I'm writing up an EICR. On one of the lighting circuits the potential load is theoretically about 1300W on a 5A BS3871 breaker. In reality, the arrangement has been in place for at least 8 years there are no signs of thermal damage, it is difficult to find lamps these days that would max out all of the fittings (although there are those vintage and tough lamps that get around this), and they are highly unlikely to ever have all of the lamps on at once. My instinct is to give it a code 3, what would you give it?