Class 1 exposed conductive parts require earthing, if it’s earthed In situ then it’s no code.
best practice is to earth the plate directly however i dont see the issue if it’s earthed full stop by one way or another.
The regulations will not tell you how to earth it other than it requires earthing.
 
That’s a good point, I hadn’t thought of DB’s and CU’s. I think I’ve seen a couple of them with flyleads between case and cover but they might have been purpose built panels for machines and plant equipment.
Yes I hadn't considered that - Fusebox CUs do come with a flylead to the front case - but I've not seen it on other ones I've installed recently - and some of them don't have the best screw fixings *cough* BG and MK *cough* in my experience.

Though most CUs are coated steel, so I've never actually checked whether they are normally conductive when in good condition
 
the reasons i would give it a C3 is that it does not comply with MI ( as westie pointed out), and if the screws were removed for decorating or whatever, a fault on the switch would not trip MCB. therefore it "is improvement recommended. ", because i say so (smiley).
 
Class 1 exposed conductive parts require earthing, if it’s earthed In situ then it’s no code.
best practice is to earth the plate directly however i dont see the issue if it’s earthed full stop by one way or another.
The regulations will not tell you how to earth it other than it requires earthing.

The instructions with the accessory will demonstrate a cpc to the front plate.

Very interesting discussion, and I can probably see the validity of every view. Thats the 'joy' of doing EICRs to a consistent standard.

My concern would be the worry that screws might come loose or a lug break with constant use of the switch (something that doesn't happen with CUs so much).

but if an R2 to the front plate is satisfactory, then it is probably acceptable to consider that effectively earthed without necessarily needing to remove it to check the earthing connection....

However, if I remove a front plate and find the earth not to the plate, personally I'd still feel duty bound to correct it there and then to avoid any further thought.
 
All earth wires must be terminated to the back box.
An example that not all MF’s instructions are the be all and end all.
Pick shows the cpc from the cable not directly to the switch.
This does however highlight that a fly lead is required
 

Attachments

  • B849BD2C-110F-49CF-8288-BB01C7CFA772.png
    214.6 KB · Views: 22
Last edited:
the reasons i would give it a C3 is that it does not comply with MI ( as westie pointed out), and if the screws were removed for decorating or whatever, a fault on the switch would not trip MCB. therefore it "is improvement recommended. ", because i say so (smiley).
I’d be more concerned with the exposed conductive parts exposed by removing the switch personally.
 
All earth wires must be terminated to the back box.
An example that not all MF’s instructions are the be all and end all.
Pick shows the cpc from the cable not directly to the switch.
This does however highlight that a fly lead is required
It;s a M/C switch, terminate the cpcs into the back box and run a fly lead to the plate switch, how much would that cost you? not much I imagine then no need to code
 
My two pennyworth; I've always terminated cpc into back box, then a fly lead to faceplate. My thinking is if cpc become disconnected when plate is removed and/or replaced, is just that particular plate, not the rest of that circuit. I've even taken it further with multi gang switches, and put all cpc's in wago, then flylead to back box and plate, for the same reason, and also you can't successfully terminate multiple cpc's into one back box terminal.
 

Reply to EICR Code for metal light switches with earth to backbox in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
579
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
906
Hi, I've bought a "yagusmart" smart switch from Amazon and it has no earth terminal. Although there are no metal facing parts I would think the...
Replies
2
Views
650
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
640

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock