Discuss Eicr code for spurs within bathroom zone 2 but inside cabinet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Welchyboy1

-
Esteemed
Arms
Reaction score
985
Hi all

Eicr being undertaken, what code if any would you consider for this scinario

Small bathroom in a flat, with airing cupboard inside, no room for immersion and pump spurs (looks like spurs was inside airing cupboard at one point but cupboard has been made smaller to enlarge bathroom and left the spurs on the outside of the airing cupboard

The spurs sit at about 530mm from shower screen, so in zone 2, its a solid glass panel on that side of the shower enclosure so not accessible from this side

The spurs have been boxed inside a cabinet with a standard hinged door

Would you insist the hinges are removed and it is fixed with screws/chrome caps like a panel(removal for use with a tool only)
It does have a 24hr time clock inside so it will-have to be accessed from time to time

Any thoughts greatly appreciated!
 
C3 IMO. as long as you consider that there is no danger involved.
 
Thats what I was thinking but just called Napit tech they were adamant in a cupboard equates to outside zones no code
Not advisable to have a socket in there though

Good enough for me
 
No need to remove hinges etc, just fit a lock that needs a key or a tool to open it.
 
You take the shower screen into account, ie, if it's a 600 screen then zone 2 starts at the end of the screen and wouldn't touch the cupboard.
If I've understood what you are saying.
 
Thats what I was thinking but just called Napit tech they were adamant in a cupboard equates to outside zones no code
Not advisable to have a socket in there though

Good enough for me
I agree with Napit. It's outside the zones (officially) if it's in an enclosure. Not going to win any awards, though.
 

Reply to Eicr code for spurs within bathroom zone 2 but inside cabinet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, a friend has asked about fitting an electrically heated towel rail in their bathroom. The location is on the wall opposite the bath in a...
Replies
2
Views
4K
I have been asked by Trading Standards to carry out a report on some electrical work installed by another company (5 years ago). The 'new' wet...
Replies
31
Views
3K
So this was an interesting conversation today and wanted peoples advice. Plumber asked me if I could fit a socket inside an enSuite Vainty unit...
Replies
21
Views
4K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I'm a pretty competent DIYer and always try to follow the relevant IEE/IET regs. Recently I ordered an LED bathroom cabinet from Amazon to...
Replies
29
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock