C3 in my book, unless the pefc is abnormally high.
 
It's a code 2 for me.
 
Use the adiabatic equation to confirm whether or not the single cpc size is adequate. If so, no code, but noted. If not, C2.
i agree. if the single cpc can withstand the pefc, then a C3.
 
C3... improvement recommended. i'd be inclined to fix it if it could be done economically and without pulling up floors etc.
 
Why a C3? We run ring final circuits in steel conduit and use that as a single earth.

Where is the reg that says r2 must be a ring?

Reg 543.2.9 says that with the exception of metal enclosures or coverings used as a cpc the cpc must be run as a ring with both ends connected to the earthing terminal at the circuits origin
 
Reg 543.2.9 says that with the exception of metal enclosures or coverings used as a cpc the cpc must be run as a ring with both ends connected to the earthing terminal at the circuits origin

What does 543.2.9 say in its entirety. Word for word. I'm away from home and don't have my bgb?
 
What does 543.2.9 say in its entirety. Word for word. I'm away from home and don't have my bgb?

Here you go
ImageUploadedByTapatalk1428852299.648443.jpg
 
Guess I'll have to eat humble pie on that one then.

My point still stands though, if single cpc is adequate to carry fault current then at worst C3, if not then C2.
 

Reply to EICR coding disagreement.... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
593
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
650
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Replies
20
Views
712
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock