NYY-J cables are manufactured for direct burial in the ground however to comply with BS7671 they must be protected by a duct or conduit. The only type of cable suitable for direct burial according to BS7671 is a cable which incorporates an earthed armour or metal sheath. So your method of installation is not compliant, see Regulation 522.8.10.
 
NYY-J cables are manufactured for direct burial in the ground however to comply with BS7671 they must be protected by a duct or conduit. The only type of cable suitable for direct burial according to BS7671 is a cable which incorporates an earthed armour or metal sheath. So your method of installation is not compliant, see Regulation 522.8.10.
I am not sure anyone is saying it is compliant.
 
I know but in #2 you say you weren't sure if you would Code it when it is a non-compliant means of installation.
 
Last edited:
I know but in #2 you say you wouldn't Code it when it is a non-compliant means of installation.
Correct.

Nor would I code other things because they are non-compliant, I would code them if they represented an immediate danger, a potential danger, or a recommended improvement (Or FI etc).

There isn't a requirement or option on an EICR for "not compliant" nor should there be.

Old wiring colours are non-compliant but Prima facie I wouldn't code that, Plastic CU again isn't compliant, but again in-itself I wouldn't automatically code that, and so on.

The idea of a periodic report is to make a qualified assessment if the installation is safe/suitable. That doesn't mean it has to be 100% compliant with the latest regulations.

As said earlier on in the thread, the same item, given no RCD protection would attract a different code.
 
I agree the new Coding system is poor the old Catergories were better. Having said that the cable is not installed in compliance with BS7671 and comparing it with old conductor colours and all insulated consumer units isn't relevant, that is a case of a previous compliance no longer satisfying current requirements. This cable installation has never been compliant, the fact it has rcd protection is irrelevant.
 
I agree the new Coding system is poor the old Catergories were better. Having said that the cable is not installed in compliance with BS7671 and comparing it with old conductor colours and all insulated consumer units isn't relevant, that is a case of a previous compliance no longer satisfying current requirements. This cable installation has never been compliant, the fact it has rcd protection is irrelevant.
I would disagree, how safe or unsafe something is isn't contingent on whether is was compliant or not previously, but wholly on does it or does it not present a danger.

Having or not having rcd protection changes this significantly.
 
Does it present a danger or not well we cannot anticipate that but following the requirements of BS7671 we would hope this danger is significantly reduced which is why EICRs are carried out. Item 5.9 of the condition report inspection schedule is relevant here asking whether wiring systems are appropriate etc......
Regulation 522.8.10 clearly states that unless a cable has an earthed armour or sheath then additional precautions are required such as duct or conduit, it does not suggest rcd protection as an alternative therefore some level of Coding in the Report is required.
 

Reply to EICR Codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
651
Hi All, just carried out an EICR on a rented property that has mains smoke detectors, there is no SPD fitted and as I understand any safety...
Replies
1
Views
5K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Came across this on an EICR and was wondering how everyone else would code it. Basically there’s a sangamo time clock that controls a contactor...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock