Discuss Eicr,I never like these in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
650
What’s your thoughts on this,codes etc.
Quite a lot if these,on wall lights & chain hanging lanterns.
It needs some enclosure sure, but it was ok 20 years ago,& no probs.
 

Attachments

  • 82647318-4BFF-4E7F-8BF1-51D91964FA63.jpeg
    75.8 KB · Views: 195
Best practice guide has C2 for:
  • Unenclosed electrical connections, such as at luminaires. (Such a defect can contribute to a fire, particularly where extra-low voltage filament lamps are used)
 
What would be classed as a suitable enclosure for these type of fittings? I have previously stated that i always flush a small metal architrave box in the wall to put the connections in for lights of this type but as soon as the fixing screws are taken out then any connection is always going to be exposed anyway.
I suppose maybe its all about how the connections sit against the wall and what type of wall it is etc. Also the fact that you could get rogue strands of cable sticking out of connectors wouldn't help being very close to the fitting.
 
What would be classed as a suitable enclosure for these type of fittings? I have previously stated that i always flush a small metal architrave box in the wall to put the connections in for lights of this type but as soon as the fixing screws are taken out then any connection is always going to be exposed anyway.
I suppose maybe its all about how the connections sit against the wall and what type of wall it is etc. Also the fact that you could get rogue strands of cable sticking out of connectors wouldn't help being very close to the fitting.
A flush metal box is fine when you take the screws out of any switch, socket etc the connections are exposed the recess metal box is the enclosure
 
So would it ever be acceptable to say that the fitting itself is the enclosure for these connections? I only ask this because when i was an apprentice in the 80's (gulp) the electricians i worked with nearly always just tucked the connections behind fittings of this type.
Maybe it was just different thinking then.
 
So would it ever be acceptable to say that the fitting itself is the enclosure for these connections? I only ask this because when i was an apprentice in the 80's (gulp) the electricians i worked with nearly always just tucked the connections behind fittings of this type.
Maybe it was just different thinking then.
I still see it a lot of the time now its still common
 
Although a chase in brickwork hidden behind the luminaire prevents access to the connections, it's neither insulative like a plastic junction box nor earthed like the flush architrave box, nor does it protect the terminals and exposed basic insulation from moisture etc. If any moisture is present, leakage can occur into the brick etc. I don't mind if the back of the luminaire forms the 'cover' of the box, so long as the rest of the box is made of something suitable.
 
Connector block shoved in a hole lacks care & attention imo but you will find examples in nearly every house up & down the country...
Can you touch the cores/connections when the light is in place... probably not

is it a bit badgers rough then probably yes.
in a perfect world some sort of plastic ‘box’ would Be used to house the electrical connections.
but the issue is quite often lack of physical space , most modern wall lights & ceiling lights don’t allow enough room for a 3 x 2 inch wago box to sit behind it...
 
Rough perhaps, but I think it may be okay, and compliant. Here is why:

526.5
Every termination and joint in a live conductor or a PEN conductor shall be made within one of the following or a combination thereof:
(i) A suitable accessory complying with the appropriate product standard
(ii) An equipment enclosure complying with the appropriate product standard
(iii) An enclosure partially formed or completed with building material which is non-combustible when tested to BS 476-4.

I know precisely nothing about BS 476-4, but I find it difficult to imagine that brickwork, plaster, plasterboard etc would be deemed combustible when tested to any standard.
 
Personally I would replace those connectors with wagos (other makes available).
The Wago 224 are ideal for this sort of thing. Used some in similar situation where there was barely any earth left (had been cut short) though in this case there was a metal architrave box or similar in the wall.

9880717951006.jpg
 
Rough perhaps, but I think it may be okay, and compliant. Here is why:

526.5
Every termination and joint in a live conductor or a PEN conductor shall be made within one of the following or a combination thereof:
(i) A suitable accessory complying with the appropriate product standard
(ii) An equipment enclosure complying with the appropriate product standard
(iii) An enclosure partially formed or completed with building material which is non-combustible when tested to BS 476-4.

I know precisely nothing about BS 476-4, but I find it difficult to imagine that brickwork, plaster, plasterboard etc would be deemed combustible when tested to any standard.
Ok, still not happy with it though, so what code.
[automerge]1601103809[/automerge]
The Wago 224 are ideal for this sort of thing. Used some in similar situation where there was barely any earth left (had been cut short) though in this case there was a metal architrave box or similar in the wall.

9880717951006.jpg
Yea,definitely be better but hiding them behind a old fashioned wall light would be not easy.
would need some more chopping out of brickwork, making it your responsibility,is it still rough or acceptable.
 
Still code 2 for me,it’s definitely not correct ,still needs a enclosure,pattresss.
If unsheathed cables were visible outside the enclosure once on I'd agree C2, but for the sake of argument is this any different from most of the metal decorative light fittings that come with a single bar that connects to the ceiling - they have no 'back' other than that provided by the plasterboard, yet the cabling within is usually not sheathed or in a separate enclosure (apart from the IP rated ones which are those hideous tiny ones)

And the plasterboard in these cases (unless specifically fire rated), is arguably more combustible than the wall would be in this case.

I like the way Paul Meenan from E5 approaches C2 - one thing has to happen for it to be dangerous. If the unsheathed cabling is exposed, then a nick to the insulation means danger as live parts could be accessible.

If it's within the metal enclosure, then worst that will happen with the same nick is that the metal enclosure would become live, which would then require another failure of fault protection to become dangerous.
 
Rough perhaps, but I think it may be okay, and compliant. Here is why:

526.5
Every termination and joint in a live conductor or a PEN conductor shall be made within one of the following or a combination thereof:
(i) A suitable accessory complying with the appropriate product standard
(ii) An equipment enclosure complying with the appropriate product standard
(iii) An enclosure partially formed or completed with building material which is non-combustible when tested to BS 476-4.

I know precisely nothing about BS 476-4, but I find it difficult to imagine that brickwork, plaster, plasterboard etc would be deemed combustible when tested to any standard.
What’s your thoughts on this,codes etc.
Quite a lot if these,on wall lights & chain hanging lanterns.
It needs some enclosure sure, but it was ok 20 years ago,& no probs.

Hello Cliffed.
This type of wall light connection is very common. See Pretty Mouth's comments which explains the thinking used (excuse?) for doing so. The bashing out of the masonry behind the light constitutes an "incombustible enclosure" I was given to understand in my 1960s apprenticeship. I never accepted this myself and have always installed a metal architrave box to enclose a 3 x 5 amp connector block, which fits in nicely, the front of the light fitting forming the lid of the enclosure. I have never (yet) encountered a wall light fitting that didn't completely cover the architrave box. On a slightly different note, wall lights are fashionable items which the Management occasionally decrees should be changed. Personally I find removing and replacing such fittings when required is easier with conventional screw terminals rather than Wagos etc, but each to their own. To answer your question, I would give it a C3. Regards, Colin Jenkins.
Edit. For after-market ceiling fittings fittings with no backplate (very common) I always cut a circular backplate from Tufnol or similar to enclose the connections.
 
Still code 2 for me,it’s definitely not correct ,still needs a enclosure,pattresss.
C2 - potentially dangerous. How so?
[automerge]1601116879[/automerge]
The Wago 224 are ideal for this sort of thing. Used some in similar situation where there was barely any earth left (had been cut short) though in this case there was a metal architrave box or similar in the wall.

9880717951006.jpg
These are ok, but I always worry that I might accidentally release the conductors when cramming them into whatever is enclosing them. I prefer the lever 221s myself.
 
These are ok, but I always worry that I might accidentally release the conductors when cramming them into whatever is enclosing them. I prefer the lever 221s myself.

If the cable comes forward into the enclosure I do usually use 221s, but where the cable is trimmed right back to the wall and you only have an inch or so of exposed wire and limited space, then the 224 comes into its own
 
Thanks for all comments ,all cabling needs to be connected in appropriate enclosure,the wall light is not an enclosure.
Cables can be seen when light is fitted & also the danger of causing a fault when re-fitting light.
Agree with all & pondering C3 or C2,the difference there is unsatisfactory or satisffactory status.
 
Last edited:
all cabling needs to be connected in appropriate enclosure,the wall light is not an enclosure.
If the wall light is a metallic class 2 one, then I'd agree, the terminations would need to be in one of those supplied tiny plastic boxes to insulated them from the metal casing. But looking at your picture it appears to be earthed, so I'm assuming class 1? In which case I don't see any problem with the connections being made in the base (again I'm assuming a hollow metallic base).
 
Code 2,says it all really.
[automerge]1601191955[/automerge]
Another one bites the dust ?
 

Attachments

  • B1AFF681-73E8-4A49-B3AD-34C23E1E79AC.png
    317.6 KB · Views: 41
  • 96093E12-004A-4B35-A832-C83822883AF6.jpeg
    141.2 KB · Views: 44
Code 2,says it all really.
[automerge]1601191955[/automerge]
Another one bites the dust ?
The three paragraphs you have selected from BPG4 wouldn't apply in the case of your original post because:

1. Single insulated conductors are not accessible to touch or likely to come into contact with metalwork
2. Connections are made within an enclosure according to BS7671. Read carefully the regulation I posted at #11
3. No fire barrier has been breached

With this in mind, please explain how you think this is a C2 - potentially dangerous?
 
The three paragraphs you have selected from BPG4 wouldn't apply in the case of your original post because:

1. Single insulated conductors are not accessible to touch or likely to come into contact with metalwork
2. Connections are made within an enclosure according to BS7671. Read carefully the regulation I posted at #11
3. No fire barrier has been breached

With this in mind, please explain how you think this is a C2 - potentially dangerous?
Could be potentially dangerous,& definitely a fire hazard.
 
Could be potentially dangerous,& definitely a fire hazard.
Please can you qualify that statement with some kind of explanation? How is it potentially dangerous? What is the increased risk of installing this way? How is there an increased risk of fire over other common installation methods? Please explain.
 
Please can you qualify that statement with some kind of explanation? How is it potentially dangerous? What is the increased risk of installing this way? How is there an increased risk of fire over other common installation methods? Please explain.
Not the best connection.
No actually fire barrier,the connections can be seen,when light is refixed.
Failure of earth connection @ light, danger of live @ fitting,causing shock hazard to persons.
[automerge]1601227658[/automerge]
How can anyone actually say this is ok, it’s like going back to the bad old days.
Would anyone just leave it like this,C2 .
 

Attachments

  • DAB902FF-9C2D-4728-9D63-9DB6EFA3AFCD.png
    548 KB · Views: 33
Is that on a brick wall? If so it’s not a fire rest is it?
Certainly not more of a fire hazard than on a plasterboard ceiling imo, and most modern Class 1 lights use the ceiling as part of their enclosure so presumably they feel it's sufficient.

As already mentioned, 526.5 allows building material that is non-combustible to BS 476-4 but since that is no doubt £100 I'm not looking up whether brick or plaster is covered, though I'd expect it is.

If there was a hole through to the cavity there might be another argument - but then that is the case with most ceiling lights and even many pendants
[automerge]1601228255[/automerge]
Not the best connection.

I'd fix that on site and charge accordingly, not note it. But either the connection is tight and secure or not. We aren't coding workmanship.

No actually fire barrier,

the connections can be seen,when light is refixed.

I (and others I think) assumed the light fitting went over that hole and covered it, but if the terminal blocks were visible when the light went back on then we've been talking at cross purposes and obviously it's a C2 (maybe C1) and I don't think anyone here would argue otherwise...


Failure of earth connection @ light, danger of live @ fitting,causing shock hazard to persons.

Can't tell that from the picture, but no earth continuity at a Class 1 light is certainly a C2, don't think anyone here would say otherwise?

How can anyone actually say this is ok, it’s like going back to the bad old days.
Would anyone just leave it like this,C2 .
[/QUOTE]
 
Last edited:
Not the best connection.
No actually fire barrier,the connections can be seen,when light is refixed.
Failure of earth connection @ light, danger of live @ fitting,causing shock hazard to persons.
[automerge]1601227658[/automerge]
How can anyone actually say this is ok, it’s like going back to the bad old days.
Would anyone just leave it like this,C2 .

I think you need to upload a picture of the light fitted back on the wall, we can only comment on what we see.

The type of enclosure has no bearing on the soundness of the connections. If the light is not earthed due to a loose connection, again the type of enclosure is irrelevant. If there is physical access to live parts when the light is fitted then it's a C1, so why didn't you say this in your first post?
 
You funny man.
My conscience is still intact,& still C2
I’m sorry mate. If the light is fixed back and connections are enclosed, it’s not a fire risk and it’s not a shock risk C3 at best, and that probably been harsh. If a metal fitting isn’t earthed then that’s a C2. If you can get your finger to the connections it’s a C1.
Ideally this should have a metal architrave box behind it, that would be good practice. All you are seeing is bad practice.
 
I’m sorry mate. If the light is fixed back and connections are enclosed, it’s not a fire risk and it’s not a shock risk C3 at best, and that probably been harsh. If a metal fitting isn’t earthed then that’s a C2. If you can get your finger to the connections it’s a C1.
Ideally this should have a metal architrave box behind it, that would be good practice. All you are seeing is bad practice.
Ok,down to interpretation,opinion & experience.
Its my report my interpretation,my conscience,I’m sticking.
Thanks all for your comments all taken on board.
 

Reply to Eicr,I never like these in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
770
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Info: Located in US I have a 48” T8 fixture that I recently added LED’s by removing the ballast and wiring directly. After doing so when hanging...
Replies
8
Views
926
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
654

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock