Discuss eicr coding question in the UK Electrical Forum area at ElectriciansForums.net

D

Dave the spark

How would you code a cooker isolator switch mounted within the cooker space, I.e directly above the hobs?

It's a metal faceplate mounted flush on metal splash back.
 
Personally, I would give it a C2 because the customer could be cooking pasta one day, accidently spill the water over the cooker isolator and could cause it to develop a fault. Also steam from cooking won't do the isolator any good. Not to mention the heat from the hob.


Code C1 ‘Danger present’. Risk of injury. Immediate remedial action required.
Code C2 ‘Potentially dangerous’. Urgent remedial action required
Code C3 ‘Improvement recommended’
http://www.electricalsafetyfirst.org.uk/mediafile/100126678/best-Practice-Guide-4.pdf.
 
What regulation are you going to use on a code 2 out of interest?
Being as a kitchen isn't considered a special location anymore, there is no regulation that I can think of, However in the electricians guide to building the regulations, it says that an outlet should be at least 300mm away. As explained in my scenario there is a potential danger by water spilling onto the isolator / steam and heat effects. Hence my thinking it would be a C2
 
I wouldn't give it 'urgent action required'. Just a comment and a recommendation maybe? Daz
 
I think the issue is more likely attributed to the fact, if the chip pan catches fire on the hob, you would have to put you hand through the flames to turn it off. The odd splash of water and little bit of steam won't amount to much of an issue IMO :)
 
For a C1 or C2 you need a reg to refer to so I'd go with C3 and a comment.
 
Being as a kitchen isn't considered a special location anymore, there is no regulation that I can think of, However in the electricians guide to building the regulations, it says that an outlet should be at least 300mm away. As explained in my scenario there is a potential danger by water spilling onto the isolator / steam and heat effects. Hence my thinking it would be a C2

An eicr is based solely on BS7671 and not on whatever other guides or picture books might be out there.

If you cannot reference a regulation from BS7671 then you cannot code it.
 
I think the issue is more likely attributed to the fact, if the chip pan catches fire on the hob, you would have to put you hand through the flames to turn it off. The odd splash of water and little bit of steam won't amount to much of an issue IMO :)

How does that prevent it being turned off? The hob controls will still be just as accessible as they were before the fire started.
 
Personally, I would give it a C2 because the customer could be cooking pasta one day, accidently spill the water over the cooker isolator and could cause it to develop a fault. Also steam from cooking won't do the isolator any good. Not to mention the heat from the hob.


Code C1 ‘Danger present’. Risk of injury. Immediate remedial action required.
Code C2 ‘Potentially dangerous’. Urgent remedial action required
Code C3 ‘Improvement recommended’
http://www.electricalsafetyfirst.org.uk/mediafile/100126678/best-Practice-Guide-4.pdf.

Based on that logic every socket outlet above a kitchen worktop is just as much at risk of having water spilled on it.
 
Based on that logic every socket outlet above a kitchen worktop is just as much at risk of having water spilled on it.

Okay, if not the water, what about the heat and steam?

The steam can enter the isolator and condense on the metal in the backbox / isolator.

Here's a picture of what I had to fix a while ago:

5795d.jpg



Would regulation 522.2 External Heat Sources Apply??


522.2.1 In order to avoid the effects of heat from external wiring systems, one or more of the following methods or an equally effective method shall be used to protect a wiring system:

(i) Shielding
(ii) Placing Sufficiently far from the source of heat
(iii) Selecting a system with due regard for the additional temperature rise which may occur
(iv) Local reinforcement or substitution of insulating material


Also 512.2 External Influences?
 
Last edited:
How does that prevent it being turned off? The hob controls will still be just as accessible as they were before the fire started.
I remember when I was an apprentice, toasting our sandwiches on an electric fire for lunch. One day mine slipped off the bars, and started to catch the fire alight. Whilst I started to kick my cheese & pickled onion off the blaze, my electrician got up and turned the fire off at the socket. Guess that's what an isolator is all about, Mr Manwaring ;)
 
S
I remember when I was an apprentice, toasting our sandwiches on an electric fire for lunch. One day mine slipped off the bars, and started to catch the fire alight. Whilst I started to kick my cheese & pickled onion off the blaze, my electrician got up and turned the fire off at the socket. Guess that's what an isolator is all about, Mr Manwaring ;)

Switching off the heater would have worked just as well is my point.

And if it's an electric hob then turning it off doesn't remove the source of heat, it cools down very slowly. The fastest way to remove the source of heat in this case is to remove the burning pan from the hob.
 

Reply to eicr coding question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
641
Hi I am seeking help and best practices to achieve below tasks. I am not across regulations hence will appreciate best approach to achieve below...
Replies
11
Views
3K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
3K
I hope this is the correct thread. I have to replace the main oven selector switch in a Smeg A4-5 cooker. I can't find a proper service manual...
Replies
0
Views
464
An odd question granted but bear with me. I've got to extend a radial circuit in a community centre to fit a new hand dryer in the toilets, but I...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock