor is neither continuous or direct from a to z, does not warrent an observation or a code.
 
Thank you,

The main bonding conductor has been correctly selected but is not continuous to the MET. It travels 1m from the main gas to the earth lug of a metal back box which has the 1.5mm CPC of a radial socket circuit terminated into.

Does anyone know if this Ok with NICEIC? doesn't seem specifically so with regs?
 
Thank you,

The main bonding conductor has been correctly selected but is not continuous to the MET. It travels 1m from the main gas to the earth lug of a metal back box which has the 1.5mm CPC of a radial socket circuit terminated into.

Does anyone know if this Ok with NICEIC? doesn't seem specifically so with regs?

Does the bonding conductor actually fit into the earth lug of the metal back box properly or is there another bodge lurking there?
 

Reply to EICR Classification codes Main bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
432
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
705
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
886
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock